Old 10-27-2012, 09:33 PM   #1
jcaudill
Feedback Score: 2 reviews
Recipes 
 
Join Date: Dec 2010
Location: VA Beach, VA
Posts: 831
Liked 57 Times on 43 Posts
Likes Given: 4

Default Building a glycol manifold - need help with simple problem

So I am building a glycol manifold because I have two fermenters now and need to chill both off my single glycol chilling unit. The pump is more than powerful enough to do so.

The plan is to use solenoids from valves4projects that will open when a temp sensor falls outside the setpoint and the fermenter needs cooling - pretty basic.

The problem comes when both solenoids are closed. The type of pump that is in the glycol chiller (and I can't change this) probably should not be deadheaded. So when both solenoids are closed, it needs to be following a loop that just circulates the chilled liquid right back into the return. So this way it will keep flowing and the pump will always be happy.

I know I can accomplish this via another solenoid that is energized open (as opposed to buying an expensive N/O solenoid) until one of the other solenoids opens up. But I think there must be some kind of mechanical solution that I am completely missing. Maybe something that senses some kind of pressure build up and automatically opens up or maybe there is just some way I need to plumb this alternatively.

Here's a visual pic of the "manifolds":




Top is simply a return manifold. Bottom comes in from the chiller and has two outputs for the fermenters.

Thanks in advance!

Anyone have any ideas??

__________________
jcaudill is offline
 
Reply With Quote Quick reply to this message
Old 10-28-2012, 04:48 AM   #2
WPStrassburg
Feedback Score: 3 reviews
Recipes 
 
Join Date: Sep 2008
Location: Rochester, NY
Posts: 515
Liked 25 Times on 22 Posts
Likes Given: 1

Default

Either an orifice plate that allows a constant minimum flow or a check valve that will bypass once enough pressure has been built after the two solenoids close. With some relays you could only power the pump when the solenoids are energized, but that may interfere with the cooling if the pump runs while the glycol is being chilled.

__________________
WPStrassburg is offline
 
Reply With Quote Quick reply to this message
Old 10-28-2012, 06:38 PM   #3
ClaudiusB
Feedback Score: 0 reviews
Recipes 
 
Join Date: Dec 2007
Location: El Paso, Texas
Posts: 1,291
Liked 64 Times on 54 Posts
Likes Given: 126

Default

Quote:
Originally Posted by jcaudill View Post
So I am building a glycol manifold because

The problem comes when both solenoids are closed. The type of pump that is in the glycol chiller (and I can't change this) probably should not be deadheaded. So when both solenoids are closed, it needs to be following a loop that just circulates the chilled liquid right back into the return. So this way it will keep flowing and the pump will always be happy.
Quote:
But I think there must be some kind of mechanical solution
Most commercial chiller systems are supplied with an internal pressure bypass valve.
Install an adjustable pressure bypass valve at the end of your supply. These adjustable valves will bypass flow from your supply to your storage tank.

Quote:
I know I can accomplish this via another solenoid that is energized open (as opposed to buying an expensive N/O solenoid) until one of the other solenoids opens up.
My set-up uses a motorized bypass valve which is controlled by a logic controller.
I like more the technical challenge










Supply on the left, return on the right



Cheers,
ClaudiusB
ClaudiusB is offline
 
Reply With Quote Quick reply to this message
Old 10-28-2012, 09:00 PM   #4
jcaudill
Feedback Score: 2 reviews
Recipes 
 
Join Date: Dec 2010
Location: VA Beach, VA
Posts: 831
Liked 57 Times on 43 Posts
Likes Given: 4

Default

Quote:
Originally Posted by ClaudiusB View Post
Most commercial chiller systems are supplied with an internal pressure bypass valve.
Install an adjustable pressure bypass valve at the end of your supply. These adjustable valves will bypass flow from your supply to your storage tank.


My set-up uses a motorized bypass valve which is controlled by a logic controller.
I like more the technical challenge










Supply on the left, return on the right



Cheers,
ClaudiusB
Thanks for the detailed reply! I am finding all kinds of different ways I could go about this. One is using a check valve with a cracking pressure that allows the recirc to function when pressure is too high. Another is using a pressure switch that basically does the same thing except it actually energizes a solenoid when actuated.

One of the problems I'm finding is knowing what to search for. You said adjustable pressure relief valve. Are you talking something like this: http://straval.com/catlist-relief-valves/CKV-05? That is what I'd call a check valve.

On your motorized solution - can you explain what is going on there? It sounds like you're doing something like I mentioned above but I'm not quite sure. I tried to search on that Erie component but couldn't find much.

