GFCI keeps blowing

Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum

Help Support Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Cybershadow

Well-Known Member
Joined
May 19, 2010
Messages
184
Reaction score
2
Location
York
I built a heatstick and i have it running on a 20 amp circuit all by itself and it keeps blowing. It doesn't blow right away. It blows after about 5 minutes or so. Then I unplug and let it sit for a minute then I plug it back in and it forks for another minute and blows again.

I used the instructions here.
http://www.3d0g.net/brewing/heatstick

I built it using a 1500 watt element and 14/3 wire which was rated up to 1850 watts.

Any ideas?
 
Is it a new circuit breaker or has it been in the panel for a long time? Are there any other devices running on that circuit when you are running the heatstick? Are you sure it's a 20 amp breaker and not a 15 amp breaker? Is the wire from the box to the outlet you are using the correct size for that draw? What you're describing sounds like the circuit breaker is being overloaded.
 
you're exceeding the 80% rule using 14awg wire. 14 gauge wire is suited for a 15A breaker maximum and 12A at 80%. Using 12 gauge wire would put you where you need to be and would most likely solve your problem.
 
The first thing to determine is if the GFCI is tripping or if the circuit breaker is tripping. You didn't say whether you use a GFCI circuit breaker or a separate GFCI outlet. I assume that they are separate only because most 15 to 20 amp ones are.

If it is the circuit breaker then I would suspect that the breaker has aged and might need to be replaced. Fifteen hundred watts draws only 12.5 amps so a 20 amp breaker is quite sufficient.

If it is the GFCI that is tripping then you have a leak to the ground wire somewhere. It could be in your wiring of the heatstick or in the element itself. Moisture might be getting into your wiring to cause the tripping, but I have no idea why it wouldn't trip again immediately after resetting. Immediately after it trips, try unplugging it and using an ohmmeter to check both the hot lead and neutral lead to to the ground lead. There should be infinite resistance. The small current required to trip a GFCI can happen with any resistance less than about 30,000 ohms.
 
I've actually tried two different 20 amp circuits on my house and the same thing happens on both. It just trips the GFCI and not the breaker box circuit. The second one i tried was just a recepticle ran directly to the breaker box and a 20 amp circuit and that was the only thing on the circuit. I would think if it was leaking it would trip right away everytime i plug it in. It takes a few minutes to trip the GFCI.
 
Using 12 gauge wire would put you where you need to be and would most likely solve your problem.

I doubt it. If the wire was being pushed, it would be the wire failing, not the GFCI. He'd be smelling insulation burning and seeing smoke.
 
You've got a short to ground somewhere if it's blowing 2 separate GFCI's. Does the heatstick shock you when you touch the water?
 
I do not get shocked and it doesn't leak from what I can tell. The entire electrical connection is encased in jbweld, I seriously doubt the water is shorting it.
 
I do not get shocked and it doesn't leak from what I can tell. The entire electrical connection is encased in jbweld, I seriously doubt the water is shorting it.

Well unfortunately, you can't figure it out and asked for help, so the only thing you can do is try the suggestions you asked for.

Sorry, I work tech support and nothing is more irritating than someone asking for help, then dismissing the suggestions they asked for as not plausible.
 
I'm dismissing some of them cause I am not an idiot. I work tech support also and I know a little about ac wiring.
 
maybe i should try actually fastening the green ground wire to the metal pipe with a nut and bolt.
 
The entire electrical connection is encased in jbweld

That may be a no-no. J-B Weld, is a hard, hi temperature, metal filled epoxy. If you put a magnet next to uncured J-B Weld see what it will do. If you encased the electrical connections similar to potting them you may have enough leakage current flowing through the J-B Weld to trip the GFCI. It doesn't take much current to trip the GFCI.
 
^^^ Looks like 10-20% iron powder by weight. Definitely not a dielectric potting substance.

INGREDIENTS WGT% CAS # TLV/PEL
Calcium Carbonate 40-50% 1317-65-3 ACGIH: TWA 10 mg/m3
OSHA: PEL 15 mppcf
Iron Powder 10-20% 65997-19-5 ACGIH TLV 15 mg/m3
OSHA: PEL 15 mppcf
Epoxy Resin 30-40% 25068-38-6 N/E
Aromatic Hydrocarbons 1-5 % 64742-94-5 N/E
 
When all the obvious causes are elimated sometimes you just have to think outside the box and loose your paradigms.

