Which breakers are most appropriate for circuit protection in a control panel?
 
Bump! Someone has to know the difference. Will 1077 breakers work properly?
 
There is a good article describing the diifferences here.

From what I understand, you are required by the NEC to use UL 489 breakers in the panel that feeds the branch cicuit. This would be the load center or panelboard in your home.

If you install additional breakers inside your control panel (in lieu of fuses) then the 1077 breakers would be well suited for that application.

Hope this helps.
 
TrainSafe said:
There is a good article describing the diifferences here.

From what I understand, you are required by the NEC to use UL 489 breakers in the panel that feeds the branch cicuit. This would be the load center or panelboard in your home.

If you install additional breakers inside your control panel (in lieu of fuses) then the 1077 breakers would be well suited for that application.

Hope this helps.

That clears it up. I am planning on using breakers in lieu of fuses and will go with 1077 breakers. Thanks!
 