Old 08-19-2011, 01:08 AM   #1
McCuckerson
Recipes 
 
Sep 2008
Zebulon, North Carolina
Posts: 655
Liked 11 Times on 9 Posts



I scored 15' of 6awg 3/ground from my electrician neighbor. I only need 3' for the box to outlet connection, so I wanted to use the remaining 12' for a monstor main power cord to the box. I found a 50a plug that I can attach to the cable. The part where I am getting stumped is how to feed this through the control panel. I cannot find any feedthrus or bulkhead that will handle a one inch OD cable. Any suggestions?

Many thanks to Walker for finding a cheap 50a gfi breaker on ebay for me


__________________
"Real men drink their freakin' yeast starters...."

 
Reply With Quote
Old 08-19-2011, 01:14 AM   #2
Ohio-Ed
HBT_LIFETIMESUPPORTER.png
 
Ohio-Ed's Avatar
Recipes 
 
Nov 2008
Posts: 2,067
Liked 20 Times on 19 Posts


Quote:
Originally Posted by McCuckerson View Post
I scored 15' of 6awg 3/ground from my electrician neighbor. I only need 3' for the box to outlet connection, so I wanted to use the remaining 12' for a monstor main power cord to the box. I found a 50a plug that I can attach to the cable. The part where I am getting stumped is how to feed this through the control panel. I cannot find any feedthrus or bulkhead that will handle a one inch OD cable. Any suggestions?

Many thanks to Walker for finding a cheap 50a gfi breaker on ebay for me
Look up "Cord Grips" on McMaster.com

Ed



 
Reply With Quote
Old 08-19-2011, 01:17 AM   #3
McCuckerson
Recipes 
 
Sep 2008
Zebulon, North Carolina
Posts: 655
Liked 11 Times on 9 Posts


Quote:
Originally Posted by Ohio-Ed View Post
Look up "Cord Grips" on McMaster.com

Ed
Thanks ED!

Would HD or Lowes have those? What about those metal ones they sell for conduit?
__________________
"Real men drink their freakin' yeast starters...."

 
Reply With Quote
Old 08-19-2011, 01:24 AM   #4
Ohio-Ed
HBT_LIFETIMESUPPORTER.png
 
Ohio-Ed's Avatar
Recipes 
 
Nov 2008
Posts: 2,067
Liked 20 Times on 19 Posts


Quote:
Originally Posted by McCuckerson View Post
Thanks ED!
You're welcome...
Look for something like:


 
Reply With Quote
Old 08-19-2011, 01:54 AM   #5
McCuckerson
Recipes 
 
Sep 2008
Zebulon, North Carolina
Posts: 655
Liked 11 Times on 9 Posts


Darn that's sexy!
__________________
"Real men drink their freakin' yeast starters...."

 
Reply With Quote
Old 08-19-2011, 01:25 PM   #6
Walker
I use secondaries. :p
HBT_LIFETIMESUPPORTER.png
 
Walker's Avatar
Recipes 
 
Sep 2005
Cary, NC
Posts: 10,987
Liked 101 Times on 89 Posts


McCuckerson....

Is the cord you got a nice, flexible, rubber sheathed power cord (similar to what Ed has coming out of the back of his control panel) or is it fairly inflexible, plastic sheathed wiring meant for running through the walls of a house?

edit: I don't remember finding you a GFCI breaker, but.... you're welcome, I guess.
__________________
Ground Fault Brewing Co.

 
Reply With Quote
Old 08-20-2011, 03:43 AM   #7
McCuckerson
Recipes 
 
Sep 2008
Zebulon, North Carolina
Posts: 655
Liked 11 Times on 9 Posts


Quote:
Originally Posted by Walker View Post
McCuckerson....

Is the cord you got a nice, flexible, rubber sheathed power cord (similar to what Ed has coming out of the back of his control panel) or is it fairly inflexible, plastic sheathed wiring meant for running through the walls of a house?

edit: I don't remember finding you a GFCI breaker, but.... you're welcome, I guess.
Yes its beautiful soft flexible large goodness. It reminds me of the snakes I used to run when I was an in-house roady back in NY.... Anyway, I was asking about a spa panel while complaining about the price of Sqaure D GFI breakers and you found one on ebay for 54 bucks. I just installed it tonight and it works nicely. Ergo you found me a breaker
__________________
"Real men drink their freakin' yeast starters...."

 
Reply With Quote
Old 08-20-2011, 09:54 PM   #8
pvtschultz
Recipes 
 
Feb 2010
New Berlin, Wisconsin
Posts: 457
Liked 8 Times on 8 Posts


McMaster is the first place I look for anything, especially since they deliver next day to me.

http://www.mcmaster.com/#standard-cord-grips/=dpfgnp


__________________
Brewing: Amber Ale, Dunkel
Drinking: Sour Brown, Schlitz...
On Deck: Berliner Weisse, Spotted Cow Clone, CAP...
2016 Gallons Brewed: 10 :(
Gallons Brewed '11-'15: 319

http://www.homebrewtalk.com/f170/pvt...inally-298407/

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Perfect 120V power cord ryclo Electric Brewing 2 05-26-2011 03:58 PM
Power cord help MX1 Electric Brewing 5 02-27-2011 09:58 PM
240V Extension cord question for the gurus jflimbo Electric Brewing 3 01-18-2011 11:24 PM
power switch question doulovebeef Electric Brewing 6 01-06-2011 02:32 AM


Forum Jump