I can't get this figured out for the life of me so I'm asking for help. Hoping someone has a trouble shooting idea.

Short story, I have a LOVE Tss2-2100 controller with two temperature probes that I want to control two cooling areas. probe one is controlling the freezer compressor no problem. I now added a AC cabinet fan to blow air into the other side of the side by side with a probe to cool that side independently (by blowing cold freezer air over)

I have it all set at

Mode ON OFF2 (On2)
Output 1 works as in independent ON/OFF control (Figure 1 and 2),
but output 2 works as follows:
Relay 2 with c2=dir.
Temperature of probe 2 >= SP2+r2 -->relay 2 ON
Temperature of probe 2 <= SP2 -->relay 2 OFF

SP1: 42
SP2: 42 (or whatever i want)
ro: ind
r1: 2
r2: 2
r8 - on2
c0: 0 for now
c1- dir
c2 - dir
P5 - 2

I can't think of anything to change on the love.

ive tried splicing power off the fridge and by using a power cord and the fan will turn on fine if i don't connect the love. I switch it by running hot wire to 10 and then running switched wire from 11 back to other end of hot on AC fan. The other fan wire goes to neutral (either fridge neutral or other side of plug in)

What am I missing? I've also tried switching probes to see if one was defective and the second one works perfectly.

115V AC fan. 115VAC love


 
Reply With Quote
Old 08-12-2010, 08:16 AM   #2
rockytoptim
HBT_SUPPORTER.png
 
rockytoptim's Avatar
Recipes 
 
May 2009
Livonia, MI
Posts: 774
Liked 95 Times on 76 Posts


Will the AC fan work if you have it hooked up to relay 1 of the love controller? What is the amp pull of the fan you are using. The relay 2 has lower amp draw on the love than relay 1. I have a love controller but have never used the 2nd relay.
__________________
On Tap: Bee Cave Robust Porter
On Tap: Bee Cave OktoberFest
On Tap: Bee Cave Kolsch
Primary: None
Up next: ????

 
Reply With Quote
Old 08-12-2010, 01:25 PM   #3
ArtVandelay
Recipes 
 
Dec 2009
Milwaukee
Posts: 374
Liked 14 Times on 8 Posts


I haven't tried switching to relay one yet. That was next on my list of things to try.

AC fan specs
Rated Voltage: 115 V
Input Power: 11 W
Connection: Terminal
Frequency: 60 Hz
Rated Current: 0.12 A

Looking online it looks like relay 1 is 16 amps and relay 2 is 8 amps, but with the AC fan I'm still way under.


 
Reply With Quote
Old 08-12-2010, 07:00 PM   #4
ArtVandelay
Recipes 
 
Dec 2009
Milwaukee
Posts: 374
Liked 14 Times on 8 Posts


I'll fiddle around with it some more tonight. Anyone else have any other ideas I can try? Common mistakes?

This would be easier if I was completely overwhelmed but I'm just off on one little thing and can't figure it out.


 
Reply With Quote
Old 08-13-2010, 12:05 AM   #5
ArtVandelay
Recipes 
 
Dec 2009
Milwaukee
Posts: 374
Liked 14 Times on 8 Posts


Alright, I'm not getting much response so I'm just going to keep posting.

Tried switching fan over to 1 after work and that did the trick getting the fan to turn on off. I even switched around temperature probes and both are still working fine. However, now the compressor won't turn on, just like the fan didn't when run from 2. The only thing I can think is I'm missing on key setting on the LOVE. I looked it over and everything seemed right. Even had P5 set to 2

 
Reply With Quote
Old 08-13-2010, 01:07 AM   #6
ArtVandelay
Recipes 
 
Dec 2009
Milwaukee
Posts: 374
Liked 14 Times on 8 Posts


switched it all back. fan that was working on relay 1 is not working on 2 now again. Checked between hot and switch hot with volt meter and I get nothing (this is when it should be switched on).

I think I have a faulty LOVE switch 2.

Everything here looks right to me..

sp1: 42
sp2: 42
ro: ind
r1: 2
r2:2

r3: 1
r4: -99.9
r5: -99.9
r6: -99.9
r7: 99.9
r8: on2
A0: 0.1
A1: 99.9
A2: 99.9
A3: 99.9
A4: 99.9
A5: 18
A6: AHL
A7:AHL
c0: 0
c1: dir
c2: dir

c3: oPn
c4: oPn
P0: oF
P1: 0
P1: 0
P2: 0
P3: yes
P4: sd1
P5: 2
HO: 0
H2: dir-------? don't really understand these but don't think they are important
H3: dir-------? don't really understand these but don't think they are important
H4: 0
H5: 0


 
Reply With Quote
Old 08-13-2010, 01:23 AM   #7
rockytoptim
HBT_SUPPORTER.png
 
rockytoptim's Avatar
Recipes 
 
May 2009
Livonia, MI
Posts: 774
Liked 95 Times on 76 Posts


Everything looks like you got it set right. If you got the Love from Dwyer I would gives them a call maybe they can help you trouble shoot or just ask for and exchange.

H2 & H3 either turns the led indicator to on when relay is on or you can have it inverse so its on when relay is off. This won't effect how the relay actually works.
__________________
On Tap: Bee Cave Robust Porter
On Tap: Bee Cave OktoberFest
On Tap: Bee Cave Kolsch
Primary: None
Up next: ????

ArtVandelay Likes This 
Reply With Quote
Old 08-13-2010, 01:38 AM   #8
ArtVandelay
Recipes 
 
Dec 2009
Milwaukee
Posts: 374
Liked 14 Times on 8 Posts


Thanks. I appreciate the help. I've come to the same conclusion as well. I just sent dwyer an email about this so hopefully I don't have to fight too hard for an exchange.

 
Reply With Quote
Old 08-13-2010, 01:47 AM   #9
rockytoptim
HBT_SUPPORTER.png
 
rockytoptim's Avatar
Recipes 
 
May 2009
Livonia, MI
Posts: 774
Liked 95 Times on 76 Posts


Love the user name by the way. Let us know if Dwyer takes care of you and if this resolves the problem.
__________________
On Tap: Bee Cave Robust Porter
On Tap: Bee Cave OktoberFest
On Tap: Bee Cave Kolsch
Primary: None
Up next: ????

 
Reply With Quote
Old 08-13-2010, 03:15 AM   #10
ArtVandelay
Recipes 
 
Dec 2009
Milwaukee
Posts: 374
Liked 14 Times on 8 Posts


Thanks. I try to use that name on all the boards/forums I go to but it's usually taken. Got lucky here.

I just hope they will send me a new one before I have to return the faulty one. It works well enough now as a single stage controller to at least keep my kegerator functional. I can't go a week without it.

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help wiring a Love Controller theron Fermenters 9 04-02-2011 05:01 PM
Wiring a Love controller help. FDillon00 Fermenters 5 07-20-2010 12:34 PM
Love Controller Help jcalisi Fermenters 6 06-05-2010 01:40 AM
Which Love controller is better tfrost12 Kegerators & Keezers 6 05-26-2010 04:20 PM
Which Love Controller? smoes Fermenters 5 04-22-2009 12:59 PM


Forum Jump