It's a 40amp. It should work. The challenge with a panel mount breaker floating free in 3rd party box is how to connect the line side conductors, insulate those connections, and ultimately secure it to the panel. I wouldn't say it's impossible, just challenging (and for sure the code nazis would be all over that.
__________________
Welcome to BrewHardware.com. I love you.
New Stirplates are IN!
Chugger Pumps, Pump Kits, Camlocks, Sightglasses, Clear USA made Silicone Tubing, RIMS, Electric Install Parts, etc.

 
Reply With Quote
Old 12-23-2010, 02:20 AM   #22
ScubaSteve
HBT_SUPPORTER.png
 
ScubaSteve's Avatar
Recipes 
 
May 2007
, DC
Posts: 3,680
Liked 84 Times on 58 Posts


Well, this particular multi 9 model would go inside my toolbox controller....properly insulated and most likely epoxied to the floor. Duh, I see now that it's 40A. What I can't figure out...even from the MANUFACTURER'S INSTRUCTIONS, is, "where's the neutral pigtail?" i.e. how will the GFCI work if it is only hooked to both hots? In the 2P configuration, it looks as if both hots are to be connected to the line in, and in the same way the load outs are connected.....so only 4 holes...not 5? Sorry for my ignorance, wasn't aware of this type of breaker.....

 
Reply With Quote
Old 12-23-2010, 02:37 AM   #23
ClaudiusB
Recipes 
 
Dec 2007
El Paso, Texas
Posts: 1,355
Liked 101 Times on 78 Posts


Quote:
Originally Posted by ScubaSteve View Post
What about THIS one? Looks like it's a DIN rail mountable breaker without the funky bussbar connectors. Should be able to be installed inline....but I can't tell the rating. The info makes it look like it's multi-use?
It will work as a 40 A ground fault protection device only, its not a circuit breaker.
There is no thermal or magnetic overcurrent protection.
Enlarge the picture and look at the symbols.


Cheers,
ClaudiusB

 
Reply With Quote
Old 12-23-2010, 03:19 AM   #24
ScubaSteve
HBT_SUPPORTER.png
 
ScubaSteve's Avatar
Recipes 
 
May 2007
, DC
Posts: 3,680
Liked 84 Times on 58 Posts


Thanks, Claudius....I finally realized I could zoom Ground fault is what's important, as any outlet I plug into will have overcurrent protection at the main panel. As long as I don't plug into a >30A circuit (plug won't fit anyway).....it should be fine.

Anyone want to weigh in on mA sensitivities? Is 30 milli-amperes too high? I thought most GFCI's would trip around 4-6 mA......?

 
Reply With Quote
Old 12-23-2010, 03:55 AM   #25
ClaudiusB
Recipes 
 
Dec 2007
El Paso, Texas
Posts: 1,355
Liked 101 Times on 78 Posts


Quote:
Originally Posted by ScubaSteve View Post
Thanks, Claudius....I finally realized I could zoom Ground fault is what's important, as any outlet I plug into will have overcurrent protection at the main panel. As long as I don't plug into a >30A circuit (plug won't fit anyway).....it should be fine.

Anyone want to weigh in on mA sensitivities? Is 30 milli-amperes too high? I thought most GFCI's would trip around 4-6 mA......?
What does the data sheet show for a non IEC panel mount GFI?
The circuit will start to trip at 26mA.

IEC standard
1.1 Electric shock
An electric shock is the pathophysiological effect of an electric current through the human body.
Its passage affects essentially the muscular, circulatory and respiratory functions and sometimes results in serious burns.
The degree of danger for the victim is a function of the magnitude of the current, the parts of the body through which the current passes, and the duration of current flow.
IEC publication 60479-1 updated in 2005 defines four zones of current-magnitude/
time-duration, in each of which the pathophysiological effects are described (see Fig F1). Any person coming into contact with live metal risks an electric shock.
Curve C1 shows that when a current greater than 30 mA passes through a human being from one hand to feet, the person concerned is likely to be killed, unless the current is interrupted in a relatively short time.
The point 500 ms/100 mA close to the curve C1 corresponds to a probability of heart fibrillation of the order of 0.14%.
The protection of persons against electric shock in LV installations must be provided in conformity with appropriate national standards and statutory regulations, codes of practice, official guides and circulars, etc. Relevant IEC standards include: IEC 60364 series, IEC 60479 series, IEC 60755, IEC 61008 series, IEC 61009 series and IEC 60947-2.

