Old 10-22-2010, 02:09 AM   #1
Beer Maniac
SenorWanderer's Avatar
Aug 2007
Posts: 592
Liked 3 Times on 3 Posts

I just recently noticed a 240v 3 prong dryer outlet in my friends garage where I brew. It was hiding behind some scrap 2x4s. I've been planning a small HERMS upgrade to my HLT but was planning on using only a 120v element. Now that I've found this outlet my plans are changing for the better! Question is, how do I determine how much juice is available at the outlet? I'm not very experienced with electrical, but I understand the basics (120 v. 240, proper gauge wire for the amps, how to wire an outlet, how to ground a circuit, etc). I know that I could just go look at the panel, and I'll try that, but I'd like to know which type of metering tool I can pick up at home depot will tell me what I need to know.

Any suggestions, along with tips on how to use properly and safely, would be greatly appreciated!

Reply With Quote
Old 10-22-2010, 02:13 AM   #2
Dec 2009
North Pole, Alaska
Posts: 1,809
Liked 41 Times on 37 Posts

It will give you all the amperage it can until the breaker trips or the wire melts. Your power is limited by the breaker which should be sized to protect the wiring. I don't understand why you need to measure it. Just look at the breaker.
10 gallon electric system
Stovetop 110v single vessel 5 gallon system

Primary: saison
Secondary: nada
Conditioning: macaroon stout
Drinking: store bought

Reply With Quote
Old 10-22-2010, 02:34 AM   #3
Ohio-Ed's Avatar
Nov 2008
Posts: 2,067
Liked 20 Times on 19 Posts

Measurement tools will measure how much current is being drawn (or used) at a point in time, but not how much "could be" used.

As Klyph said... the breaker size is the answer you are looking for.

Reply With Quote
Old 10-22-2010, 04:05 AM   #4
DeafSmith's Avatar
Jan 2009
Richardson, TX
Posts: 1,448
Liked 34 Times on 32 Posts

If it's a dryer outlet, it's likely 30 amps. The plug configuration is one indicator (see if it is a NEMA 10-30, for example).

But really, the only way to know is to look at the breaker - no metering tool needed.

Reply With Quote
Old 10-22-2010, 09:01 PM   #5
kal's Avatar
Nov 2006
Ottawa, Canada
Posts: 2,534
Liked 355 Times on 228 Posts

I would also confirm that the wiring coming out of the breaker panel is indeed 10/3 with ground.


Reply With Quote
Old 10-22-2010, 09:20 PM   #6
Aug 2010
Maryland, Maryland
Posts: 120

Really though you already know "how much power" you have.

~240v -> ~30amps -> ~7200 watts (All maximum values for the circuit)

If for some reason you feel the need to get a multi-meter be very sure you know what you're doing. Sticking probes in any outlet or main box without knowing what you're doing can be lethal.

Ready: Nothing - All Gone :(
Bottled/Aging: Cherry Wheat
Primary: Nothing
Up Next: Irish Red Ale | Almost Flying Dog Pale Ale

My Threads:
Newbie's Fermentation Chiller
Space-Saving "Brew Closet"

Spoke'n Beer Blog - Beer and Bikes

Reply With Quote
Old 10-22-2010, 10:37 PM   #7
Vendor and Brewer
Bobby_M's Avatar
Aug 2006
Whitehouse Station, NJ
Posts: 23,287
Liked 1736 Times on 1101 Posts

I'll suggest a different route. First find out if there's a 2pole 30a breaker in the panel. Then find out if there's another electric dryer in the house, maybe in the basement, that is still in use. It's possible they just decided to move the dryer to another location and abandon the outlet in the garage. In that case, it may be disconnected at the panel.
Welcome to I love you.
Corny Keg Dry Hop Canisters $26.50 for limited time
Chugger Pumps, Pump Kits, Camlocks, Sightglasses, Clear USA made Silicone Tubing, RIMS, Electric Install Parts, etc.

Reply With Quote
Old 10-24-2010, 03:30 PM   #8
Dec 2009
Natick, USA
Posts: 27

The dryer and the garage outlet could be wired to the same breaker too. In that case, no brewing on laundry day

Reply With Quote
Old 10-24-2010, 03:48 PM   #9
Mar 2010
Posts: 998
Liked 17 Times on 16 Posts

Originally Posted by jlag View Post
The dryer and the garage outlet could be wired to the same breaker too. In that case, no brewing on laundry day
wrong! it's no laundry on brewing day

Reply With Quote
Old 02-08-2011, 04:57 AM   #10
Senior Member
petey_c's Avatar
Jun 2010
Miller Place, NY (Long Island)
Posts: 1,358
Liked 92 Times on 79 Posts

I know it's been awhile for this, but just thought I'd add something; 30/40 gal. hot water heaters, small A/C condensors, and other things can also be run on 2P30A breakers.

Reply With Quote