Im getting close to starting to buy parts for my electric build. I am just trying to go over everything before I start putting out the cash. I have a couple questions Im hoping you might be able to help me out with. Currently I am planning to run off of my dryer outlet and for now just run one element at a time. Eventually I would like to bump up to a 50A setup but in the short term I would like to set it up with a Spa Panel running off of the dryer outlet. This way it is portable to anywhere that has a dryer outlet (friends house). The main restriction that I can see is that my dryer plug in is about 50 ft from where I normally brew. I found this extension cord on Craiglist. its 100' 30A 12/3. Do you see any problems plugging this into my dryer outlet and then running this to my Spa Panel. Then 4 wire cord from Spa Panel to Control panel? Let me know if Im missing anything.

Shore Power Cord 100 ft. 30A Mil-Spec

Rig will be 5500W element, PID, RTD. Happy to answer any questions if I left something out.


 
Reply With Quote
Old 01-20-2012, 08:33 PM   #2
audger
Recipes 
 
Apr 2011
., Connecticut
Posts: 1,497
Liked 43 Times on 42 Posts


the only thing a 50+ foot cord does is cause a voltage drop, which will decrease available power to the element. everything should still work just fine, but if you measure a solid 240v at the dryer element, you will measure around 231v at the end of that 100ft extension cord. if you cut the cord in half and used 50 feet, voltage would drop by half as much, or to ~235v.

that is assuming you have a full 240v at the dryer plug, which often isnt the case. if you are starting out at only 230v, you will only have 221v at the end, etc. a heating element is a resistive load and really doesnt care what voltage it gets. if you are trying to run a pump or other controls off one of the 120v legs, you may only have 100 or 110v, which could be a problem.

a 5500w element draws 5500w at 240v. at 230v, it will only draw 5270w. at 220v it will only draw ~5000w. so you can see how the element power is derated as you decrease voltage. as long as you are aware of that, there is nothing else you should worry about.

shroomzofdoom Likes This 
Reply With Quote
Old 01-20-2012, 08:54 PM   #3
br1dge
 
br1dge's Avatar
Recipes 
 
Dec 2010
Roswell, GA
Posts: 291
Liked 9 Times on 7 Posts


Quote:
Originally Posted by audger View Post
the only thing a 50+ foot cord does is cause a voltage drop, which will decrease available power to the element. everything should still work just fine, but if you measure a solid 240v at the dryer element, you will measure around 231v at the end of that 100ft extension cord. if you cut the cord in half and used 50 feet, voltage would drop by half as much, or to ~235v.

that is assuming you have a full 240v at the dryer plug, which often isnt the case. if you are starting out at only 230v, you will only have 221v at the end, etc. a heating element is a resistive load and really doesnt care what voltage it gets. if you are trying to run a pump or other controls off one of the 120v legs, you may only have 100 or 110v, which could be a problem.

a 5500w element draws 5500w at 240v. at 230v, it will only draw 5270w. at 220v it will only draw ~5000w. so you can see how the element power is derated as you decrease voltage. as long as you are aware of that, there is nothing else you should worry about.
Thanks audger!! That doesnt sound like too much of an issue for the elements. Starting with 5500W gives me some room to lose wattage and still be fine. I was planning on eventually running my whole control panel off of the Spa Panel (after the extension cord) which would include my pumps at 120V. You said this "could" be a problem. Can you elaborate more on this?

Does this mean that if I want my full control panel to eventually run 100' from the breaker that I would need to either buy a 50A breaker to start with or maybe run heavier guage wire permanently to the Spa Panel?

It would be nice to have the whole thing portable but maybe thats just not feasible??

 
Reply With Quote
Old 01-20-2012, 10:13 PM   #4
jeffmeh
HBT_SUPPORTER.png
 
jeffmeh's Avatar
Recipes 
 
Feb 2009
Posts: 2,143
Liked 210 Times on 180 Posts


IANAE (I am not an electrician), but I thought 30 amp required 10 gauge wire.

 
Reply With Quote
Old 01-20-2012, 10:33 PM   #5
rollinred
Recipes 
 
Jan 2008
Traverse City, MI
Posts: 327
Liked 10 Times on 7 Posts


Quote:
Originally Posted by jeffmeh View Post
IANAE (I am not an electrician), but I thought 30 amp required 10 gauge wire.
What he said.

 
Reply With Quote
Old 01-21-2012, 12:14 AM   #6
Hoosier-Brewer
 
Hoosier-Brewer's Avatar
Recipes 
 
Feb 2011
East of Indy, Indiana
Posts: 271
Liked 5 Times on 5 Posts


12/3 is good for 20 amps.

 
Reply With Quote
Old 01-21-2012, 12:17 AM   #7
NoCornOrRice
Recipes 
 
Aug 2010
Great White North
Posts: 227
Liked 18 Times on 9 Posts


For that price, you could probably get 50' or more of the really good stuff: 10/4 SOOW.

 
Reply With Quote
Old 01-21-2012, 12:35 AM   #8
Hoosier-Brewer
 
Hoosier-Brewer's Avatar
Recipes 
 
Feb 2011
East of Indy, Indiana
Posts: 271
Liked 5 Times on 5 Posts


Quote:
Originally Posted by NoCornOrRice View Post
For that price, you could probably get 50' or more of the really good stuff: 10/4 SOOW.
You're probably right on that. I have a 30 amp RV cord on my camper that was ~$45 and it's 50'. Similar to this, but I got a much better price. Walmart.com: Road Power 30-Amp RV Extension Cord, 30': Computers

 
Reply With Quote
Old 01-21-2012, 07:45 PM   #9
yjfun
Recipes 
 
Jun 2010
Arlington, Washington
Posts: 225
Liked 2 Times on 2 Posts


Extension cords don't follow the same rules as regular wiring sizes in a home. If you are going to hook up anything that requires 120 volts in your control panel then you will need 4 wire cord and the allowed amp loads are as follows. #12 20amps, #10 25amps, #8 35amps, #6 45amps, #4 60amps. The reason for this is heat buildup. The breaker may not trip because the amp load isn't high enough to show a short but the cord can essentially turn into a heating element and burn your house down. Using a longer cord increases the resistance and causes even more heat.

 
Reply With Quote
Old 01-22-2012, 04:32 AM   #10
Dert
Recipes 
 
May 2011
Mpls, Mn
Posts: 96
Liked 15 Times on 10 Posts


I have #8 Cu running out to my detached garage with a 50 amp breaker...inspected and passed by the state of MN.

And, I just ran 2 50 amp circuits using #6 Al wire (XHHW-2, rated for 90 degrees C) that is rated for 55 amps at 60 degrees C. yjfun, the numbers you listed are wrong...a lot of the ampacity depends on the type of wire and how it is run.

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
12gauge extension cord rated at only 15Amps Scut_Monkey Electric Brewing 23 04-25-2011 06:01 PM
Extension Cord for Heatstick SeanT Electric Brewing 11 02-03-2011 03:25 PM
240V Extension cord question for the gurus jflimbo Electric Brewing 3 01-18-2011 11:24 PM
extension cord to fridge? kornbread Electric Brewing 4 12-17-2010 01:09 PM
Range extension cord>outlet>inline gfi snail Electric Brewing 4 12-13-2010 04:22 PM