Informative article on thermowell location and size for precise readings

Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum

Help Support Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Compacto

Active Member
Joined
Mar 17, 2015
Messages
39
Reaction score
27
Covers size, location in and depth of probe in vessel and a bunch of other stuff.

"A rule of thumb for minimum immersion length
to avoid stem conduction error is 10 times the
probe diameter plus the sensitive length of the
probe.**Most RTDs have a sensitive length of
approximately 1.0”.**So for a ¼” diameter RTD the
minimum recommended immersion is 3.5”.***
Thermowells require about 4.5” as a minimum
for best accuracy."


"A thermowell/RTD assembly was immersed in a
bath to determine the stem conduction at
various depths.**At 4.5 inches most of the error
has disappeared.**As you can see the error is
mostly independent of the bath temperature
used.**The error is expressed as a percentage of
the delta T between ambient and process
conditions.**"


http://www.burnsengineering.com/loc...hermowell_selection_and_application_notes.pdf
 