Hey all, I'm reconfiguring my heatstick set-up and have run into a challenge. Hoping the electrical experts out there can give me some feedback.

I run a 2000 watt heatstick on a 20A circuit. My wiring is all 12 AWG, and I'm plugged into a GFI protected outlet.

I'd like to add an inlet box to my rig for convenience, however I'm having a hard time locating a 20A inlet. Would it be a safety risk to use this 15A inlet such as this one as long as I'm still connected to my 20A GFI outlet down the chain? I don't mind the risk of damage to the inlet, but do mnd the risk of damage to my noggin.

For that matter, as I was unable to find the appropriate 20A plug for my original cord I've been using a 15A plug. It shows no sign of stress or heat, but maybe that's been a bad idea.
 
Last edited by a moderator:
Big question - 120 or 240V power?
Short answer 120V = No / 240V = Ok - This is based on the normal power/amps going through the equipment. You could damage the equipment which could lead to damaging your noggin when it becomes unsafe and stray hot wires are touching things they shouldn't.

Also the link you post is for a male receptical, this is not good. You want a female one just like standard outlets.
 
If it's going on the heat stick, it needs to be male.

The amperage ratings are primarily guidelines to how much current a device can take before it starts to suffer from excessive heat. An additional issue you have is that the ambient temperature is high because the inlet is connected to a hot element. That is good reason to want to exceed the usual safety specifications rather than skimp on them.

If it gets hot to the touch or shows signs of heat damage then you know you have a problem.
 
It depends on how many amps you're pulling. Using a 15 amp receptacle with a 20A breaker is ok as long as you don't exceed 15 amps with whaterver you're powering. I prefer to match my receptacles with my breakers so that I never have to worry about it, but if you keep an eye on how many amps you're pulling, you'll be ok. Most devices will tell you how many amps and volts they run on.
 
...Also the link you post is for a male receptical, this is not good. You want a female one just like standard outlets.

Sorry, I think I misunderstood. If it is an input into the heatstick then it's fine.
 
If it's going on the heat stick, it needs to be male.

The amperage ratings are primarily guidelines to how much current a device can take before it starts to suffer from excessive heat. An additional issue you have is that the ambient temperature is high because the inlet is connected to a hot element. That is good reason to want to exceed the usual safety specifications rather than skimp on them.

If it gets hot to the touch or shows signs of heat damage then you know you have a problem.

This is correct. A more direct way of saying it is that you are choosing components that are underrated for your application, which is not the most prudent way to proceed. It may work, but why take the chance?

You can look at the Neutrik Powercon 20a. They have a "power in" chassis mount and a "power out" cord connector. Or you could search on "NEMA 5-20 inlet"

For your plug, you should have a NEMA 5-20 plug fed from a NEMA 5-20 GFCI.

You should be using 12awg copper in your cord to the heat stick, and in your wiring from a 20a circuit breaker in panel to the 20a GFCI outlet.

None of these components are difficult to obtain.
 
You want a straight blade connection? I would think an interlock would be a better approach for this part of your rig, itll protect against disconnects - the cord cant come out

http://www.amazon.com/dp/B003AU799W/?tag=skimlinks_replacement-20

If you still want straight get one of these
http://www.amazon.com/dp/B00AB5YXEI/?tag=skimlinks_replacement-20

or get a single gange single 1.406" hole device like the link below and a waterproof cover from HD/Lowes
http://www.amazon.com/dp/B000FPDKOI/?tag=skimlinks_replacement-20

and put this cover on ti
 
Last edited by a moderator:
As mentioned before, female receptacles are inappropriate for this use. The first one you mention is bulky and expensive.

I would go with the blue 20A powercon connectors from Neutrik.
 
Thanks for all the responses. I'm curious why a female receptacle is inappropriate. Perhaps it would help to diagram what I'm doing here as I'm open to anything: just looking for the simplest solution and don't want to drop excessive amounts of money on this.

I'm looking for the simplest connection at the red components in the diagram below. I've labeled them according to my original proposed solution, but am open to new ideas.
Screen+Shot+2013-04-12+at+11.25.56+AM.png

In this diagram, the head of the arrows represents a MALE plug.

And, to confirm: this is 120V.
 
You want the male inlet on the appliance side, because you always supply power from a female socket to avoid having a male plug with an exposed hot prong.
 
You want the male inlet on the appliance side, because you always supply power from a female socket to avoid having a male plug with an exposed hot prong.

This is what I planned to do. I tried to illustrate that in my diagram, but perhaps it's not clear that the power comes from the circuit on the right and moves right to left toward the heatstick.

Given that, any other suggestions? I'm still unclear on the risk of using a 15A plug or inlet besides getting hot and melting. For example, if you use a 15A connection at some point, will that jeopardize the 20A GFI from being able to trip?
 
It depends on how many amps you're pulling. Using a 15 amp receptacle with a 20A breaker is ok as long as you don't exceed 15 amps with whaterver you're powering. I prefer to match my receptacles with my breakers so that I never have to worry about it, but if you keep an eye on how many amps you're pulling, you'll be ok. Most devices will tell you how many amps and volts they run on.
I will highly disagree with this. Wire up everything off a 20a breaker for a 20a load. Especially if you are wiring this into your house try to stay as close to code as possible.
 
I will highly disagree with this. Wire up everything off a 20a breaker for a 20a load. Especially if you are wiring this into your house try to stay as close to code as possible.
So, all the lamps cords in your house are 12ga wire?

How is this any different than any other appliance plugged into an outlet? As long as nothing within the appliance doesn't exceed the rating, it's fine.
 
So, all the lamps cords in your house are 12ga wire?

How is this any different than any other appliance plugged into an outlet? As long as nothing within the appliance doesn't exceed the rating, it's fine.

Agreed. For the OP though, his 2000w element exceeds the rating of his 15a components.
 