Old 11-07-2011, 12:29 AM   #11
bigljd
Recipes 
 
Oct 2010
Sacramento, CA
Posts: 410
Liked 24 Times on 19 Posts


Quote:
Originally Posted by samc View Post
Maybe a dumb observation but isn't 10g overkill for this switch? It can't handle the power that 10g does so why not downsize the wire to the switch?

Could be I just don't understand whats going on here.

I'm basing my control panel on this P-J schematic (minus the timer):




The load to the heating element will go thru the switch. P-J explains why the switch will work for this application here:

http://www.homebrewtalk.com/f170/con...4/#post3118433

Hope that helps



 
Reply With Quote
Old 11-07-2011, 12:41 AM   #12
bowhuntah
Registered User
Recipes 
 
Jun 2011
Windham, Maine
Posts: 111
Liked 2 Times on 1 Posts


Quote:
Originally Posted by clearwaterbrewer View Post
15W will not cut it for 10ga..
Agreed. I used a 25W iron.



 
Reply With Quote
Old 11-07-2011, 12:53 AM   #13
bigljd
Recipes 
 
Oct 2010
Sacramento, CA
Posts: 410
Liked 24 Times on 19 Posts


Quote:
Originally Posted by bowhuntah View Post
Agreed. I used a 25W iron.
I picked up an adjustable 20 to 50 watt iron from Radio Shack, so I should be good. I got a little practice today soldering the 2 resistors from the schematic together, and then soldered them to a fuse holder. I did a lot of soldering of electronic stuff when I was a kid, but it's been a long time.

 
Reply With Quote
Old 11-07-2011, 01:36 AM   #14
laddg
Recipes 
 
Jun 2011
Ham Lake, MINNESOTA
Posts: 26
Liked 1 Times on 1 Posts


Quote:
Originally Posted by samc View Post
Maybe a dumb observation but isn't 10g overkill for this switch? It can't handle the power that 10g does so why not downsize the wire to the switch?
+100 for the concern here. It looks to me like you are switching the heater elements through that switch, and I cannot believe it could possibly handle the current. Check that out carefully or you could create an overheat / fire condition.

DJG

 
Reply With Quote
Old 11-07-2011, 01:46 AM   #15
samc
Recipes 
 
Aug 2008
Portland OR
Posts: 5,373
Liked 62 Times on 58 Posts


Quote:
Originally Posted by laddg View Post
+100 for the concern here. It looks to me like you are switching the heater elements through that switch, and I cannot believe it could possibly handle the current. Check that out carefully or you could create an overheat / fire condition.

DJG
That's not my concern at all. All I was saying was that you don't have any need to size wire above the load the switch can handle, therefore the soldering issue is much easier. If a wire can handle 30 amps @ 240v but the switch only handles 10amps and you put 30 amps on it the switch will burn up.

 
Reply With Quote
Old 11-07-2011, 03:00 AM   #16
Yuri_Rage
Gritty.
HBT_MODERATOR.png
 
Yuri_Rage's Avatar
Recipes 
 
Jul 2006
Southwest
Posts: 14,238
Liked 780 Times on 497 Posts


A bit more food for thought - crimped connections are often recommended over solder in high current applications. A fault (even momentary) could melt the solder and cause further harm.
__________________
Homebrewed Blog..........YouTube Channel .......... Shirts, posters, etc

 
Reply With Quote
Old 11-07-2011, 03:03 AM   #17
samc
Recipes 
 
Aug 2008
Portland OR
Posts: 5,373
Liked 62 Times on 58 Posts


So the ? is still out, why do you need 10 gauge wire going into a switch that can't handle the load a 10 gauge can handle?

Reason: removed OT banter

 
Reply With Quote
Old 11-07-2011, 01:42 PM   #18
mabrungard
HBT_LIFETIMESUPPORTER.png
 
mabrungard's Avatar
Recipes 
 
Feb 2011
Carmel, IN
Posts: 3,987
Liked 535 Times on 421 Posts


Why are you bringing 10g wire to that switch? It can't handle the current that the wire can, so reducing to a smaller wire is prudent. If your system was assuming that high amperage will be routed through the switch, then you need to use a relay on this circuit so that the high amperage is not routed through the switch.
__________________
Martin B
Carmel, IN
BJCP National
Foam Blowers of Indiana (FBI)

Brewing Water Information at:
https://sites.google.com/site/brunwater/

Like Bru'n Water on Facebook for occasional discussions on brewing water and Bru'n Water
https://www.facebook.com/pages/Brun-...?ref=bookmarks

 
Reply With Quote
Old 11-07-2011, 03:36 PM   #19
lschiavo
HBT_LIFETIMESUPPORTER.png
 
lschiavo's Avatar
Recipes 
 
Sep 2009
Surrounded by Yoopers
Posts: 4,407
Liked 991 Times on 668 Posts


I would not use this switch for high current. If the switch was meant to handle 30A, It would not be an issue connecting 10ga wire to it.

I also do not agree with the (2) 1k 1W resistors. They will not handle the power dissipated. I used (4) 1k 1W resistors in series. This gives 30mA fault current and dissipates 3.6W. It will trip the GFCI and cannot burn up if the GFCI fails to trip. The fuse in the circuit serves no function as the current is limited by the resistors. The fuse really does no harm but I think it is a weak link in a critical circuit.

**edit** And while I'm at it, why is anyone fusing the PID at 1A? I contacted an Auber tech and he said the PID is internally protected and no additional fusing is necessary. The PID could be connected after the 10A fuse in the above drawing and save a few components. And why a 10A fuse?? No wire size is indicated on the drawings. I used a 15A fuse with #14ga wire to power my receptacles and PID.

 
Reply With Quote
Old 11-07-2011, 03:38 PM   #20
mccumath
Recipes 
 
Dec 2010
Idaho
Posts: 1,008
Liked 198 Times on 191 Posts


How about using a terminal block rated for the 10 gauge wire, then run appropriate sized wire to your switches, PID, etc. from the block? Looks like you are wiring up a panel for an E-build, so this may be beneficial and keeps the inside of the control box looking clean.


__________________
Put it all in the primary, and let the BeerGods sort it out

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
3-Wire Vs. 4-Wire GFCI BigBobsBrews Electric Brewing 20 09-23-2011 10:56 PM
Wire a switch to a heat stick? tarponteaser Electric Brewing 5 08-29-2011 11:02 PM
Gauge of ground wire GRHunter Electric Brewing 12 05-25-2011 10:26 PM
Any issue using larger gauge wire? adivito Electric Brewing 7 04-11-2011 09:45 PM
Heatstick 12 gauge electrical wire/cord? redalert Electric Brewing 11 01-07-2011 04:09 PM


Forum Jump