I know there is quite a bit of info regarding this topic that has already been discussed. However, after searching I still have a few unanswered questions.

I am looking to build an extension cord to run from a 30amp 3 prong dryer outlet to a 5500w boil kettle. My question is in regards to wire size. Due to being a renter, I am unable to add a closer outlet and am faced with a distance of 60 feet to the outlet. I am aware that NEC code says 10 gauge wire is sufficient for the 30amp circuit. I also realize that at 60 feet there will be a descent voltage drop. If I understand correctly the NEC does not care anything about voltage drop only carrying capacity. If I use 10 gauge as opposed to 8 gauge is the voltage drop my only concern. I can live with some power loss at the element as 5500w is large enough lo lose a bit and still provide plenty for a vigorous boil.

Most importantly I want to do this safely but if possible stick with 10 gauge soow wire as the 8 gauge soow is about twice the price per foot. If I am correct the only downfall with the 10 gauge is the loss in voltage not a safety issue. If this is incorrect logic please correct me.

Reply With Quote
Old 01-18-2011, 10:00 PM   #2
Dec 2010
Bellevue, NE
Posts: 183
Liked 2 Times on 2 Posts

I don't have any trouble running a similar setup
Kegged: Amarillo Ale, Edwort's Apfelwein, Golden Dragon, 1554, 888 RIS

Reply With Quote
Old 01-18-2011, 10:18 PM   #3
Dec 2010
Denver, Colorado
Posts: 7

I run pretty much the exact same setup, except my cable run is a tad shorter. I register the same voltage at the end of the cable as I do at the outlet.

I feel you though, that 10/4 cable is freakin expensive for the plyable extension cable type.

Reply With Quote
Old 01-18-2011, 11:24 PM   #4
ScubaSteve's Avatar
May 2007
New Bern, NC
Posts: 3,677
Liked 83 Times on 57 Posts

10 awg will carry 30A fine. But not 50A. And don't use romex! (looks like you know that...just sayin')....

Reply With Quote
Thread Tools

Similar Threads
Thread Thread Starter Forum Replies Last Post
12gauge extension cord rated at only 15Amps Scut_Monkey Electric Brewing 23 04-25-2011 06:01 PM
extension cord to fridge? kornbread Electric Brewing 4 12-17-2010 01:09 PM
Range extension cord>outlet>inline gfi snail Electric Brewing 4 12-13-2010 04:22 PM
Need Help from the Electrical Gurus! akthor Electric Brewing 0 12-06-2010 03:44 PM
Strange issue with 240v legs. 120v on both, no 240v Brewmoor Electric Brewing 5 12-03-2010 07:15 PM

Forum Jump