Default rtd reading 50 degrees low

I have a copper coil through my HLT to use as a HERMS with an RTD probe on the output side of the copper coil. The RTD is reading about 50 degrees low. The controller (Ascon x1) seems to be operating properly... when I compensate for the temp difference it sends a switch signal to the SSR that's controls the (120v) heating element in the HLT at appropriate times.
I am using an Ebay RTD probe with 3 wires out of the probe- could a mis-wiring from the probe to the PID account for the bad temp reading, or do I have a bad probe?


chrisdb is offline
 
Reply With Quote
Old 03-16-2012, 01:28 PM   #2
Junkster
Feedback Score: 0 reviews
Recipes 
 
Join Date: Feb 2011
Location: North Central, Ohio
Posts: 509
Liked 31 Times on 22 Posts
Likes Given: 3

Default

If you have a meter, check the resistance of the RTD & refer to the reference tables for that particular unit and see how close you are. If I remember correctly, 2 of the wires are connected together on one side of the RTD so those should read very close to 0 ohms and between either of those and the third wire is the resistance that changes with temperature.


Junkster is offline
 
Reply With Quote
Old 03-16-2012, 01:51 PM   #3
chrisdb
Feedback Score: 0 reviews
Recipes 
 
Join Date: Nov 2010
Location: philadelphia, pa
Posts: 223
Liked 9 Times on 9 Posts
Likes Given: 4

Default

quite right- 2 conductors connect to one terminal in the PID. Checking resistance between the three makes a lot of sense- beats rolling the dice like I did. Thanks!
chrisdb is offline
 
Reply With Quote
Old 03-16-2012, 03:37 PM   #4
JRems
Feedback Score: 0 reviews
Recipes 
 
Join Date: Nov 2010
Location: Mahopac, NY
Posts: 2,230
Liked 60 Times on 52 Posts
Likes Given: 9

Default

There's more than one kind of rtd as well maybe you have the settings on the pid wrong for the type of rtd you have. I think one rtd is pt100 and the other is a Cu50, at least that's what my auber manual has listed as supporting different rtd sensors.
JRems is offline
 
Reply With Quote
Reply


Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Auber SYL-2352 Overshoots mash temp by about 5 degrees. BrewinBigD Electric Brewing 6 02-06-2012 11:26 PM
Ever see a pot of boiling water give a reading of -55F? I have... Puffy84 Electric Brewing 6 06-27-2011 04:25 PM
PID Pv value off 13.5 degrees F Malintent Electric Brewing 4 03-04-2011 10:55 PM


Forum Jump

Newest Threads

LATEST SPONSOR DEALS