I gotcha ya, but their website said it is non conductive. Whether that holds up to a GFCI trip, i dunno.
 
There are others using the same JB weld potting with 0 issues. Just saying...I used it just as Pol instructed and was skeptical. Granted I didn't do an ohm reading, but a continuity check sticking both leads in the solidified block showed no continuity. Interested to see what you find if the GFCI is more sensitive than a meter.
 
That may be a no-no. J-B Weld, is a hard, hi temperature, metal filled epoxy. If you put a magnet next to uncured J-B Weld see what it will do. If you encased the electrical connections similar to potting them you may have enough leakage current flowing through the J-B Weld to trip the GFCI. It doesn't take much current to trip the GFCI.


I'd think long and hard about this. I used to have all my connections potted in J-B Weld (element in kettle, not a heatstick). It always blew the GFCI. I moved to an electric box set up like kal's where I did not pot anything and have not had an issue. Just my experience, no real data to back it up.
 
That may be a no-no. J-B Weld, is a hard, hi temperature, metal filled epoxy. If you put a magnet next to uncured J-B Weld see what it will do. If you encased the electrical connections similar to potting them you may have enough leakage current flowing through the J-B Weld to trip the GFCI. It doesn't take much current to trip the GFCI.

Per the J-B Weld FAQ (and many hundreds of built and running heatsticks), J-B Weld is an insulator. It does not conduct electricity.

OP's problem is likely a short between one of the element leads and the drain pipe, with thermal expansion triggering it. There is very little clearance between the element screws and the pipe wall. Great care must be taken in centering the element prior to sealing with the J-B Weld, plus insuring no wire "whiskers" are left hanging out of the screws.

A less likely, but possible cause is a faulty element. These things aren't manufactured to the highest of tolerances and I have personally seen DOA elements.
 
:off:

Kind of, I have potted elements that I haven't hooked up yet so I can't speak to the JB weld GFCI issue. If I do have tripping issues I'd like to go with Kal's solution (hadn't run across it when I potted mine). Is it possible, or even worth it to try and clean the JB weld off the elements or just buck up and pay for new?
 
There are others using the same JB weld potting with 0 issues. Just saying...I used it just as Pol instructed and was skeptical. Granted I didn't do an ohm reading, but a continuity check sticking both leads in the solidified block showed no continuity. Interested to see what you find if the GFCI is more sensitive than a meter.

It doesn't take alot of current to trip a GFCI, milliamps will do it. It won't look like a dead short or zero ohms. It just appeared like he tried everything else and it was time to look at the non-obvious. I just wouldn't pot anything electrical with something that is 20% iron by weight. It would be interesting if someone had a multimeter to put it on a higher scale and try to see what resistance they read when probing a cured piece of J-B Weld. I would think this is a leakage problem because if there were a dead short the GFCI would open immediately. I also wonder if J-B Weld is an insulator only when cured and perhaps the J-B Weld has not cured fully yet.
 
It doesn't take alot of current to trip a GFCI, milliamps will do it. It won't look like a dead short or zero ohms. It just appeared like he tried everything else and it was time to look at the non-obvious. I just wouldn't pot anything electrical with something that is 20% iron by weight.
I'm not saying it's not possible, but I would think even a few miliamps would trigger the audible continuity check on a Fluke Meter. By all means, check everything.I'd just be more suspect of a leak. jkarps expansion theory seems logical too since it's fine until things get heated up where as if it was teh JBweld shorting, it'd be instant.
 
It doesn't take alot of current to trip a GFCI, milliamps will do it. It won't look like a dead short or zero ohms. It just appeared like he tried everything else and it was time to look at the non-obvious. I just wouldn't pot anything electrical with something that is 20% iron by weight.

Nonetheless, it's a product specifically endorsed for this use, and hundreds of people have had success. I've also used J-B Weld to pot sensitive altimeter circuits I designed that work in the mA range with flawless success.

A little knowledge with a multimeter that can read mA should easily isolate the leak. I still suspect the two scenarios I've suggested. I've gotten reports just like this numerous times from heatstick builders. Every single time it was a short during construction.
 
I'm not saying it's not possible, but I would think even a few miliamps would trigger the audible continuity check on a Fluke Meter. By all means, check everything.I'd just be more suspect of a leak. jkarps expansion theory seems logical too since it's fine until things get heated up where as if it was teh JBweld shorting, it'd be instant.