I noticed one other weird thing last night. I hooked up a part of the manifold I showed above last night, except it had one input, and one output and I put a pressure gauge at the end because I wanted to see what the pressure was when the pump was deadheaded and when the output was hooked up to return to the chiller. (The answer was 9 psi when deadheaded and around 3 when not). The weird thing though is it was doing something strange to my pump which is a recirculation pump (has the agitator attached to the bottom to stir the glycol bath). After I shut the chiller off, if I turned it back on the pump wouldn't work. I have to open the top of the chiller, and manually turn the agitator with my hand and that must have freed something up because next time I turned it on all was well. But then next time it would be back to not working and I'd have to do the same thing. So instead of using the manifold I just hooked it up to my immersion chiller to make sure everything is ok and this problem disappeared. So best I can come up with maybe the flow was backing up against the agitator motor and binding it up? I don't know what about that manifold design would cause that unless it had something to do with the pressure gauge.

All help is very much appreciated!
__________________
jcaudill is offline
 
Reply With Quote Quick reply to this message
Old 10-29-2012, 09:40 PM   #5
jcaudill
Feedback Score: 2 reviews
Recipes 
 
Join Date: Dec 2010
Location: VA Beach, VA
Posts: 831
Liked 57 Times on 43 Posts
Likes Given: 4

Default

One more question for you too: I realized I can't use those solenoids for this. The opening is too small. What are you using for a solenoid or actuator type valve? Thanks!

__________________
jcaudill is offline
 
Reply With Quote Quick reply to this message
Old 10-30-2012, 04:00 AM   #6
fastev
Feedback Score: 2 reviews
Recipes 
 
Join Date: Jul 2010
Location: San Jose
Posts: 113
Liked 3 Times on 2 Posts

Default

You could put the solenoid valves on the outlet of your ferms rather than the inlet. You could add a ~4lb check valve that would put a slight load on the pump, but when the solenoid valve opens you'll have a lower resistance loop through the ferm.

__________________
fastev is offline
 
Reply With Quote Quick reply to this message
Old 10-30-2012, 10:13 PM   #7
jcaudill
Feedback Score: 2 reviews
Recipes 
 
Join Date: Dec 2010
Location: VA Beach, VA
Posts: 831
Liked 57 Times on 43 Posts
Likes Given: 4

Default

Thanks for the reply! What would moving the solenoids accomplish? Just curious. I did order new solenoids yesterday that have much larger orifices - so that problem is taken care of. I just need to handle the check valve now.

This leads me to two questions:

1) Finding a 4psi model is a bit tricky. I'd have to get a custom one made I think?
2) Should I put a low pressure check valve on the outlet of the pump to prevent backflow? Seems like that could potentially be an issue as well.

Thanks again!

__________________
jcaudill is offline
 
Reply With Quote Quick reply to this message
Old 10-31-2012, 02:59 PM   #8
jcaudill
Feedback Score: 2 reviews
Recipes 
 
Join Date: Dec 2010
Location: VA Beach, VA
Posts: 831
Liked 57 Times on 43 Posts
Likes Given: 4

Default

So I ended up ordering a 5psi cracking pressure check valve last night, in 3/8" that I'll end up reducing down but the orifice was much bigger on the 3/8" that the 1/4" so the check valve should not impede flow.

I just need to know if I should put a check valve near the pump outlet, or inlet to the manifold as well so that there is no backflow.

Thanks guys!

__________________
jcaudill is offline
 
Reply With Quote Quick reply to this message
Old 11-01-2012, 12:44 PM   #9
MaxOut
Feedback Score: 1 reviews
Recipes 
 
Join Date: Jan 2011
Location: Hughesville, Maryland
Posts: 727
Liked 61 Times on 43 Posts
Likes Given: 2

Default

I would wire a simple DPDT ($5.00) relay to you selenoids that will shut the chiller off when both valves are closed. KISS and save power.

__________________
MaxOut Brew Station on HBT

MaxOut Brew Station on AHA
MaxOut is offline
 
Reply With Quote Quick reply to this message
Old 11-01-2012, 12:48 PM   #10
jcaudill
Feedback Score: 2 reviews
Recipes 
 
Join Date: Dec 2010
Location: VA Beach, VA
Posts: 831
Liked 57 Times on 43 Posts
Likes Given: 4

Default

It's a good idea.. but unfortunately not possible The chiller and pump have to stay on. Both are responsible for keeping the bath chilled (the pump has an agitator to keep the bath evenly distributed and from freezing).

__________________
jcaudill is offline
 
Reply With Quote Quick reply to this message
Reply



Quick Reply
Message:
Options
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Building a Gas Manifold Kord78 Brew Stands 1 01-06-2012 08:44 PM
building a manifold Firebat138 Kettles, Mash Tuns, & Hot Liquor Tanks 32 08-01-2011 12:24 AM
Building a copper manifold r8rphan Kettles, Mash Tuns, & Hot Liquor Tanks 24 12-21-2010 03:38 PM
Building my own glycol chiller JeremyHB Fermenters 12 12-12-2010 04:14 PM
Building a manifold on the cheap??? Rhys79 Equipment/Sanitation 7 05-29-2008 12:55 AM



Newest Threads

LATEST SPONSOR DEALS