Another thing: The 80% rule? Please read deeper into the NEC code.

I found this link where in note 4 they say 4 wires should not exceed 80% is this out of date or am I missing something (not meant to be rude in the slightest degree, just trying to get my ducks in line and safe as possible).
 
If the four wires were the three phases plus a neutral, then it becomes more than three current carrying conductors. But if it is the three phase conductors and a ground, that is only three current carrying conductors.
 
P-J thanks for the reply. Here is a link to the wire Lowes. length would be 30-40'. Run for 3 hrs. The way I plan to hook it up would be:

dryer outlet - dryer cord (6') - Spa panel - 10/4 wire (30-40') - control panel

Are you sure this is 4 wire? In the picture there is black, white, and green.
 