Quote:
Originally Posted by lschiavo View Post
Most lugs are not rated for more than one conductor so adding another tap to your feed through lugs may not be correct. You could replace the stove panel with a small load-center and gain a few future breakers while at it. Six service disconnects is the rule. You have two now if I understand correctly.
That's probably what I'll wind up doing, just means I need to upgrade to thicker copper feeding the sub panel. I had some 10G around and was trying to save time. Only in the house another year so trying to minimize my investments.

Also, if I'm going to go with the switch would it make more sense to put it upstream of the PID? That way when I cut the power with the switch it kills the PID and the element at the same time.

 
Reply With Quote
Old 12-01-2011, 12:29 AM   #12
lschiavo
HBT_LIFETIMESUPPORTER.png
 
lschiavo's Avatar
Recipes 
 
Sep 2009
Surrounded by Yoopers
Posts: 4,594
Liked 1046 Times on 711 Posts


Quote:
Originally Posted by mrbippers View Post
Also, if I'm going to go with the switch would it make more sense to put it upstream of the PID? That way when I cut the power with the switch it kills the PID and the element at the same time.
You certainly could. That way it would be a MAIN switch for the box.

 
Reply With Quote
Old 12-01-2011, 12:53 AM   #13
lazybean
Recipes 
 
Sep 2009
San Diego
Posts: 177
Liked 1 Times on 1 Posts


L630 is a 240v only, if you use the ground as a neutral you will trip the GFCI instantly.
the NEMA L1430 is rated for 120/240, it is 4wire(2 hots,1 neutral, 1 ground)

 
Reply With Quote
Old 12-01-2011, 01:00 AM   #14
lschiavo
HBT_LIFETIMESUPPORTER.png
 
lschiavo's Avatar
Recipes 
 
Sep 2009
Surrounded by Yoopers
Posts: 4,594
Liked 1046 Times on 711 Posts


Quote:
Originally Posted by lazybean View Post
L630 is a 240v only, if you use the ground as a neutral you will trip the GFCI instantly.
the NEMA L1430 is rated for 120/240, it is 4wire(2 hots,1 neutral, 1 ground)
The Auber PID can be powered by a range of AC voltage I believe. I assumed it was powered with 240V in this circuit. It should be ok I think.

 
Reply With Quote
Old 12-01-2011, 01:19 AM   #15
lazybean
Recipes 
 
Sep 2009
San Diego
Posts: 177
Liked 1 Times on 1 Posts


My bad, when i looked at the wiring diagram i thought he had the SSR and Controler running 120 off the ground.

Should put my beer down when posting.

 
Reply With Quote
Old 12-01-2011, 01:25 AM   #16
lschiavo
HBT_LIFETIMESUPPORTER.png
 
lschiavo's Avatar
Recipes 
 
Sep 2009
Surrounded by Yoopers
Posts: 4,594
Liked 1046 Times on 711 Posts


Quote:
Originally Posted by lazybean View Post
Should put my beer down when posting.
Never! I almost always post with beer in hand. It keeps things interesting

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
My two 5500 watt element 1 PID and SSR build bigljd Electric Brewing 54 01-21-2015 06:52 PM
Simple Brutus 20 Electric Build digg1es Electric Brewing 10 08-15-2012 11:03 PM
Simple Electric Build....From the Pros ekjohns Electric Brewing 111 04-10-2012 11:19 PM
another simple e build wncbrewer Electric Brewing 4 06-27-2011 12:41 AM
Simple Electricity Design - 1 Element Martin2D Electric Brewing 2 11-28-2010 01:21 AM


Forum Jump