I'm wondering if a switches amperage rating changes as the voltage on it changes.

For example, I have a switch rated at 660V and 10A. I'm wondering if this can handle switching a 240V 30A load (in lieu of a power relay for a 240V 5500W element).

Thanks for any help.

njbabs is offline
Reply With Quote
Old 07-13-2011, 08:58 PM   #2
Feedback Score: 0 reviews
Join Date: Mar 2010
Location: Beer Capital of the World
Posts: 1,063
Liked 12 Times on 11 Posts
Likes Given: 88


Yes, a switch's amp rating does change as the voltage changes, but we can't tell you exactly what the different ratings may be. Only the manufacturer can tell you. IMO, you shouldn't have that kind of current running through a switch. The switch should activate a relay that can handle the current.
"You can do anything you set your mind to when you have vision, determination, and an endless supply of beer."
EarthBound is offline
Reply With Quote
Old 07-13-2011, 10:30 PM   #3
Feedback Score: 0 reviews
Join Date: Aug 2010
Location: South Carolina
Posts: 9
Liked 1 Times on 1 Posts

Default More specific switch ratings

The values provided for amps and voltage are maximums per the manufacturer. It is not uncommon for a switch to have a different rating at a lower voltage, but it should not be assumed. In most cases, if a switch has multiple ratings they will be listed on the switch, or in the manufacturer's documentation.

The thermal stress on a switch is a function of the amps no matter what voltage is applied, so there will be a limit to the amps any switch can carry. Opening and closing creates arcing and mechanical forces that can vary based on voltage and current, and type of load. Stay within the rated value(s) for the switch.
pjohnson is offline
Reply With Quote

Thread Tools

Similar Threads
Thread Thread Starter Forum Replies Last Post
Voltage test on PID/SSR Psych Electric Brewing 5 01-21-2013 07:05 PM
switch terminology bruin_ale Electric Brewing 15 02-17-2011 12:00 AM
control panel on/off switch stevehaun Electric Brewing 3 12-18-2010 04:49 PM
What kind of switch is this? terrazza Electric Brewing 3 12-11-2010 02:37 AM
Simple switch question wilceaser Electric Brewing 2 11-18-2010 05:22 PM

Forum Jump

Newest Threads