I just hooked up my Dinico BBP-CD-101 PID, using an RTD sensor. On appearances, everything looks in order. The device display works properly, and it's "controlling" my electric element. However, it overshoots the temp. It basically never shuts the signal off to the relay. I'm not overly technical, and the "instructions" that came with the PID are pretty much worthless to me.

Anyone out there used one of these or any other PID that might be similar? I figured that the "SV" is my temp setting, and the "PV" is the actual temp. When I tried it, I set the SV for 66 degrees C (152F), and the PV was showing as 17 degrees C. It went up to 19, but never beyond. However, my test water went up to 66 degrees C, and then just kept going.

I double and triple checked the wiring, and everything looks good. The only possible variable is that the RTD sensor has two wires with blue connectors to attach to the PID, and another wire with a red connector. The instructions show two "-" wires and one "+" wire should come from the RTD sensor and go to the PID. So the variable is that it doesn't say which "-" wire is which, and they are identical. Attached is the "instructions" that came with the PID. I used the wiring diagram with the RTD sensor, not the thermocouple.

Any help is greatly appreciated.

Thanks,

d

File Type: pdf PID Instructions.pdf (277.2 KB, 38 views)
__________________
dan_rouse is offline
 
Reply With Quote Quick reply to this message
Old 03-06-2013, 06:37 PM   #2
crane
Feedback Score: 0 reviews
Recipes 
 
Join Date: Sep 2011
Location: San Diego, CA
Posts: 280
Liked 25 Times on 22 Posts
Likes Given: 1

Default

The two blue "-" wires are electrically identical and interchangeable so as long as you have them connected to the two "-" terminals on the PID then you are fine.

The SV should correspond to setpoint variable and the PV should correspond to the process variable which is the measured temp of the RTD. Since the measured temp never got above 19 the PID rightfully never turned off the heater. Does your PID allow for different types of temp sensors, RTD, thermocouple, thermistors? If so then check to make sure it is setup to read a 3-wire RTD and not one of the others. There should be a menu setting to select which type of sensor you are using.

__________________
crane is offline
 
Reply With Quote Quick reply to this message
Old 03-06-2013, 11:14 PM   #3
dan_rouse
Feedback Score: 0 reviews
Recipes 
 
Join Date: Feb 2013
Posts: 27
Default

Quote:
Originally Posted by crane View Post
The two blue "-" wires are electrically identical and interchangeable so as long as you have them connected to the two "-" terminals on the PID then you are fine.

The SV should correspond to setpoint variable and the PV should correspond to the process variable which is the measured temp of the RTD. Since the measured temp never got above 19 the PID rightfully never turned off the heater. Does your PID allow for different types of temp sensors, RTD, thermocouple, thermistors? If so then check to make sure it is setup to read a 3-wire RTD and not one of the others. There should be a menu setting to select which type of sensor you are using.
That's actually quite helpful. An incorrect setting for the type of sensor makes perfect sense. Now I just need to figure out how to change the setting.

Thanks.
__________________
dan_rouse is offline
 
Reply With Quote Quick reply to this message
Old 03-09-2013, 04:21 PM   #4
dan_rouse
Feedback Score: 0 reviews
Recipes 
 
Join Date: Feb 2013
Posts: 27
Default

Crane

Update - there were two hidden menus for changing a couple of settings to switch the input sensor and temp thresholds. The instructions didn't mention either, but the PID distributor walked me through it and now it's working perfectly.

Thanks for the help.

__________________
dan_rouse is offline
 
Reply With Quote Quick reply to this message
Old 03-10-2013, 03:46 PM   #5
crane
Feedback Score: 0 reviews
Recipes 
 
Join Date: Sep 2011
Location: San Diego, CA
Posts: 280
Liked 25 Times on 22 Posts
Likes Given: 1

Default

Quote:
Originally Posted by dan_rouse
Crane

Update - there were two hidden menus for changing a couple of settings to switch the input sensor and temp thresholds. The instructions didn't mention either, but the PID distributor walked me through it and now it's working perfectly.

Thanks for the help.
Awesome. Now you just have to make some beer with it.
__________________
crane is offline
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
temperature controller from deas fridge - use as external controller on live fridge? BrewingChemist DIY Projects 1 05-22-2012 10:21 PM
rKc CD101 Help... trango1981 Electric Brewing 14 01-12-2012 09:15 PM
For Sale - Need a temperature controller GoNova For Sale 7 02-21-2011 10:20 PM
Johnson Analog Temperature Controller Temperature Profile Coastarine Equipment/Sanitation 4 10-11-2010 03:58 PM
temperature controller trainfever Bottling/Kegging 6 09-21-2008 05:01 PM