I agree with you...check everything. I am not saying the J-B Weld would cause a direct short. I am suggesting it is a high resistance short maybe a couple thousand ohms lending to your leakage theory. Or then again I may be barking up the wrong tree entirely. It is just a theory. If I had a highpot machine I could try an experiment.
 
I work on carpet cleaning equipment. We test every unit on a gfci circuit before it goes out the door because of liablility issues. The craziest things can blow a gfci. I have seen residue from powdered cleaning solution cause a slight short to ground. I have seen an element that when hot has a short from thermal expansion, but has nothing when cool.
 
A decent multi meter capable of measuring in the Megohm range should detect the problem. Run the heat stick until the GFI trips, unplug the heat stick, then measure the resistance from hot to ground, neutral to ground. Any reading less than infinity is a smoking gun. Be sure you are not touching the terminals because your skin resistance will throw off the measurements.

Years ago I had the GFI for the garage tripping intermittently on me. Turns out it was the outdoor light cable, buried in the ground, taking on moisture when it had rained and drying out in between. Look for cracks in the chord also.
 
true, but i have permantly sealed my contacts with jb weld. I need to find a way to liquify silicone caulk to pour around the element instead of jb weld. Silicon will allow me to disassemble the heatstick. I'll probably just have to build a new one and be extra careful.
 
true, but i have permantly sealed my contacts with jb weld. I need to find a way to liquify silicone caulk to pour around the element instead of jb weld. Silicon will allow me to disassemble the heatstick. I'll probably just have to build a new one and be extra careful.

It seems insulating these heatsticks is the most annoying part of electric brewing. I'm interested in these that another user purchased premade. I won't pay their price, but it appears to just be large heat shrink around everything. I grabbed a large piece from work and plan on trying it out. I am considering putting orings on either side inside the heat shrink as well.
element-5500-watt_75_detail.jpg
 
I see in your original post you mention a fork. You are not putting that fork in the outlet are you? That could cause it.

...sorry, I thought it was funny to see the typo and could not help myself. :D
 
One possibility is moisture getting inside the element. It sounds similar to a problem I have had. I use a rebuilt drop-in electric range top as my brew stove (I rebuilt it to get three heating coils close enough together to get my 10 gallon Megapot over them.) During initial testing, I found that the GFCI would trip after a minute or so of heating, and any one of the three coils alone would trip it. If I turned the stove off for a few minutes, and then back on, it would trip more quickly, sometimes immediately, sometimes after only a few seconds. I wanted to do a test to see how long it would take to heat my water to boiling, so I temporarily wired around the GFCI to run the test. The day after the test (45 minutes with the stove on full blast), I put the GFCI back in the circuit to trouble shoot the problem and the problem was gone. My conclusion is that the coils get moisture inside them, which vaporizes after a minute or so of heating, causing the GFCI to trip. If you continue heating the coil (without the GFCI in the circuit) it bakes the moisture out and everything is fine for a while, but the coils will accumulate moisture if left unheated for weeks or months. I solved my problem by simply wiring a regular 30 amp breaker inside my GFCI box, in parallel with the GFCI breaker. At the start of the brew day, if the GFCI trips, I turn on the regular breaker, run the stove for 5 minutes to bake out the moisture, then turn off the regular breaker and turn the GFCI breaker back on and continue without problem.
I know those water heater elements are designed to be used underwater, unlike the coils on my stove, but it does sound to me like water could be getting either into the element or around the connections to the element, and it wouldn't take more than a very tiny amount to trip a GFCI.
 
I'm starting to think it may be a leak too. That is why i need to find a different method other than jb weld. I am gonna hop on google and see what i can find. Jb weld is to permanent and i need a better way to be able to disassemble and troubleshoot.. I'll post what I find for sure.
 
true, but i have permantly sealed my contacts with jb weld.

I meant probing the prongs of the plug. That would settle the issue that there is indeed a ground fault in the stick, if that is not already established 100%.

Enough people have used JB weld to pot electrical connections that I think it is not the most likely culprit, notwithstanding it has iron powder in the mix. It is like you said, though, a permanent assembly.
 
A decent multi meter capable of measuring in the Megohm range should detect the problem. Run the heat stick until the GFI trips, unplug the heat stick, then measure the resistance from hot to ground, neutral to ground. Any reading less than infinity is a smoking gun. Be sure you are not touching the terminals because your skin resistance will throw off the measurements.

Actually, that's not a very good test. It could be there's a crack in the element that's taking in water when heating. GFCI trips based on current, not voltage so testing resistance isn't a reliable method.
 