Can I build an electric control panel for rims, the rims tube running a 2000W 240V element, and the Boil Kettle running a 5500W 240V element. I will heat water in the kettle, then pump it to my cooler hlt to wait for sparge. Im asking if I make this thing 40 Amp (GFI, SSrs, relays, everything) can I run the Rims and the boil kettle at the same time? That way I can be heating sparge water while my mash is circulating.

It should work, maybe, because total wattage would be at 7500W. So total amps with both elements running at max would be 31.25 amps. Two march pumps would add 2.8 amps, so 34 amps pretty much at max power. That is only a little bit above the 80% of 32 amps, but both pumps would only be running at very few intervals. Would 40 amp service work or should I go ahead and do 50 amp stuff?

 
Reply With Quote
Old 03-31-2011, 03:38 AM   #2
Sparky
 
Sparky's Avatar
Recipes 
 
Nov 2008
Muir Beach, California
Posts: 291
Liked 13 Times on 10 Posts


2,000/240 = 8.3 amps
5,500/240 = ~23 amps
Pumps & bling-bling = ~ 4amps
Total = 35.3amps
A little overcurrent protection (120%) = 42.36 amps

So, your call. My "official-inspection-code" call would be 50 amps, but my (internal) Sparky call is okay on the 40 (despite getting the pending spit-balls on the next posts!).

Now, remember, there is different wire type. So, you may be able to choose a different type (depending upon your circumstance) to get the required amps.

 
Reply With Quote
Old 03-31-2011, 05:05 AM   #3
onthekeg
Recipes 
 
Feb 2009
Posts: 1,786
Liked 83 Times on 65 Posts


I won't answer after Sparky, he is much more qualified than I. I will say that it works for me and leave it at that.

 
Reply With Quote
Old 03-31-2011, 05:24 AM   #4
Inodoro_Pereyra
Recipes 
 
Feb 2011
Miami, Florida
Posts: 868
Liked 12 Times on 12 Posts


Quote:
Originally Posted by Sparky View Post
So, your call. My "official-inspection-code" call would be 50 amps,
I agree with this part. My DIN wired brain calls for a safety margin of 141.42% (√2), which, for 35.3 A, would be 49.92173655 A.
__________________
A pessimist is a well informed optimist.

 
Reply With Quote
Old 03-31-2011, 07:19 AM   #5
milesvdustin
Recipes 
 
Feb 2010
Pensacola, Florida
Posts: 633
Liked 16 Times on 15 Posts


Ok, I appreciate the advice guys. First up, gotta get an enclosure for this thing.

 