So, a while back I bought 2 of these 230V Love controllers before they were discontinued at a great price: Controllers-Panel Mount And Love On/Off Temperature Controllers - Cole-Parmer Catalog

I had no use for them at the time, but knew I would come up with something. Well I am now looking to to control some heating elements in my brew setup, but only use 110V lines. Is there any reason these would not work as is, or is it more involved than what I am thinking?

 
Reply With Quote
Old 01-27-2009, 04:44 PM   #2
bull8042
I like 'em shaved
HBT_LIFETIMESUPPORTER.png
 
bull8042's Avatar
Recipes 
 
Jul 2008
Fort Mill, SC
Posts: 10,263
Liked 452 Times on 448 Posts


The 230V you are referring to is the supply voltage for the controller, not the load rating.
You will have to supply 230AC to the control to power it up....It doesn't care if the load is 110VAC or 5VDC, as long as you don't exceed the current rating on the contacts.
__________________
"I brew with a water cooler and some part from the toilet." - JohnnyO

"I do gravity feed the last gallon or two through my Therminator, but I expect you could suck start a Volkswagen before you could suck start one of these. - GilaMinumBeer

"..... Bull was right." - TXCurtis

 
Reply With Quote
Old 01-27-2009, 09:25 PM   #3
bull8042
I like 'em shaved
HBT_LIFETIMESUPPORTER.png
 
bull8042's Avatar
Recipes 
 
Jul 2008
Fort Mill, SC
Posts: 10,263
Liked 452 Times on 448 Posts


Hey Ryan, you have too many PMs and I am unable to reply to yours right now.
Here is what I wanted to say:

OK, in answer to your most basic question, "Is is it possible to use these controllers off the 110V line I have at my disposal in the way I want to?" The answer would be "no". You will have to supply them 230VAC to power them up.
Also, a 2kW element at 110VAC draws 18.2A. Your controller's contacts are rated at 16A, so you would also have to have an SSR to handle the power to the heater.
I am about to leave for the evening, but I will try to redraw the diagram in the morning if you want and see if I can provide a better explanation.
__________________
"I brew with a water cooler and some part from the toilet." - JohnnyO

"I do gravity feed the last gallon or two through my Therminator, but I expect you could suck start a Volkswagen before you could suck start one of these. - GilaMinumBeer

"..... Bull was right." - TXCurtis

 
Reply With Quote
Old 01-27-2009, 09:27 PM   #4
Ryan_PA
 
Ryan_PA's Avatar
Recipes 
 
Aug 2006
Horsham, PA, Pennsylvania
Posts: 1,881
Liked 13 Times on 9 Posts


Thanks man. I did clear my PMs.

 
Reply With Quote
Reply
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
DIY 110v Stirplate Update Catt22 Chillers & Stir Plates 10 07-05-2009 05:42 PM
110v boil kettle SSRider Equipment/Sanitation 16 01-26-2009 05:53 PM
Largest 110V Breaker? Cpt_Kirks Equipment/Sanitation 16 01-10-2009 05:31 PM
Line voltage controller for temp. controll? cudaaar Equipment/Sanitation 7 06-26-2008 01:20 AM
Johnson temp controller - line for probe malkore Bottling/Kegging 7 06-30-2007 06:26 PM


Forum Jump