Old 05-27-2011, 01:01 AM   #1
CanadianNorth
Recipes 
 
Aug 2009
Newfoundland, Canada
Posts: 117


hey folks,

So I'm in the process of designing a system similiar to Kal's (electricbrewery.com). Not going to be as 'shiny', but eh.

i have two questions:

I installed a 30 amp GFCI breaker in my panel the other day, and hooked it up to a 4-wire dryer plug. Seems all good, voltage tests out dead on at 240, etc. However, when I push the test button the breaker nothing happens. I assumed it would 'pop' , like a regular GFCI plug in a bathroom. Am I missing something here? does there need to be a load on the circuit, or do I have a bum breaker??

As well, I notice that it LOOKS like Kal is using a ground with his 2 240 hot wire to his boil kettle. However, doesn't the GFCI measure the relationship between the neutral and the hot wire? so, don't you need to use the neural instead of ground, to make the GFCI effective?

THANKS!!!!!!!

<<P.S. I am going to have two electrical engineer friends check over my diagram and help with building the unit, I have no intention of killing myself >>


__________________
.
It's just beer man.... they've been doing it for years......

 
Reply With Quote
Old 05-27-2011, 01:15 AM   #2
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,337
Liked 300 Times on 235 Posts


Quote:
Originally Posted by CanadianNorth View Post
...
I installed a 30 amp GFCI breaker in my panel the other day, and hooked it up to a 4-wire dryer plug. Seems all good, voltage tests out dead on at 240, etc. However, when I push the test button the breaker nothing happens.
...
One of 2 things. Either the breaker is not wired properly or it is defective.



 
Reply With Quote
Old 05-27-2011, 02:03 AM   #3
CanadianNorth
Recipes 
 
Aug 2009
Newfoundland, Canada
Posts: 117

thats unfortunate. i'm 99% sure it is wired right
__________________
.
It's just beer man.... they've been doing it for years......

 
Reply With Quote
Old 05-27-2011, 02:13 AM   #4
P-J
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Mar 2010
Charlotte, NC
Posts: 3,337
Liked 300 Times on 235 Posts


Can you sketch a diagram on how you have it wired? Or - snap a picture? This way we can be sure it is set up right. I'm interested in how you have your 'white' wire connection set up to your GFCI breaker input and output.

 
Reply With Quote
Old 05-27-2011, 02:13 AM   #5
BrewMoreBeers
Recipes 
 
Aug 2010
Ohio
Posts: 396
Liked 4 Times on 4 Posts


I have a 60 amp GFI that I recently installed... I just tested it with no load and the test button tripped the breaker as expected.

 
Reply With Quote
Old 05-27-2011, 03:00 AM   #6
acefaser
Recipes 
 
Feb 2011
firestone, co
Posts: 326
Liked 19 Times on 13 Posts


Does the white wire from your 4 wire dryer plug go into the breaker and then the white wire installed in the breaker go to the white terminal bar?
I agree we need to see your wiring diagram.

 
Reply With Quote
Old 05-27-2011, 09:25 AM   #7
CanadianNorth
Recipes 
 
Aug 2009
Newfoundland, Canada
Posts: 117

Quote:
Originally Posted by acefaser View Post
Does the white wire from your 4 wire dryer plug go into the breaker and then the white wire installed in the breaker go to the white terminal bar?
I agree we need to see your wiring diagram.
yes,

The ground from the recepticle goes to the ground in the breaker panel. The hots go to breaker, of course, and the white wire from the recepticle goes into the breaker as well, just above a coiled white wire. That coiled white wire comes out of the breaker and goes in turn to the neutral bar on the panel.
__________________
.
It's just beer man.... they've been doing it for years......

 
Reply With Quote
Old 05-27-2011, 01:14 PM   #8
BrewMoreBeers
Recipes 
 
Aug 2010
Ohio
Posts: 396
Liked 4 Times on 4 Posts


sounds like a bad breaker to me. I assume you have cycled it a few times just to be sure the breaker switch throws properly.



 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
PID and heating element lian82 Electric Brewing 2 05-15-2011 09:01 AM
120v on 220v element? hatrickwah Electric Brewing 34 03-07-2011 09:14 PM
120 v heating element nediver Electric Brewing 6 02-18-2011 02:42 PM
Power/E-stop Wiring for 2 inputs (120V & 220V) thelorax121 Electric Brewing 15 02-03-2011 02:58 AM
Where did you get your heating element? CircleC-Brewer Electric Brewing 20 10-29-2010 02:26 PM


Forum Jump