Default Honeywell VR8200 power usage

I'm working on a Brutus clone that uses three Honeywell VR8200 gas controls. I'm trying to figure out the amount of power required for the 110VAC->24VAC transformer. Although it will probably never happen, I'd like to have a transformer big enough to run all three gas controllers at the same time. The manual for the VR8200 (found here) claims the following:
Hold-in current: 300mA max
Drop-out current: 250 to 90 mA
Thermostat heat anticipator setting: 0.5A.

Do I need to include the anticipator in overall current consumption, which would basically mean that each VR8200 uses 800mA? If so, then I'm looking for at least 2.4 amps of 24VAC. That would mean a transformer at least 60VA?

I'm pretty sure I know what the heat anticipator does (i.e. account for overshoot), but I don't know how it works, so I don't know how the 0.5A spec applies to the overall power consumption.

Thanks,
BB


blazinbrush is offline
 
Reply With Quote
Old 05-16-2013, 04:07 AM   #2
Namako
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
Namako's Avatar
Recipes 
 
Join Date: Aug 2007
Location: Eagle River, Alaska
Posts: 146
Liked 14 Times on 8 Posts
Likes Given: 22

Default

Humm... I have the same question, and found your post in my search. Did you ever get an answer, or decide on a solution?


__________________
Namako

Indecision... may or may not be my problem... I'm not sure

Primary 1 - Empty
Primary 2 - Empty
Kegged: Empty
Planned: Maerzen, Maibock, and a Kellerbier/Zwickle
Coming Soon: An upgraded Blichmann 20-gallon, Kal-inspired, BCS-controlled, all-electric RIMS-based pico-brewery (by mid-Summer 2015, after the winter thaw, and the NHC, I swear!!)
Namako is offline
 
Reply With Quote
Old 05-16-2013, 09:49 AM   #3
Yellowirenut
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
Yellowirenut's Avatar
Recipes 
 
Join Date: Feb 2013
Location: , Indiana
Posts: 423
Liked 57 Times on 49 Posts
Likes Given: 14

Default

http://www.amazon.com/White-Rodgers-...ER+120V%2F75VA

You should then have plenty of push.
It also has a built in pop fuse.
It is available at many places I was just using amazon for reference.
__________________
~Besancon Brasserie~
Yellowirenut is offline
 
Reply With Quote
Old 05-16-2013, 09:57 AM   #4
Namako
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
Namako's Avatar
Recipes 
 
Join Date: Aug 2007
Location: Eagle River, Alaska
Posts: 146
Liked 14 Times on 8 Posts
Likes Given: 22

Default

I guess my question was more related to whether the heat anticipator setting (0.5A) actually needs to be considered in the calculations, and whether the draw is on whenever the gas valve is open.
__________________
Namako

Indecision... may or may not be my problem... I'm not sure

Primary 1 - Empty
Primary 2 - Empty
Kegged: Empty
Planned: Maerzen, Maibock, and a Kellerbier/Zwickle
Coming Soon: An upgraded Blichmann 20-gallon, Kal-inspired, BCS-controlled, all-electric RIMS-based pico-brewery (by mid-Summer 2015, after the winter thaw, and the NHC, I swear!!)
Namako is offline
 
Reply With Quote
Old 05-16-2013, 01:11 PM   #5
reynolds5520
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Jan 2010
Location: Western Fingerlakes NY
Posts: 284
Liked 37 Times on 30 Posts
Likes Given: 16

Default

Short answer, you need a transformer that can supply at least 300mA per valve at 24 VAC. (A higher amp rating is O.K., the valve will only use the amps it needs.)


Longer answer, the heat anticipator is a resistive heating circuit built into a thermostat. When a furnace is running, the current of the valve runs through the anticipator. The anticipator heats up the thermostat so that it kicks the furnace off before the room air is all the way up to the set point. This helps to prevent overshoot since the furnace blower will keep adding heat to the room, even after the burner is off, until the furnace has cooled to the fan off point.

