First of all, I am by no means an expert when it comes to reading wiring diagrams, but when looking at Auber's instructions (Page 6 of 8. Diagram 5.3) it looks to me that they have the neutral line running into the load side of the SSR. This doesn't make any sense to me. Shouldn't it be a hot leg?

http://auberins.com/images/Manual/Ma...sion%203.4.pdf

 
Reply With Quote
Old 02-11-2011, 03:44 PM   #2
stevehaun
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Dec 2006
hudson, wi
Posts: 692
Liked 38 Times on 32 Posts


I think the diagram is wrong. I am not an expert, but I don't think you should ever switch a neutral. Diagram 5.4 looks ok for a 240 vac heater.
Here is a installation manual from watlow that specifically states not to fuse or switch the neutral of a 120 vac circuit.
http://www.watlow.com/downloads/en/m...-0028-0007.pdf

 
Reply With Quote
Old 02-11-2011, 03:45 PM   #3
stevehaun
HBT_LIFETIMESUPPORTER.png
Recipes 
 
Dec 2006
hudson, wi
Posts: 692
Liked 38 Times on 32 Posts


sorry

Reason: duplicate post

 
Reply With Quote
Old 02-11-2011, 05:13 PM   #4
JonW
HBT_LIFETIMESUPPORTER.png
 
JonW's Avatar
Recipes 
 
Dec 2009
Huntington Beach ☼
Posts: 2,010
Liked 247 Times on 154 Posts


I'm no expert either, but even I know that it is against electrical code to have a switched or fused neutral.

SSR terminal #1 should be tied to Auberins terminal #9 and the heater element should be tied to Auberins terminal #10.
__________________
Surf City Brewing (TM)

My Single Tier, 3 Pump, BCS-462, Brutus Build:..... [LINK]
My customized BCS-462 controller web interface:.. [LINK]
My 8 tap, 11 keg, upright Keezer build:.................... [LINK]

 
Reply With Quote
Old 02-11-2011, 05:38 PM   #5
samc
Recipes 
 
Aug 2008
Portland OR
Posts: 5,387
Liked 62 Times on 58 Posts


You should email them. They have always responded quickly to my ???. It would be nice to know what they were thinking when they did those instructions.

 
Reply With Quote
Old 02-11-2011, 05:50 PM   #6
Dunerunner
Recipes 
 
Jul 2010
Florence, OR
Posts: 795
Liked 15 Times on 14 Posts


Quote:
Originally Posted by JonW View Post
I'm no expert either, but even I know that it is against electrical code to have a switched or fused neutral.

SSR terminal #1 should be tied to Auberins terminal #9 and the heater element should be tied to Auberins terminal #10.
This is correct, never switch (break) a neutral. Switch the (HOT) lead in a 120VAC circuit.

In a 240VAC circuit, sepecially to a heater element, both hot leads should be broken. This can be done by controlling the output to the heater element with a 120VAC DPDT relay. 120 to the coil of the relay, 240 single phase through each of the relay contacts to the heater. This electrically isolates the heater element. If you break one leg of the 240, there is still 120VAC to ground available at the heater element just looking for a ground, possibly YOU!!

 
Reply With Quote
Old 02-11-2011, 05:54 PM   #7
passedpawn
Waste Allocation Load Lifter - Earth Class
HBT_ADMIN.png
 
passedpawn's Avatar
Recipes 
 
Apr 2009
☼ Clearwater, FL ☼
Posts: 25,826
Liked 6691 Times on 3955 Posts


Quote:
Originally Posted by HossTheGreat View Post
First of all, I am by no means an expert when it comes to reading wiring diagrams, but when looking at Auber's instructions (Page 6 of 8. Diagram 5.3) it looks to me that they have the neutral line running into the load side of the SSR. This doesn't make any sense to me. Shouldn't it be a hot leg?

http://auberins.com/images/Manual/Ma...sion%203.4.pdf
Looks wrong to me. Don't do it that way. Switch the load line before the heater element.
__________________
- Andrew

 
Reply With Quote
Old 02-11-2011, 06:04 PM   #8
HossTheGreat
Recipes 
 
Mar 2009
Posts: 537
Liked 5 Times on 4 Posts


Good to know that It's the diagram and not me that's wrong. As for electrically isolating the heating element, I'm actually going to run both hot legs through a 30 amp switch. The switch will sit in between the SSR and the outlet feeding the element. When I want to cut power to the element, I will flip the switch off. This way I can be sure that there is absolutely no current being delivered to the element despite what the pid is telling the SSR (or in the event of an SSR failure).

 
Reply With Quote
Old 02-11-2011, 10:09 PM   #9
samc
Recipes 
 
Aug 2008
Portland OR
Posts: 5,387
Liked 62 Times on 58 Posts


Answer from Auber

"Yes the argument is correct. It would be better to switch the hot line. However, since there is a double pole switch at the power entrance, it does not make much difference.
Thank you for pointing out this problem. We will revise the manual."

 
Reply With Quote
Old 02-11-2011, 10:34 PM   #10
HossTheGreat
Recipes 
 
Mar 2009
Posts: 537
Liked 5 Times on 4 Posts


Quote:
Originally Posted by samc View Post
Answer from Auber

"Yes the argument is correct. It would be better to switch the hot line. However, since there is a double pole switch at the power entrance, it does not make much difference.
Thank you for pointing out this problem. We will revise the manual."
Thanks for the info...I was planning on emailing them myself tonight.

 
Reply With Quote


Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need help with my electrical diagram!!! Gabrew Electric Brewing 208 03-05-2011 02:10 AM
Wiring diagram workable? Control box TheSlash Electric Brewing 2 02-10-2011 08:54 PM
Electric diagram w/ RIMS snail Electric Brewing 13 11-28-2010 03:00 AM
Final Electrical diagram, maybe??????????? EuBrew Electric Brewing 12 11-01-2010 10:16 PM
Wiring diagram advice frank551 Electric Brewing 6 10-19-2010 01:56 PM


Forum Jump