If going from 3-wire 240V into spa panel as shown would I still get to use 120V off one of the 240V legs like I am now with 4-wire 240V? If so that would be awesome as I built my panel around 4-wire 240V then moved to older apartment where both dryer and range are 3-wire and I'm stuck with running extension cords for pump and power for BCS-460 controller.


kevin509 is offline
 
Reply With Quote
Old 02-13-2012, 06:51 AM   #22
lschiavo
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
lschiavo's Avatar
Recipes 
 
Join Date: Sep 2009
Location: Surrounded by Yoopers
Posts: 4,387
Liked 948 Times on 637 Posts
Likes Given: 780

Default

Quote:
Originally Posted by kevin509 View Post
If going from 3-wire 240V into spa panel as shown would I still get to use 120V off one of the 240V legs like I am now with 4-wire 240V? If so that would be awesome as I built my panel around 4-wire 240V then moved to older apartment where both dryer and range are 3-wire and I'm stuck with running extension cords for pump and power for BCS-460 controller.
It will work. You will be using an equipment ground as a neutral though. This was allowed in the past as a way around supplying a neutral to 120V control systems in 240V appliances. A bare ground wire is not intended to carry current. If you are using it that way it is "technically" not correct.
lschiavo is offline
 
Reply With Quote
Old 02-13-2012, 07:09 AM   #23
lschiavo
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
lschiavo's Avatar
Recipes 
 
Join Date: Sep 2009
Location: Surrounded by Yoopers
Posts: 4,387
Liked 948 Times on 637 Posts
Likes Given: 780

Default

Quote:
Originally Posted by kerklein2 View Post
Well the stuff Home Depot has (Cerro Wire) is only 25A, as is anything McMaster has. But I just found this that is 30A as well as nice and cheap. I'll be going with it.

http://lockingpowercords.com/Products/513-104-soow-wire.aspx
The temperature rating is critical in the ampacity rating. Most wire/cable is rated at 90C. Most connectors and some cable is rated at 75C. Lower temp rating-->lower amp rating. You will be fine using #10 protected at 30A. Derating for length is generally only necessary over 100 feet.
lschiavo is offline
 
Reply With Quote
Reply


Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Thinking about 120v BIAB setup theschick Electric Brewing 41 01-13-2012 02:29 AM
120v/2000w & 240v/5500w together in keggle Flyin Electric Brewing 11 09-17-2011 05:42 AM
can someone help with 120v? agezzi Electric Brewing 58 08-15-2011 11:12 AM
Switch for running element at 120v OR 240V? thelorax121 Electric Brewing 14 05-10-2011 11:37 PM
Strange issue with 240v legs. 120v on both, no 240v Brewmoor Electric Brewing 5 12-03-2010 07:15 PM


Forum Jump

Newest Threads

LATEST SPONSOR DEALS