If you need the curve I will make a JPEG pic.

Cheers,
ClaudiusB

 
Reply With Quote
Old 12-23-2010, 04:53 AM   #26
ClaudiusB
Recipes 
 
Dec 2007
El Paso, Texas
Posts: 1,355
Liked 101 Times on 78 Posts


Read this info

GENERAL ELECTRIC
Install GFCI Circuit Breakers on Grounded Power Supply Circuits only
CLASS A
1) To minimize false tripping: Do not connect to swimming pool equipment installed before adoption of the 1965 National Electrical Code.
2) 30 milliampere ground fault equipment protection circuit breakers (yellow TEST button) are NOT intended, and are NOT suitable, for ground fault protection of personnel coming in contact with electrical parts. Use 5 milliampere GFCI circuit breakers for this application.
3) 5 milliampere GFCI circuit breakers (red TEST button) and 30 milliampere ground fault equipment protection circuit breakers (yellow TEST button) are intended for use on 120Vac circuits (1-pole circuit breaker) or 120/240 or 208Y/120Vac (2-pole circuit breaker), 60 Hz circuits onl

 
Reply With Quote
Old 12-23-2010, 07:14 PM   #27
ScubaSteve
HBT_SUPPORTER.png
 
ScubaSteve's Avatar
Recipes 
 
May 2007
, DC
Posts: 3,680
Liked 84 Times on 58 Posts


Great info! I can be stubborn at times, but in this case there is no room for error or cheaper components! Gonna keep an eye out for a cable.....plus I'll probably get a look in the panel to see exactly what breakers I have......

 
Reply With Quote
Old 12-24-2010, 09:28 PM   #28
sjvicker
Recipes 
 
May 2008
Des Moines, WA
Posts: 101

If you have a Cutler Hammer BR series you can pick up a 50AMP hot tub sub panel, yank the GFCI out of it and put it in your main panel for $80 (Lowes). Since it sounds like you want to keep everything portable why not wire a 50amp breaker from your main panel down to a suitable outlet, put the GFCI hot tub sub panel in your portable control box and build a 6AWG extension cord to connect the two?

I have a Cutler Hammer CH series and the cheapest 50amp GFCI I could find was over $150 so I'm going from my main box to the BR series hot tub sub panel GFCI and from there to another sub panel with a 15amp and two 30amp breakers. I'll then go from the subsub panel to a simple control box. I already have about 20' of 6-3 wire and need to go about 30' to the brew area so this option was the best on my wallet when factoring in all costs.
__________________
Strait Jacket Brewing

 
Reply With Quote
Old 12-27-2010, 05:57 PM   #29
ScubaSteve
HBT_SUPPORTER.png
 
ScubaSteve's Avatar
Recipes 
 
May 2007
, DC
Posts: 3,680
Liked 84 Times on 58 Posts


Unfortunately, I also have the Cutler Hammer CH series in my main panel. I have a $60 gift card for Lowe's, so I'm leaning in the direction of getting a spa panel and a few feet of 6ga wire. I'd like to install a receptacle next to it and keep it putting out 50A in case I get a welder....so then I'll need a 50A range cord and a 30A breaker inside my toolbox control panel.

On another note, anyone seen or use one of THESE DONUT STYLE GFCI'S? Looks like you need a contactor as well.....

 
Reply With Quote
Old 12-29-2010, 01:38 AM   #30
wyzazz
Recipes 
 
Aug 2009
Atwater, OH
Posts: 4,316
Liked 56 Times on 53 Posts


Would this work for a GFI Cord? It's only got 3 wires...
__________________
Quote:
Originally Posted by Revvy View Post
And I'd like to see my 1.080 beers ready from grain to glass in a week, and served to me by red-headed twin penthouse pets wearing garter belts and fishnet stockings, with Irish accents, calling me "master luv gun," but we can't always get what we want can we? :)

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI keeps blowing Cybershadow Electric Brewing 51 12-22-2010 06:14 PM
my take on covering the heating element connections Broncobum Electric Brewing 30 11-05-2010 06:25 PM
Show me your waterproof heatstick connections CoalCracker Electric Brewing 3 10-27-2010 08:42 PM
GFCI wiring? ExHempKnight Electric Brewing 5 10-23-2010 08:53 PM
Multiple GFCI wiring question Cpt_Kirks Electric Brewing 8 10-20-2010 03:22 PM


Forum Jump