PID controlled 3-Way valve Wiring Help

Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum

Help Support Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Adacarda

Active Member
Joined
Jul 15, 2011
Messages
37
Reaction score
0
Location
Lititz
Hello all,
I am going to use this: http://misolie.com/showshop.asp?id=358 valve for a HERMS bypass loop and plan on controlling it with an Auber SYL-1512A PID in on-off mode. The idea is that by incorporating a bypass loop I can contol the HLT temperature separate from the mash temperature. Anyhow, I have a 24V transformer for my gas valve, so would I be better off stepping down to 12VDC from that or just get a separate 120VAC to 12VDC transformer? I am leaning toward the later, but what I am confused about is if I will need some kind of relay? My wiring knowledge is basic, so any diagrams would be great! I also plan on using an RTD sensor at the outlet of the HERMS coil. Any help would be appreciated.
 
The PID can drive a solenoid valve directly but you will need a 12 VDC power source. Easiest is to have separate power supply for that, although stepping down from 24 VDC to 12 VDC is also very straightforward.
 