Johnson Digital Controller Problem - Not holding temp - Home Brew Forums
Home Brew Forums > Home Brewing Beer > Equipment/Sanitation > Johnson Digital Controller Problem - Not holding temp
Cool Brewing Giveaway - Supporting Membership Drive & Discount

Reply
 
Thread Tools
Old 04-12-2011, 02:49 PM   #1
Pugalicious
Recipes 
 
Sep 2010
San Diego, CA
Posts: 64
Liked 8 Times on 6 Posts



So I keep setting my Johnson digital temp controller (attached to a new GE 7.2 cu ft chest freezer) to a specific temperature but it is continually stays 2-5 degrees (f) cooler than what I've set the controller to. For example, right now I have it set at 42 f (I'm not fermenting right now, only serving) but last night the controller read 38. This morning it says 40. For serving, this isn't a big problem but I'm about to brew another batch and I can't have a 5 degree swing in my fermentation temp! That's why I got the freezer and controller in the first place!

FYI, the controller and freezer are both less than four months old.

Am I missing a setting or something on my controller? It seems like it's fairly straight forward.

Thanks in advance for your help guys!

-Jason



 
Reply With Quote
Old 04-12-2011, 03:08 PM   #2
weirdboy
HBT_LIFETIMESUPPORTER.png
Recipes 
 
May 2009
Los Angeles
Posts: 8,090
Liked 474 Times on 382 Posts


Assuming you are talking about the Johnson A419 controller, you probably want to adjust your Differential setting. I believe the factory default is something like 10 degrees F.

So, you can shrink that differential down, but what it going to happen is that it will likely cycle your fridge way more than is healthy for it. If you adjust the differential down, you ought to increase the anti-short cycle delay to make sure it's at least 10-15 minutes.



 
Reply With Quote
Old 04-12-2011, 03:13 PM   #3
Homercidal
Licensed Sensual Massage Therapist.
HBT_MODERATOR.png
 
Homercidal's Avatar
Recipes 
 
Feb 2008
Reed City, MI
Posts: 29,873
Liked 4530 Times on 3055 Posts


Where is the sensor?? I have heard of different locations, but I think having it somewhat insulated, attached to the side of the fermenter, will be the best place.

The fermenting wort cannot change temps as fast as the air outside, due to it's thermal mass. So what you want to do is average your temps outside within a range that promotes the proper temp inside.

Also on my Johnson there were various settings beyond the setpoint. You can have it set to CUT IN or CUT OUT, set or Heating or Cooling and any combination of that. Then you can set the Differential and Offset. And there is an anti-short-circuit feature that tells the device to not cycle any more often than, say, 2 minutes, to help prevent your freezer from killing itself.


I'd have to read the manual again on the settings to remember exactly how it all goes together. I know that after I got mine set up, my heater inside my freezer, kept my temps withing a degree or so for the whole fermentation.

 
Reply With Quote
Old 04-12-2011, 03:45 PM   #4
wildwest450
Registered User
Recipes 
 
Dec 2007
Posts: 8,969
Liked 172 Times on 157 Posts


Just tape the bulb to the side of the fullest keg halfway down. I set mine for a 5 degree diff, from 39f to 44f, giving me a nice 42f pour. Remember the ambient air will be cooler than the actual beer temp. After the freezer cycles it will drop a few degrees cooler than it's set at. The actual beer temp is the only important factor.

_

 
Reply With Quote
Old 04-12-2011, 10:49 PM   #5
Pugalicious
Recipes 
 
Sep 2010
San Diego, CA
Posts: 64
Liked 8 Times on 6 Posts


Thanks guys! Looks like I can tweak the settings to dial it in a bit. Good call on the cycle times. I don't want to kill my freezer. This site and all if you on it are the best!

