Spa Panel, how many AMPS - Home Brew Forums

Register Now!
Home Brew Forums > Home Brewing Beer > Electric Brewing > Spa Panel, how many AMPS

Reply
 
Thread Tools
Old 03-03-2012, 05:31 AM   #1
Sanderoll
Recipes 
 
May 2011
Montreal, Québec
Posts: 24



I want to go the electric route soon. Going one step at a time, I'm already brewing with speciality grain with my extract. I want to go BIAB electric, full volume boil.

I just won an auction on Ebay for a GFCI spa panel breaker box they tell me to choose between 40-50-60 amps.

Right now I'm in an appartement, the place I want to plug it to was a place for a stove/oven. I have 40 amps circuit breaker there (200 amps service in the house). Not sure about the wire gauge, the plug is 4 prong.

I want to build to a 3 vessel brewing rig to do 5 and 10 gallons batches.

Is there a problem buying a 50 or 60 amp spa panel on my 40 amp circuit for now so I don't have to buy another 50 or 60 amp later. (maybe running 2x 5500w or 4500w element + 2 march pump) I plan on buying my own place in a couple of years, putting my cash down aside as we talk .

I think this set up from Tiber Brew : http://www.homebrewtalk.com/f170/ele...d-help-183775/ looks similar to my future plan any use to have a 60 amps breaker spabox (if I upgrade the breaker in breaker box and wires) or its useless and i should only go with 50 and it will do for now and for future 2 march pumps +2x element ?

Reason: added couple info

 
Reply With Quote
Old 03-03-2012, 10:34 PM   #2
pvtschultz
Recipes 
 
Feb 2010
New Berlin, Wisconsin
Posts: 457
Liked 8 Times on 8 Posts


You can use whatever one you want, the primary breaker will act as an over-current protection device and your spa panel breaker will keep you for electrocuting yourself. A single 5500W element will pull 25 amps and will boil a 10 gallon batch. If you ever decide that you need to fire two 5500W elements in the future, a 60 amp GFCI spa panel will come in handy.
__________________
Brewing: Amber Ale, Dunkel
Drinking: Sour Brown, Schlitz...
On Deck: Berliner Weisse, Spotted Cow Clone, CAP...
2016 Gallons Brewed: 10 :(
Gallons Brewed '11-'15: 319

http://www.homebrewtalk.com/f170/pvt...inally-298407/

 
Reply With Quote
Old 03-03-2012, 10:40 PM   #3
Bobby_M
Vendor and Brewer
HBT_SPONSOR.png
 
Bobby_M's Avatar
Recipes 
 
Aug 2006
Whitehouse Station, NJ
Posts: 23,245
Liked 1695 Times on 1089 Posts


No reason not to get the 60.
__________________
Welcome to BrewHardware.com. I love you.
Corny Keg Dry Hop Canisters $26.50 for limited time
Chugger Pumps, Pump Kits, Camlocks, Sightglasses, Clear USA made Silicone Tubing, RIMS, Electric Install Parts, etc.

 
Reply With Quote
Old 03-05-2012, 04:20 AM   #4
Sanderoll
Recipes 
 
May 2011
Montreal, Québec
Posts: 24


I won the auction a couple days ago and I didn't want to wait to long before paying the seller so I went with the 50 amps. If I need more for other purposes like pumps or lights I'll just use a wall outlet.

Quote:
Originally Posted by pvtschultz View Post
You can use whatever one you want, the primary breaker will act as an over-current protection device and your spa panel breaker will keep you for electrocuting yourself.
That's what I thought but I rather ask to make sure their was no problem doing so.

Quote:
Originally Posted by pvtschultz View Post
A single 5500W element will pull 25 amps and will boil a 10 gallon batch. If you ever decide that you need to fire two 5500W elements in the future, a 60 amp GFCI spa panel will come in handy.
Is it overkill 5500W what for BIAB 5 gallon batch ?
Is 2x 5500 + 2x March pump good on a 50 amps gfci ?

 
Reply With Quote
Old 03-05-2012, 01:31 PM   #5
pvtschultz
Recipes 
 
Feb 2010
New Berlin, Wisconsin
Posts: 457
Liked 8 Times on 8 Posts


I like the 5500W element with 5 gallon boils; going from tap water temp to mash temp and then to boil happen quite quickly (especially when compared to doing stove top batches). You just need a way to tame it a bit during the boil. I use a PWM for that purpose but the better PID controllers have a manual mode built in as well. I brew in a keggle so the larger element will allow me to brew bigger batches. But then again, my ferm chamber limits me to two carboys at a time...
__________________
Brewing: Amber Ale, Dunkel
Drinking: Sour Brown, Schlitz...
On Deck: Berliner Weisse, Spotted Cow Clone, CAP...
2016 Gallons Brewed: 10 :(
Gallons Brewed '11-'15: 319

http://www.homebrewtalk.com/f170/pvt...inally-298407/

 
Reply With Quote
Old 03-05-2012, 04:06 PM   #6
yjfun
Recipes 
 
Jun 2010
Arlington, Washington
Posts: 225
Liked 2 Times on 2 Posts


The spa panel that you won is probably a 100 or 125amp panel and they just installed whatever size gfci breaker that you wanted before shipping. If this is so then it probably also has 2 more spaces for more breakers. When you get your new residence you can feed this panel with whatever you want up to it's maximum rating and then add a couple of 20 amp gfci breakers for any ancillary equipment that you are wanting to use during your brew day (like your pumps and all your control wiring) leaving you with the full 50 amps for your elements.

