Any issue using larger gauge wire? - Home Brew Forums
Register Now For Free!

Home Brew Forums > Home Brewing Beer > Electric Brewing > Any issue using larger gauge wire?

Reply
 
Thread Tools
Old 04-08-2011, 04:33 PM   #1
adivito
Recipes 
 
Feb 2010
Naperville
Posts: 187
Liked 1 Times on 1 Posts



Quick question for the electrical experts out there. Currently I have a 50 amp and a 30 amp receptacle in my garage. I am thinking about swapping where they are located. I have 6 gauge to both receptacles so moving the 50 where I want isnt an issue. Where I want to move the 30 amp receptacle to only has a 6 gauge run. Is there any issues using a larger gauge wire? I dont believe there is, but wanted to double check. Thanks

 
Reply With Quote
Old 04-08-2011, 04:38 PM   #2
Inodoro_Pereyra
Recipes 
 
Feb 2011
Miami, Florida
Posts: 868
Liked 12 Times on 12 Posts


None. Having larger wire will make it work cooler, which is a good thing.
__________________
A pessimist is a well informed optimist.

 
Reply With Quote
Old 04-08-2011, 04:40 PM   #3
adivito
Recipes 
 
Feb 2010
Naperville
Posts: 187
Liked 1 Times on 1 Posts


Thats what I thought, just needed to double check.

 
Reply With Quote
Old 04-08-2011, 04:42 PM   #4
Inodoro_Pereyra
Recipes 
 
Feb 2011
Miami, Florida
Posts: 868
Liked 12 Times on 12 Posts


A #6 will handle 55A @ 60*C. For 30A, it won't even break a sweat.
__________________
A pessimist is a well informed optimist.

 
Reply With Quote
Old 04-11-2011, 02:21 AM   #5
kal
HBT_SUPPORTER.png
 
kal's Avatar
Recipes 
 
Nov 2006
Ottawa, Canada
Posts: 2,548
Liked 364 Times on 234 Posts


The only issue is cost. Typically you use the smallest wire you need to save $$$.

Kal

 
Reply With Quote
Old 04-11-2011, 02:58 AM   #6
samc
Recipes 
 
Aug 2008
Portland OR
Posts: 5,387
Liked 63 Times on 59 Posts


If you can cleanly terminate the wire in the device then it sounds ok. Sometimes trying to fit a too large gauge wire into the wrong device can be difficult. Note that you will usually find a size range on the plug or receptacle.

 
Reply With Quote
Old 04-11-2011, 07:28 PM   #7
smokinghole
Senior Member
HBT_LIFETIMESUPPORTER.png
 
smokinghole's Avatar
Recipes 
 
Nov 2009
Lucid Dream Land
Posts: 2,920
Liked 132 Times on 108 Posts


Not that you'll be dealing with this type of power but it is none the less interesting. I did a tour one day of a satellite tracking facility when I was stationed at Eglin AFB. For the super high voltage stuff they just used copper pipe. I guess the electrical engineers figured out somehow that when you get to have very thick gauge wire the electricity only flows on the outer strands leaving the inner strands unused. So to save money/copper they did copper plumbing pipe for certain circuits.
__________________
Going through life is hard.
Going through life stupid is harder.

 
Reply With Quote
Old 04-11-2011, 09:45 PM   #8
Bernie Brewer
Grouchy Old Fart
HBT_LIFETIMESUPPORTER.png
 
Bernie Brewer's Avatar
Recipes 
 
Feb 2006
Eldorado, WI
Posts: 7,507
Liked 148 Times on 59 Posts


Quote:
Originally Posted by samc View Post
If you can cleanly terminate the wire in the device then it sounds ok. Sometimes trying to fit a too large gauge wire into the wrong device can be difficult. Note that you will usually find a size range on the plug or receptacle.
What he said. As long as the wire will fit, you are golden.

Quote:
Originally Posted by smokinghole View Post
Not that you'll be dealing with this type of power but it is none the less interesting. I did a tour one day of a satellite tracking facility when I was stationed at Eglin AFB. For the super high voltage stuff they just used copper pipe. I guess the electrical engineers figured out somehow that when you get to have very thick gauge wire the electricity only flows on the outer strands leaving the inner strands unused. So to save money/copper they did copper plumbing pipe for certain circuits.
That's called skin effect. The current does flow in the middle too, but there is definitely more on the outside.
__________________
I like to squeeze the nickle until the buffalo craps-mt rob

"Why don't we get drunk and screw?" Jimmy Buffett

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
3 wire 240v GFCI question thelorax121 Electric Brewing 25 03-30-2011 02:31 AM
4 wire conversion kjackbrown Electric Brewing 15 03-06-2011 10:23 PM
RTD extension wire Dave258 Electric Brewing 8 02-03-2011 12:06 PM
Heatstick 12 gauge electrical wire/cord? redalert Electric Brewing 11 01-07-2011 04:09 PM
Dallas one wire and connector question EuBrew Electric Brewing 11 12-21-2010 07:56 PM