| jakenbake |
12-20-2011 10:26 PM |
Quote:
Originally Posted by audger
if you google "LM35" the #2 result is a datasheet for it. there is ground and VCC in, and then a variable voltage output that is ratiometric to the temperature (+10mV per degree C). if you put a multimeter on a 7 foot loop of wire, you will see anywhere up to maybe 100mV or more induced into it just from moving the wire around. thats a +/- of 10 or more degreees, which is an enormous range for what its being used for. i would really only use a LM35 sensor on a fixed circuit board with short leads, and where i could control the noise very well. over many feet you should be using something digital.
|
if you're seeing that much movement, then the sensor is bad or it is picking up a bunch of noise. Physically moving the wire doesnt induce any more or less electric field. Moving it towards a noise source does. Using twisted shielded cable will certainly help with any noise.
You could also amplify the signal output from the sensor (making the noise a much smaller part of the error). An op amp in a non inverting amp configuration could do this for you.
Again, I need to know what the sensor is connected to. If it is sourcing a lot of current then the resistance of the cable will drop a lot of voltage, throwing your reading off.
Either way, I don't think that much noise should be seen at 100 ft of cable, much less 7 ft.
edit: also, looking at the datasheet, if there is a large capacitance hanging on the output at the receive end, the output can't drive the capacitance, and it could be oscillating. the resistance of the wire could play a large role in that.
|