I found that a 4500 watt element is plenty fast enough for 10 gallon batches and it keeps all the wiring and components quite a bit cheaper since you only need to buy 20 amp switches and wire instead of 30 amp.

 
Reply With Quote
Old 03-05-2012, 06:12 PM   #7
audger
Recipes 
 
Apr 2011
., Connecticut
Posts: 1,497
Liked 43 Times on 42 Posts


Quote:
Is there a problem buying a 50 or 60 amp spa panel on my 40 amp circuit for now so I don't have to buy another 50 or 60 amp later. (maybe running 2x 5500w or 4500w element + 2 march pump)
the only problem with putting a breaker that is too large in the circuit is that it will no longer protect the wiring behind it from overheating. if you are concious about not overloading the wire between the breaker and heating element, then it shouldnt be a big problem (besides not being up to code), but you have no safety net. if you accidentally pull too many amps, you can start an electrical fire as the breaker wont trip before the wire gets too hot.

you can put a 60A GFCI breaker behind a regular 40A breaker in the box- that would be OK (although harder to install, and also probably not up to code). it would atleast mean you couldnt burn your house down as easily....

 
Reply With Quote
Old 03-05-2012, 06:37 PM   #8
pvtschultz
Recipes 
 
Feb 2010
New Berlin, Wisconsin
Posts: 457
Liked 8 Times on 8 Posts


Quote:
Originally Posted by audger View Post
You can put a 60A GFCI breaker behind a regular 40A breaker in the box- that would be OK (although harder to install, and also probably not up to code). it would atleast mean you couldnt burn your house down as easily....
He bought a spa panel which is a sub panel being fed from the main. There are hundreds of us here that use the 50 amp GE spa panel sold by Home Depot to protect us from electrocution. My spa panel plugs into my dryer outlet which is protected by a 30 amp breaker. There is nothing wrong with that at all. What you said is akin to not being able to plug a GFI protected 1/2 amp floor lamp into a 15 amp branch. In a nut shell, GFI is GFI no matter what the current running through it is (within the design limits of course).

And, I'm guessing that 99% of our eBreweries don't follow the NEC to a "T" anyways, with the exception of the many electrical engineers and electricians on the board.
__________________
Brewing: Amber Ale, Dunkel
Drinking: Sour Brown, Schlitz...
On Deck: Berliner Weisse, Spotted Cow Clone, CAP...
2016 Gallons Brewed: 10 :(
Gallons Brewed '11-'15: 319

http://www.homebrewtalk.com/f170/pvt...inally-298407/

 
Reply With Quote
Old 03-06-2012, 01:50 AM   #9
Dgonza9
 
Dgonza9's Avatar
Recipes 
 
May 2010
Evanston, Illinois
Posts: 1,182
Liked 11 Times on 11 Posts


Quote:
Originally Posted by audger View Post
the only problem with putting a breaker that is too large in the circuit is that it will no longer protect the wiring behind it from overheating. if you are concious about not overloading the wire between the breaker and heating element, then it shouldnt be a big problem (besides not being up to code), but you have no safety net. if you accidentally pull too many amps, you can start an electrical fire as the breaker wont trip before the wire gets too hot.

you can put a 60A GFCI breaker behind a regular 40A breaker in the box- that would be OK (although harder to install, and also probably not up to code). it would atleast mean you couldnt burn your house down as easily....
I'm confused. If he has a 30 amp breaker in the main panel feeding the spa panel, the main breaker will trip if more than 30 amps is drawn, no? So what difference does it make how many amps the breaker in the spa panel is?

Or are you saying that the wiring leading to the element is not rated as high as the main breaker? In that case, a fuse could protect the wire, no? but that element will draw 25 amps or so, right? So why wouldn't he use 10 gauge wire?
__________________
On Tap: Belgian Barrel Aged Barleywine, Da Yooper's Oatmeal Stout, Breakfast Stout, Hop Your Face Off IIPA, Catcher in the Rye Saison, "Wino-head" Nelsin Sauvin Gumballhead.

Bourbon Barrel Duchesse De Bourgnone
Kegged:

Fermenting English Mild

on Deck: Lager?

 
Reply With Quote
Old 03-10-2012, 03:14 AM   #10
Sanderoll
Recipes 
 
May 2011
Montreal, Québec
Posts: 24


I just received the breaker today I got the 50 amps but the break isn't installed in the enclosure. Not a problem I saw someone post how to install it. I wonder however is it normal that when I genlty shake the breaker it feels like small pieces are moving inside. Also, the test button is pushed.

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Spa panel Banjoman002 Electric Brewing 1 02-24-2012 10:39 PM
What guage wire from main panel to spa panel? AdamCanFly Electric Brewing 22 02-01-2012 03:36 AM
Mounting spa panel guts in control panel kevink Electric Brewing 7 08-20-2011 02:31 AM
panel to spa panel wiring buffalobrewer Electric Brewing 4 11-29-2010 12:06 AM
How do I run lower volts and amps to my switches? Ranger9913 Electric Brewing 8 10-17-2010 02:38 PM


Forum Jump