I haven't been able to find a definitive answer to this question yet.

I would like to run a 120v element for my HLT and a 240v element for my boil kettle at the same time. To accomplish this, my plan is to run a 120v supply and a 240v supply into one control panel, though keep them completely separate, except for the grounding.

Has anyone else done this? Would this cause any problems? Should both power systems be grounded together? I'm concerned that if the grounds and hooked togther and a 30amp fault occurs on the panel, that the current could run down the 14AWG ground. Or would a fault run simultaneously down both the 10AWG and 14AWG grounds?

Any electrical engineers or electricians care to bite?

Thanks.
 
Don't bother, just run the 240v and split the neutral and one hot leg off to FORM a 120v line in the box. This works, it's "normal", just did it recently so my 240v power box also has a 120v fan plug on it for my vent fan. Works a treat, no more extra extension cords ;)
 
Don't bother, just run the 240v and split the neutral and one hot leg off to FORM a 120v line in the box. This works, it's "normal", just did it recently so my 240v power box also has a 120v fan plug on it for my vent fan. Works a treat, no more extra extension cords ;)

This will work fine.. You just need to make sure the Amperage is correct size to support both.
 
This will work fine.. You just need to make sure the Amperage is correct size to support both.

Good to keep in mind yes, just because your big fat 240v cable can handle everything you need doesn't mean the 20gauge wire you just put in for your 120v line will handle the 120v device.

Use switches/plugs/wiring rated for more than your anticipated load on the 120v line. Remember, watts divided by volts = amps, add an extra 20% to the amps for safety padding.
 
The issue at hand though is that the 240v plug is only rated for 30amps. I'm bringing in the 120v power source not to have 120v service but to add an additional 15amps to run the second burner.
 
If a line to ground fault occurs, and both ground wires are connected in parallel, the fault current will flow in both grounds. But that's not really an issue; it will likely tend to favor the 10ga because it would theoretically have less impedance than the 14ga.

You wouldn't have a '30amp fault occur' though; a short is going to draw whatever short circuit current is available, and that might be a couple thousand amperes theoretically, until the breaker trips (which should be pretty fast since that will definitely be in the instantaneous/magnetic trip range).

Usually it would be good to put a label on the panel such as 'energized from multiple sources' just as a note to self that unplugging one plug isn't enough.
 
The 240v 30amp service is good enough for Cal's high end setup.
I would keep it simple and design a 240V 4-wire panel, perhaps using internal wiring and components rated for 50 Amp service. Add a secondary 120v panel if/when you decide it is necessary for large batches or back to back batches. Even if you have to alternate between power to HLT and Boil, you will be heating the water twice as fast with 240V 5500 Watts vs a 120V element.
 
You can run the two power sources together into you control panel, yes tie all the equiptment grounding wires together. Don't worry about the size of the smaller ground wire. On a line to ground fault that tiny wire will in reality carry several hundred amps (mind you for a very short amount of time) until the breaker trips. I recommend getting a 3 pole contactor and wiring into your on/off, kill, e-stop, oh s&!t... switch. That way you can turn off the power to your entire system with one switch. You can find 3 pole contactors on ebay just as inexpensive as the 2 pole contactors others are using.
 
I'm sorta thinking that in this scenario all equipment grounding wires are supposed to be sized according to the largest OCP that serves a device. IOW, if you have a 30A breaker feeding one part and a 15A breaker feeding another, all grounding wires would have to be min of 10ga.

I think the reason may be that if we assume a dead short and low enough resistance/impedance to ground to drive high enough fault current to trip the breaker everything from a practical standpoint probably will work out fine. However, what if the ideal situation doesn't occur...that for what ever reason 29 amps of fault current from the 30A system tries to use your 14ga grounding wire from that 15A circuit?
 
While it would be cleaner to simply have one 50A outlet/power cable to power everything, as long as you keep them completely separate and don't hardwire anything into house power I think you'd be fine.

It's not uncommon to see high end powerful home theater amplifiers that come with 2 power cords to meet the rated specs (example). You must of course plug them into separate circuits.

Kal
 
Thanks for the input Kal. This whole concept seems to be a bit of a stumper. I haven't been able to find anything on the web regarding this in any electrical/diy forums.

The reasoning behind my whole idea to use two power sources is to be able to brew back-to-back batches like your 50a setup, though I'm limited by my 30a dryer plug. By essentially running two systems within one panel, I hope to use the 120v 15a source to heat my HLT and the 240v 30a source to run the rest of the control panel.

I notice with your theatre amplifier example that both plugs look as if they're 15a service. Therefore, any fault would not exceed 15a and would run out either 14AWG ground wire.

The dilemma that we're wrestling with for a two power source panel is a short on the 30a side of the panel travelling down the 15a (14AWG) ground.
 
Correct. Using proper wire size is fundamental. I'd probably use 10ga for both grounds.

Kal
 
I have three feeds in conduit from my loadcenter to my control panel. Technically the metal conduit is sufficient for equipment ground but I chose to run an additional equipment ground which is sized for the largest overcurrent device or 50A = #10ga. This one equipment ground covers all the feeds per NEC 250.122(C). If you are running individual cables like romex for example, each cable must have it's own equipment ground. They all get tied together in your control panel and you essentially have several parallel equipment grounds which when added will end up exceeding the minimum requirement for a conduit.
 
Hmmm...interesting.

So even though the hot wires originate at separate breakers the grounding wires within these cables can be considered parallel connections, or do you just consider the individual cables as separate entities (which ends up being the same net result)?
 
If doing it of course you must keep neutrals separate and use the incoming hot with the corresponding neutral. If doing it in conduit I would run each circuit in its own conduit lest you get into deratings for more than three current carrying conductors in the same conduit.
 
Hmmm...interesting.

So even though the hot wires originate at separate breakers the grounding wires within these cables can be considered parallel connections, or do you just consider the individual cables as separate entities (which ends up being the same net result)?

Yes, I think...The ground per cable is most likely required for some guy accidentally cutting through it with a sawzall. It's grounding overkill to run separate cables.
 
If doing it of course you must keep neutrals separate and use the incoming hot with the corresponding neutral. If doing it in conduit I would run each circuit in its own conduit lest you get into deratings for more than three current carrying conductors in the same conduit.

Derating has to be considered but unless you are getting over 10 current carrying conductors is easily met. We always fill 1-in conduit home runs from the panel. It is most cost effective for conduit and copper.
 
Oh ok that makes sense, I could definitely see that for rigid conduit. For EMT or maybe even IMC maybe not so much?
 
I have 2 separate 30a/240v GFI circuits and 1 30a/120v GGI circuit. 7 wires of which 1 is ground. I have 2 RIMS, 1 HLT and 1 BK. I kept the wire size down to 10ga by doing this. Makes like a lot easier.
 