Ok, so I am not very technically inclined. I want to see if my idea makes sense, and more importantly, if I am risking starting a fire.

Following the "heatstick=awesome" thread design, I run into the huge problem that the house I brew in does not have 20A outlets (available for brewing), and I'm not confident in my ability to attempt to mess around with the house wiring.

So, I know from the thread that regular home outlets can handle heating elements up to 1500W at best. I know that won't produce enough to boil -- my goal is really just to help accellerate the boiling in conjunction with the stove.

Ok, enough blabbing. Here's my idea.

Could I run two 1500W heating elements through a surge-protected power strip (obviously plugged into one outlet) without danger and/or risk of fire?

 
Reply With Quote
Old 03-20-2010, 01:44 AM   #2
willynilly
Registered User
Recipes 
 
Feb 2010
Avon
Posts: 728
Liked 8 Times on 7 Posts


You plan to run 25A through a 15A outlet? The breaker will stop you from doing that. You will have 0 watts. Not much danger of fire, when there is no power to the outlet.

 
Reply With Quote
Old 03-20-2010, 01:47 AM   #3
kmack747
 
kmack747's Avatar
Recipes 
 
Jan 2010
Bad Axe, Michigan
Posts: 154

In short NO. Each element will pull 13 amps. Most household outlets are 15 amps so two elements will be way more than an outlet can handle. Power strips can only handle 15 amps.

 
Reply With Quote
Old 03-20-2010, 01:50 AM   #4
ReverseApacheMaster
Registered User
Recipes 
 
Jul 2009
Keller, Texas
Posts: 4,882
Liked 254 Times on 196 Posts


I said I was technically incompetent. =p

Would I be able to run two separately off of different outlets without risk?

 
Reply With Quote
Old 03-20-2010, 01:51 AM   #5
willynilly
Registered User
Recipes 
 
Feb 2010
Avon
Posts: 728
Liked 8 Times on 7 Posts


Quote:
Originally Posted by ReverseApacheMaster View Post
I said I was technically incompetent. =p

Would I be able to run two separately off of different outlets without risk?
12.5A on a 15A circuit, yes, as long as nothing else is running on those circuits

 
Reply With Quote
Old 03-20-2010, 02:29 AM   #6
DeafSmith
HBT_LIFETIMESUPPORTER.png
 
DeafSmith's Avatar
Recipes 
 
Jan 2009
Richardson, TX
Posts: 1,448
Liked 34 Times on 32 Posts


Quote:
Originally Posted by ReverseApacheMaster View Post
Would I be able to run two separately off of different outlets without risk?
Yes, as long as the two outlets are on different breakers.

 
Reply With Quote
Old 03-20-2010, 02:58 AM   #7
Cliff897
Recipes 
 
Dec 2009
NJ
Posts: 468
Liked 7 Times on 6 Posts


Quote:
Originally Posted by ReverseApacheMaster View Post
Would I be able to run two separately off of different outlets without risk?
No risk? That all depends, but yes: you can get 220 VAC from two separate circuits. They need to be on different breakers so that might possibly mean you gotta run a line from another room.
Smart money would be to figure out which breakers control which outlets. Find two near your brew station and use them


I've run 220 motors that way for years and years.

 
Reply With Quote
Old 03-20-2010, 03:00 AM   #8
willynilly
Registered User
Recipes 
 
Feb 2010
Avon
Posts: 728
Liked 8 Times on 7 Posts


He isnt looking for 220VAC...

He is running a 120VAC 1500W element.

 
Reply With Quote
Old 03-20-2010, 06:54 AM   #9
wilserbrewer
BIAB Expert Tailor
HBT_SPONSOR.png
 
wilserbrewer's Avatar
Recipes 
 
May 2007
Jersey Shore, New Jersey
Posts: 9,694
Liked 1461 Times on 1111 Posts


Two 1500w elements require two separate 15A circuits (ok, outlets on seperate circuits). You certainly can't run two elements off a little "power strip".

 
Reply With Quote
Old 03-20-2010, 04:00 PM   #10
Marsdude
 
Marsdude's Avatar
Recipes 
 
Jan 2010
Fort Collins, CO, Colorado
Posts: 472
Liked 2 Times on 1 Posts


Quote:
Originally Posted by ReverseApacheMaster View Post
I said I was technically incompetent. =p

Would I be able to run two separately off of different outlets without risk?
I agree with willynilly that you could use two different outlets as long as they are on separate breakers. This could prove to be difficult if you live in an older home. All of your kitchen outlets could be on the same circuit. A newer, however, home should have two separate circuits, one feeding half of your outlets and one feeding the other half.


 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Heatstick = awesome! BackBayBrewing Brew Stands 586 10-19-2015 11:24 PM
Double Heatstick? Cpt_Kirks Brew Stands 4 01-06-2011 02:30 PM
Heatstick First Use lieb2101 Brew Stands 2 03-01-2010 07:18 PM
wanted: heatstick bkov For Sale 3 10-23-2009 01:59 AM
Looking for heatstick(s) VTBrewer Brew Stands 44 02-27-2009 02:30 AM


Forum Jump