What size wire are you running before and after the GFI? I see your terminal blocks say 65A 6AWG but I'm not sure if that's what you're using for wire. If you are using 6 gauge wire you're fine. Depending on your insulation rating (in celcius) of your THHN or similar wire, you can safely run 60A to well over that (90C insulation).
I'm assuming you're running 10AWG after your 6AWG terminal blocks?
Do you plan on running both elements at the same time? What wattage elements? 240V I'm assuming.
How are you controlling the SSRD's??So I can't control two AC legs with an SSRD?
Do I need to use 65a terminal blocks for Hot1 & Hot2? Do I need to use 6AWG from the terminal blocks to the 30a breakers?
Maximum wire gauge: 8Terminal Blocks from Mouser:
845-CDB6/2 $8.39
Maximum wire gauge: 8
Yeah - that's for the output. Input is 10 to 2 AWG. See the data sheet.
Ahhhh, I thought something must be wrong. Seemed odd 8-22 gauge.