The listed spec for the heat anticipator setting allows an installer to adjust the anticipator in the thermostat to an initial set point to match the current of the valve. The anticipator may then get further adjusted to eliminate overshoot or short cycle times.

In other words, the heat anticipator spec isn't an additional load in the valve, and isn't important to this application.
reynolds5520 is offline
Stealthcruiser Likes This 
Reply With Quote
Old 05-16-2013, 09:22 PM   #6
Namako
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
Namako's Avatar
Recipes 
 
Join Date: Aug 2007
Location: Eagle River, Alaska
Posts: 146
Liked 14 Times on 8 Posts
Likes Given: 22

Default

Excellent answer!!! Thanks for that!!

If the 0.5A laod is not relevant to our applications, it would appear that most of the 24VAC transformers used in these applications would work to drive 2 or 3 gas valves.

I purchased the Honeywell AT72D transformer that puts out 40AV at 100% power, and I'm hoping it will drive two Honeywell VR8200A gas valves. Looks like it will work just fine, doesn't it?
__________________
Namako

Indecision... may or may not be my problem... I'm not sure

Primary 1 - Empty
Primary 2 - Empty
Kegged: Empty
Planned: Maerzen, Maibock, and a Kellerbier/Zwickle
Coming Soon: An upgraded Blichmann 20-gallon, Kal-inspired, BCS-controlled, all-electric RIMS-based pico-brewery (by mid-Summer 2015, after the winter thaw, and the NHC, I swear!!)
Namako is offline
 
Reply With Quote
Old 05-17-2013, 12:48 PM   #7
blazinbrush
Feedback Score: 0 reviews
Recipes 
 
Join Date: Dec 2010
Location: Springs, CO
Posts: 14
Likes Given: 1

Default

Agreed, nice answer, reynolds! That makes perfect sense.

I ended up not finding the answer to my question so I just bought one big enough to supply the additional 500mA.

For reference, here's the one I bought:
http://www.mpja.com/24V-4A-Center-Ta...nfo/7845%20TR/

It was less expensive than many 40VA transformers I found. I've been using it for a year and half now and it's been doing it's job. It will drive three VR8200 controllers.

BB
blazinbrush is offline
 
Reply With Quote
Old 05-17-2013, 12:54 PM   #8
blazinbrush
Feedback Score: 0 reviews
Recipes 
 
Join Date: Dec 2010
Location: Springs, CO
Posts: 14
Likes Given: 1

Default

Yes, Namako, I would say the AT72D should work just fine. Looks like it's 24VA, which should be plenty to run 2 controllers. Looks like HD also has a Johnstone PF42440 40VA transformer for $12.59.
blazinbrush is offline
 
Reply With Quote
Old 05-17-2013, 02:50 PM   #9
kladue
Senior Member
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Dec 2006
Location: Turner, Oregon, Oregon most of the time now
Posts: 2,318
Liked 50 Times on 45 Posts

Default

For a single VR8200 you should use a 40Va transformer, lower Va transformers will open the valve but will heat up when running for more than a few minutes. For 2 valves a 75Va transformer would be appropriate for both valves operating at the same time.
What appliance builders install is meant for exposed air cooled operation and can be lower Va rated, when installed in a non ventilated control panel you need the higher Va rated transformer that is not as heavily loaded because of limited heat dissipation inside enclosure.


kladue is offline
2
People Like This 
Reply With Quote
Reply


Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Honeywell S8610U splobucket Brew Stands 8 09-02-2012 11:09 PM
low pressure propane Valves (Honeywell) rzarko Brew Stands 6 04-01-2011 08:09 AM
Anyone using AUBER SYL-1512A and Honeywell Y8610U together? Rad-Rabbit Other 2 03-02-2011 04:39 AM
Anyone every try PID on a Honeywell Solenoid? BrianL Brew Stands 0 06-29-2010 04:08 PM
honeywell burner and TC with ASCO valve frolf Brew Stands 6 03-04-2010 12:08 AM


Forum Jump

Newest Threads

LATEST SPONSOR DEALS