Which breakers are most appropriate for circuit protection in a control panel?

 
Reply With Quote
Old 02-28-2012, 11:28 PM   #2
Mb2658
Recipes 
 
Nov 2011
, NE
Posts: 421
Liked 36 Times on 26 Posts


Bump! Someone has to know the difference. Will 1077 breakers work properly?

 
Reply With Quote
Old 02-29-2012, 02:22 AM   #3
TrainSafe
 
TrainSafe's Avatar
Recipes 
 
Mar 2011
Appleton, WI
Posts: 808
Liked 69 Times on 46 Posts


There is a good article describing the diifferences here.

From what I understand, you are required by the NEC to use UL 489 breakers in the panel that feeds the branch cicuit. This would be the load center or panelboard in your home.

If you install additional breakers inside your control panel (in lieu of fuses) then the 1077 breakers would be well suited for that application.

Hope this helps.

 
Reply With Quote
Old 02-29-2012, 04:42 AM   #4
Mb2658
Recipes 
 
Nov 2011
, NE
Posts: 421
Liked 36 Times on 26 Posts


Quote:
Originally Posted by TrainSafe
There is a good article describing the diifferences here.

From what I understand, you are required by the NEC to use UL 489 breakers in the panel that feeds the branch cicuit. This would be the load center or panelboard in your home.

If you install additional breakers inside your control panel (in lieu of fuses) then the 1077 breakers would be well suited for that application.

Hope this helps.
That clears it up. I am planning on using breakers in lieu of fuses and will go with 1077 breakers. Thanks!

 