Serious brain cramp = seriously stupid question: If you were wiring a 5500W element directly to a 4-wire 220VAC dryer plug, how would you connect it? Hots to the posts, ground to the keggle, what about the neutral?

Also, can 2 separate 120VAC outlets safely power a 220VAC element? Both hots to a terminal, grounds to keggle, same problem with the neutral?
__________________
"Real men drink their freakin' yeast starters...."

 
Reply With Quote
Old 02-26-2011, 09:58 PM   #2
burbelly
Recipes 
 
Feb 2011
miami, fl
Posts: 56
Liked 1 Times on 1 Posts


You don't use it. It is used for 120v. Also, two separate 120v outlets might still be on the same pole. It would still yield 120v. I would make sure that they were linked circuits for safety reasons. If one breaker trips and not the other, you might presume it is safe because the power level seems to have stopped. In reality you would still have 120v flowing and looking for a path. Don't be the path!


 
Reply With Quote
Old 02-26-2011, 10:04 PM   #3
Ohio-Ed
HBT_LIFETIMESUPPORTER.png
 
Ohio-Ed's Avatar
Recipes 
 
Nov 2008
Posts: 2,067
Liked 20 Times on 19 Posts


Quote:
Originally Posted by McCuckerson View Post
Serious brain cramp = seriously stupid question: If you were wiring a 5500W element directly to a 4-wire 220VAC dryer plug, how would you connect it? Hots to the posts, ground to the keggle, what about the neutral?

Also, can 2 separate 120VAC outlets safely power a 220VAC element? Both hots to a terminal, grounds to keggle, same problem with the neutral?
Neutral is not used for 220v.

Simple answer... NO, don't try to power a 220v element with 2, 120v outlets.

Ed

 
Reply With Quote
Old 02-26-2011, 10:05 PM   #4
TheBroonery
Recipes 
 
Feb 2010
Gaithersburg, MD
Posts: 373
Liked 5 Times on 4 Posts


Quote:
Originally Posted by McCuckerson View Post
Also, can 2 separate 120VAC outlets safely power a 220VAC element? Both hots to a terminal, grounds to keggle, same problem with the neutral?
Safely? No. But possibily? It depends.. the hots would need to be coming from separate circuits that are each from one of the 2 bus bars in the main panel. They would also need to be of the same amperage. I don't recommend it.

 
Reply With Quote
Old 02-26-2011, 10:06 PM   #5
Dunerunner
 
Dunerunner's Avatar
Recipes 
 
Jul 2010
Florence, OR
Posts: 795
Liked 15 Times on 14 Posts


The two 120 VAC outlets are probably driven from the same phase of the 220VAC feeding the house. The result would be 120VAC, not what you are looking for. Running a 220V source directly to a heating element of of a 30 or 50 Amp breaker without a disconnect, other than the plug in the outlet is just plain UNSAFE!

This is why there is a National Electric Code. Your boil kettle needs to be grounded (remember ground and Neutral are two different things). The Neutral is provided in the Dryer Circuit because most modern dryers utilize 120VAC controls.

Please, build a control panel, even a rudimentary one to do this.

 
Reply With Quote
Old 02-26-2011, 10:08 PM   #6
McCuckerson
 
McCuckerson's Avatar
Recipes 
 
Sep 2008
Zebulon, North Carolina
Posts: 655
Liked 11 Times on 9 Posts


Thanks guys! I will not try it.
__________________
"Real men drink their freakin' yeast starters...."

 
Reply With Quote
Old 03-09-2011, 11:58 PM   #7
McCuckerson
 
McCuckerson's Avatar
Recipes 
 
Sep 2008
Zebulon, North Carolina
Posts: 655
Liked 11 Times on 9 Posts


Quote:
Originally Posted by Dunerunner View Post
... Please, build a control panel, even a rudimentary one to do this.
Do you guys recommend a disconnect in the control panel? I brew within 6 feet of the breaker panel in my garage and I thought I would use the breaker as the switch.
__________________
"Real men drink their freakin' yeast starters...."

 
Reply With Quote
Old 03-10-2011, 12:17 AM   #8
Monster Mash
Recipes 
 
Apr 2006
Castaic, CA
Posts: 1,323
Liked 93 Times on 72 Posts


Quote:
Originally Posted by McCuckerson View Post
Do you guys recommend a disconnect in the control panel? I brew within 6 feet of the breaker panel in my garage and I thought I would use the breaker as the switch.
Only if it is a GFCI breaker. If it isn't you can replace it with one and you'll be fine. I prefer not to use the breaker to switch the panel on and off though because it wears out the breaker over time.
__________________
My 1BBL Brewery Pics

 
Reply With Quote
Old 03-10-2011, 12:42 AM   #9
DeafSmith
HBT_LIFETIMESUPPORTER.png
 
DeafSmith's Avatar
Recipes 
 
Jan 2009
Richardson, TX
Posts: 1,448
Liked 34 Times on 32 Posts


Quote:
Originally Posted by McCuckerson View Post
Do you guys recommend a disconnect in the control panel? I brew within 6 feet of the breaker panel in my garage and I thought I would use the breaker as the switch.
I use a spa disconnect panel for GFCI protection near the wall receptacle, but on my brew stove, which is some distance away, I have one of these (actually, mine is made by Square D, but is basically the same):
http://www.lowes.com/pd_12587-1318-L...t%3Ddisconnect

This allows me to turn power on and off without wearing out a breaker, and also gives me an easy to reach emergency off switch.

 
Reply With Quote
Old 03-10-2011, 12:44 AM   #10
samc
Recipes 
 
Aug 2008
Portland OR
Posts: 5,387
Liked 63 Times on 59 Posts


Are your arms 6 feet long? If not I'd go with a disconnect/switch within reach of your brewing rig.

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
ASL-51 timer wiring rgrrbt Electric Brewing 25 09-24-2016 11:10 PM
What does your element look like? dboblitt Electric Brewing 4 01-10-2012 04:08 PM
Wiring a Spa Disconnect Chefkeith Electric Brewing 5 12-12-2010 12:31 AM
Simple PID Wiring mcgeebc Electric Brewing 5 12-10-2010 10:06 PM
Pid Wiring Question... Dgonza9 Electric Brewing 11 11-01-2010 02:24 AM


Forum Jump