Home Brew Forums

Home Brew Forums (http://www.homebrewtalk.com/forum.php)
-   Automated Brewing Forum (http://www.homebrewtalk.com/f235/)
-   -   Source an RTD (http://www.homebrewtalk.com/f235/source-rtd-405394/)

LBussy 04-16-2013 06:50 PM

Source an RTD
 
I need to find a 2-wire RTD for a controller I am putting together. I can find them all over the interwebz but I'd like to get one from a reputable place. Any ideas or recommendations?

This is for a keezer/fermentation chamber build if that matters.

Stephonovich 04-18-2013 12:47 AM

Digi-Key

That being said, a 4 wire RTD is much more accurate. A 2 wire is prone to two errors; compartment temperature affecting the resistance of your leads, and self-heating due to increased current causing the RTD itself to heat up. 3 wire eliminates compartment temperature, but still has the self heating effect.

Mind you, it's probably not going to have a huge effect overall on your accuracy, but it would bug me. 3 wire only needs an extra line run; 4 wire needs a constant current source (not hard to source or make).

LBussy 04-18-2013 09:39 AM

Thank you I'll have a look.

As a person with OCD tendencies I can appreciate your comments about the accuracy of 2-wire compared to 3 or 4. With short leads and low current, applied in an environment with a relatively high heat sink capability, these are just not likely going to be an issue for me.

DougK 04-19-2013 12:11 AM

Just to clarify, you need a current source with any RTD. Ohm's law pretty much requires it.

Also, with 2 wire RTDs, you need to account for line resistance, this is why a 3 or 4 wire configuration is more accurate: it negates the line resistance of the wire.


You could do a 2-wire setup, you would just have to calibrate the rtd measurement system. RTDs are not linear temperature devices, meaning that of 0 degrees is 0 volts, and 100 degrees is 100 volts, 50 degrees won't be 50 degrees. It might be close, but curve fitting is required. I generally use 4th degree polynomials when curve fitting a calibration curve. Best way to calibrate is to use a dekade box and inject the resistances that correspond to a given temperature. Without this, a small added lead resistance can lead to huge errors in temperature. A 4 ohm change corresponds to roughly 50 degrees. 10 feet of 20 AWG wire would have a resistance of around 0.1 Ohms, that works out to be about 1/2 a degree.


Granted, I'm used to dealing with tighter accuracy requirements than the average home brewer probably cares about, but you'll have to decide for yourself if you want to give up accuracy.


Generally get thermocouples and rtds from Omega

Stephonovich 04-19-2013 05:21 PM

Quote:

Originally Posted by DougK (Post 5121766)
Just to clarify, you need a current source with any RTD. Ohm's law pretty much requires it.

I hope someone putting together a system involving RTDs understands that.

Quote:

Originally Posted by DougK (Post 5121766)
Without this, a small added lead resistance can lead to huge errors in temperature.

Big time on this. You'll want to figure out the length of your leads first, make all your connections (crimps, solder, what have you), and measure that resistance to add into your final calibration. Or, use those leads during the cal.

DougK 04-20-2013 01:57 AM

Quote:

Originally Posted by Stephonovich (Post 5123851)
I hope someone putting together a system involving RTDs understands that.



Big time on this. You'll want to figure out the length of your leads first, make all your connections (crimps, solder, what have you), and measure that resistance to add into your final calibration. Or, use those leads during the cal.

Just making sure no one misunderstood and thought that a 2 wire RTD could be run like a thermocouple, only to be confused when they get no change in voltage with temperature.

It is MUCH easier to calibrate the lead resistance out. Some components won't give you their impedance, or they give you a nominal range. The highest accuracy will be obtained by minimizing this as much as possible.


I calibrate at the point at which an RTD is calibrated in its CAL lab. Generally at the terminal block.

LBussy 04-20-2013 10:55 AM

I've used RTD's in non-brewing systems for years ... I think some of you are over-studying for the test. :) For what we are doing a simple calibration/check is fine, self heating is not going to be an issue. You can run these out with a couple hundred feet of wire and at that point you start seeing some shift but for a 24" lead and what we do, I'd really doubt you'd see too much.

When I used them in a professional setting they were so easy to find. Now, trying to find ONE at a decent price makes me wish I had accumulated more "Stuff" when doing that work.

alien 04-24-2013 02:08 PM

Wouldn't mind knowing the answer to this too. I have a rock bottom ebay PT100 in my smoker and it is rubbish. But the alternatives seem way more expensive.

Rbeckett 04-24-2013 02:16 PM

I got 5 DS18B20's in waterproof configuration for 5 bucks from an ebay seller out of China. I am using the +5 volt dedicated power and reading the data line into a 16f877A. I have 3 PID's that also feed the alarm and relay signals to the PIC to allow me to automate the sequence and hit all of my temps and times. They are definately available and much cheaper now too.

Wheelchair Bob

alien 04-24-2013 02:30 PM

DS18B20s are great for microcontroller builds but you can't use them with off the shelf PIDs.


All times are GMT. The time now is 07:40 AM.