 
Reply With Quote
Old 04-12-2011, 11:11 PM   #6
Bobby_M
Vendor and Brewer
HBT_SPONSOR.png
 
Bobby_M's Avatar
Recipes 
 
Aug 2006
Whitehouse Station, NJ
Posts: 22,974
Liked 1583 Times on 1020 Posts


If i remember correctly, you have to watch out for the cut in vs. cut out setting. In other words, if you set it to "cut out", it will stop running the compressor at your set point. It will start x number of degrees above the set point where x=offset. If you set it to "cut in", it will run the compressor at the set point and continue to run until x degrees below the set point where x=offset.
__________________
Welcome to BrewHardware.com. I love you.
BIAB Large Mesh False Bottoms and SS HERMS COILS are IN!!
Chugger Pumps, Pump Kits, Camlocks, Sightglasses, Clear USA made Silicone Tubing, RIMS, Electric Install Parts, etc.

 
Reply With Quote
Old 04-13-2011, 09:38 PM   #7
swfc68
Recipes 
 
Jun 2010
san jose
Posts: 23


I also discovered another factor you should try and consider: the thermostat setting on my fridge needs to be tweaked to work well with my controller setting as I found that if I had the fridge set too cold I would overshoot the temp setting on the controller and I would get the results you describe. My controller would cut out when it was supposed to but there was a settling out period afterward where the temperature would drop further. I fixed that by dialing back the fridge setting so it wouldn't run quite so cold.
Once you have looked over all the settings the guys above have mentioned you might want to watch the temperature as it rises back up to see when the controller kicks in. It might actually be cutting out at the temp you set but just overshooting afterward.

-Andy

 
Reply With Quote
Old 04-14-2011, 12:35 PM   #8
Homercidal
Licensed Sensual Massage Therapist.
HBT_MODERATOR.png
 
Homercidal's Avatar
Recipes 
 
Feb 2008
Reed City, MI
Posts: 29,873
Liked 4530 Times on 3055 Posts


Quote:
Originally Posted by swfc68 View Post
I also discovered another factor you should try and consider: the thermostat setting on my fridge needs to be tweaked to work well with my controller setting as I found that if I had the fridge set too cold I would overshoot the temp setting on the controller and I would get the results you describe. My controller would cut out when it was supposed to but there was a settling out period afterward where the temperature would drop further. I fixed that by dialing back the fridge setting so it wouldn't run quite so cold.
Once you have looked over all the settings the guys above have mentioned you might want to watch the temperature as it rises back up to see when the controller kicks in. It might actually be cutting out at the temp you set but just overshooting afterward.

-Andy
You should be turning the fridge/freezer controller all the way down, so that it's always on. The temp controller will turn the fridge/freezer on. At that point the thermostat built into the fridge/freezer does nothing at all.

 
Reply With Quote
Old 04-14-2011, 03:14 PM   #9
Catt22
Recipes 
 
Jan 2009
Posts: 4,998
Liked 68 Times on 61 Posts


Quote:
Originally Posted by Homercidal View Post
You should be turning the fridge/freezer controller all the way down, so that it's always on. The temp controller will turn the fridge/freezer on. At that point the thermostat built into the fridge/freezer does nothing at all.
+1 This is correct. The refrigeration compressors are either on or off. The OEM thermostat is just that; a thermostat, and basically so is the controller. There is nothing to be gained by wiring them in series.

 
Reply With Quote
Old 04-14-2011, 03:29 PM   #10
skibumdc
Recipes 
 
Oct 2008
NoVa
Posts: 215
Liked 6 Times on 6 Posts


+2. Freezer/fridge @ max setting. The controller takes over on when to turn on/off.

Also, just b/c the johnson temp says 38 or 40+ doesn't mean the liquid inside the keg is fluctuating as wildly. 5 gallons is a decent amount of thermal lass to cool/heat so the liquid temp swings are usually only a few degrees.



 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Problem with Johnson Controls A419 Digital Temp Controller mikechambers Equipment/Sanitation 19 03-24-2015 05:35 AM
Manual Johnson controller/freezer problem Nuked99 Equipment/Sanitation 4 06-13-2010 06:53 PM
Johnson A419 Temp Controller Problem trub quaffer Equipment/Sanitation 4 06-13-2010 12:57 AM
Johnson Digital Temperature Controller Keezer Build Pash91 Equipment/Sanitation 12 01-11-2010 01:28 PM
Analog or Digital Johnson Controller? Tankard Equipment/Sanitation 8 08-01-2008 05:44 PM


Forum Jump