OK, can someone settle this for me. I have heard two stories about using a 240 VAC heating element with 110 VAC. Common sense says halving the power should give you half the wattage out of the heating element. However, I have also been told that it is not linear. If it isn't linear, is there a formula to figure out how many watts you will end up with - for instance: if I want 1800 watts with 110 VAC out of the heating element, could I use a 3500 Watt 240 VAC; or, would I need to use say a 4500 watt 240 VAC element?

Hope that made sense.


Islandboy85 is offline
 
Reply With Quote
Old 09-25-2010, 02:21 AM   #2
DeafSmith
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
DeafSmith's Avatar
Recipes 
 
Join Date: Jan 2009
Location: Richardson, TX
Posts: 1,448
Liked 33 Times on 31 Posts
Likes Given: 9

Default

Power = the square of the voltage applied divided by the resistance of the element. The resistance of the element can be determined by dividing the square of the rated voltage by the power rating. The net result is that at 120 volts (1/2 the voltage) a 240 volt element will only put out 1/4 of the power.
To get 1800 watts at 120 VAC you would need a 7200 watt, 240V element, if they even make one like that, which I doubt.

Taking the 3500 watt, 240V element as an example, the element resistance is (240*240)/3500 = 16.46 ohms. With 120 volts applied, the power is (120*120)/16.46 = 875 watts, or 1/4 the rated value.

A 4500 watt element would only develop 1125 watts at 120 V.

EDIT: Forgot to mention - if you want 1800 watts at 120V, why not just use a 2000 watt element that is rated for 120 volts? You would need a 20 amp circuit for that, but you could use a 1500 watt, 120V element on a standard 15 amp circuit.


DeafSmith is offline
 
Reply With Quote
Old 09-25-2010, 12:58 PM   #3
Islandboy85
Feedback Score: 0 reviews
Recipes 
 
Join Date: Nov 2009
Location: Dallas, Texas
Posts: 681
Liked 12 Times on 10 Posts
Likes Given: 1

Default

Quote:
Originally Posted by DeafSmith View Post
EDIT: Forgot to mention - if you want 1800 watts at 120V, why not just use a 2000 watt element that is rated for 120 volts? You would need a 20 amp circuit for that, but you could use a 1500 watt, 120V element on a standard 15 amp circuit.
Well, I only have 15 amp breakers in my apartment right now. After I get married in April I will have 240 out of her dryer outlets at her apartment...I think they're GFCI...
Islandboy85 is offline
 
Reply With Quote
Old 10-04-2010, 08:15 PM   #4
Islandboy85
Feedback Score: 0 reviews
Recipes 
 
Join Date: Nov 2009
Location: Dallas, Texas
Posts: 681
Liked 12 Times on 10 Posts
Likes Given: 1

Default

Quote:
Originally Posted by DeafSmith View Post
Power = the square of the voltage applied divided by the resistance of the element. The resistance of the element can be determined by dividing the square of the rated voltage by the power rating. The net result is that at 120 volts (1/2 the voltage) a 240 volt element will only put out 1/4 of the power.
To get 1800 watts at 120 VAC you would need a 7200 watt, 240V element, if they even make one like that, which I doubt.

Taking the 3500 watt, 240V element as an example, the element resistance is (240*240)/3500 = 16.46 ohms. With 120 volts applied, the power is (120*120)/16.46 = 875 watts, or 1/4 the rated value.

A 4500 watt element would only develop 1125 watts at 120 V.

EDIT: Forgot to mention - if you want 1800 watts at 120V, why not just use a 2000 watt element that is rated for 120 volts? You would need a 20 amp circuit for that, but you could use a 1500 watt, 120V element on a standard 15 amp circuit.
So, I think I WILL end up wiring it for 240 vac. How do I make it GFCI?
Islandboy85 is offline
 
Reply With Quote
Old 10-04-2010, 08:26 PM   #5
DeafSmith
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
DeafSmith's Avatar
Recipes 
 
Join Date: Jan 2009
Location: Richardson, TX
Posts: 1,448
Liked 33 Times on 31 Posts
Likes Given: 9

Default

A lot of people put a spa disconnect panel in line - you can get one of these with a 50 amp 240V GFCI breaker in a metal box for about $50 from Home Depot. You will need to use at least 10 gauge wire, and depending on the length of the power cable you need, it may well end up costing more than the spa panel. And then there are the 240V plugs and receptacles to buy. So count on spending at least $150 or more.
DeafSmith is offline
 
Reply With Quote
Old 10-04-2010, 08:37 PM   #6
Islandboy85
Feedback Score: 0 reviews
Recipes 
 
Join Date: Nov 2009
Location: Dallas, Texas
Posts: 681
Liked 12 Times on 10 Posts
Likes Given: 1

Default

Thanks Deafsmith.
Islandboy85 is offline
 
Reply With Quote
Old 10-17-2010, 01:45 AM   #7
Islandboy85
Feedback Score: 0 reviews
Recipes 
 
Join Date: Nov 2009
Location: Dallas, Texas
Posts: 681
Liked 12 Times on 10 Posts
Likes Given: 1

Default

Quote:
Originally Posted by DeafSmith View Post
A lot of people put a spa disconnect panel in line - you can get one of these with a 50 amp 240V GFCI breaker in a metal box for about $50 from Home Depot. You will need to use at least 10 gauge wire, and depending on the length of the power cable you need, it may well end up costing more than the spa panel. And then there are the 240V plugs and receptacles to buy. So count on spending at least $150 or more.
This is all I could find...I don't think it's right since it's three times what you estimated. http://www.homedepot.com/h_d1/N-5yc1...atalogId=10053
Islandboy85 is offline
 
Reply With Quote
Old 10-17-2010, 02:10 AM   #8
Ohio-Ed
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
Ohio-Ed's Avatar
Recipes 
 
Join Date: Nov 2008
Posts: 2,072
Liked 20 Times on 19 Posts

Default

Quote:
Originally Posted by Islandboy85 View Post
This is all I could find...I don't think it's right since it's three times what you estimated. http://www.homedepot.com/h_d1/N-5yc1...atalogId=10053
I think he was talking about something like this:
http://www.homedepot.com/h_d1/N-5yc1...atalogId=10053
Ohio-Ed is offline
 
Reply With Quote
Old 10-17-2010, 04:50 AM   #9
DeafSmith
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
DeafSmith's Avatar
Recipes 
 
Join Date: Jan 2009
Location: Richardson, TX
Posts: 1,448
Liked 33 Times on 31 Posts
Likes Given: 9

Default

Quote:
Originally Posted by Ohio-Ed View Post

Yes, that last one for $49 is the one.


DeafSmith is offline
 
Reply With Quote
Reply


Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
PWM control of heating elements chunk1227 Brew Stands 25 02-10-2012 08:41 PM
Help with Trying to install heating elements in Electric HLT albysurfin Kettles, Mash Tuns, & Hot Liquor Tanks 2 07-27-2010 05:45 AM
Heating Elements and GFCI CorgiBrew Kettles, Mash Tuns, & Hot Liquor Tanks 96 03-19-2010 06:36 PM
Heating elements... Cyan Brew Stands 61 02-16-2010 03:29 PM
Heating Elements? RoosterCogburn Brew Stands 51 01-26-2009 02:43 AM


Forum Jump

Newest Threads

LATEST SPONSOR DEALS