Default Testing a 240v control panel with 120v

So I finally completed my 240v 50a control panel, but it's going to be a month or two before I get the 240v 50a service set up in my basement, and I'm really curious to see if everything is working okay on my control panel.

I don't need to test the element outlets, I just wanted to make sure that the contactors and switches and PIDs and pump outlets were working as they're supposed to.

The contactor coils are all 120v as well, btw.

So...yeah...I don't think that there would be anything wrong hooking this baby up to a 120v 15a GFCI cord, splitting the hot wire to run into both hot lines of the 240v system and plugging it into the wall. Since I'm not running any elements at this time, there's no need for 240v service.

Right? Or should I just cool my jets and wait?

__________________
www.jolietbrewersguild.org
LandoLincoln is offline
 
Reply With Quote Quick reply to this message
Old 04-26-2013, 06:43 PM   #2
jeffmeh
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
jeffmeh's Avatar
Recipes 
 
Join Date: Feb 2009
Posts: 1,870
Liked 144 Times on 125 Posts
Likes Given: 19

Default

Perhaps you could smoke out an issue, but my view is that there will be so much reconfiguration that there will be limited value. You will have to retest when you get your 50a service, regardless. But it's your panel, so proceed if you like.

One specific question: How will you put a load on the SSR's so you are not confounded by SSR leakage?

__________________
jeffmeh is offline
 
Reply With Quote Quick reply to this message
Old 04-26-2013, 10:52 PM   #3
LandoLincoln
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
LandoLincoln's Avatar
Recipes 
 
Join Date: Feb 2011
Location: Joliet, IL
Posts: 2,204
Liked 571 Times on 329 Posts
Likes Given: 13

Default

I don't know what there would be to reconfigure. I don't have any lights that run on 240v. Nothing is 240v except for the power going to the elements, which I'm not going to be testing.

I really don't know much of anything about SSR leakage. I guess I have more reading to do.

__________________
www.jolietbrewersguild.org
LandoLincoln is offline
 
Reply With Quote Quick reply to this message
Old 04-26-2013, 11:52 PM   #4
Shockerengr
Feedback Score: 0 reviews
Recipes 
 
Join Date: Feb 2007
Posts: 442
Liked 20 Times on 17 Posts
Likes Given: 1

Default

It'll depend a lot on your setup, I tested mine (also a 240v, 50a) on 120 before I moved it to it's final spot. On my setup, all the 120 comes from a single leg, so I just powered that leg and left the other unpowered and tested from there.

SSR leakage won't be an issue unless you are indicating element status from the AC side of the elements. Since you said you don't have 240 items, I'll assume you don't have element lights (it's really the only way to get them to work on the a/c side) Essentially what happens is when you don't have the elements hooked up to provide a load, there is residual current that's enough to make the indicators glow. On my setup, when I don't have the element connected, the light glows about a 1/3rd as bright as normal.

__________________
Shockerengr is offline
 
Reply With Quote Quick reply to this message
Old 04-27-2013, 07:20 AM   #5
jeffmeh
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
jeffmeh's Avatar
Recipes 
 
Join Date: Feb 2009
Posts: 1,870
Liked 144 Times on 125 Posts
Likes Given: 19

Default

I agree that you could test all of your 120v devices by connecting a 120v hot to the hot bus that feeds them, and the neutral to your neutral bus. You would then defer the testing of your 240v devices (SSRs and elements) until you have your 240v service. If you are getting antsy, go for it.

__________________
jeffmeh is offline
 
Reply With Quote Quick reply to this message
Old 04-27-2013, 12:41 PM   #6
cank
HBT_LIFETIMESUPPORTER.png
Feedback Score: 4 reviews
Recipes 
 
Join Date: Nov 2012
Location: Jonesboro, Arkansas
Posts: 503
Liked 26 Times on 25 Posts
Likes Given: 17

Default

Could you just get a temp 30 amp 2 pole breaker?
I'm testing mine right now using a temporary non GFCI 240 v breaker. I set everything up right next to my panel and wired in a 4 wire dryer cord to power my control box, got my multi-meter out and my voltage detector and went through switches to make sure all was kosher.

__________________
cank is offline
 
Reply With Quote Quick reply to this message
Old 04-27-2013, 02:53 PM   #7
processhead
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
processhead's Avatar
Recipes 
 
Join Date: Oct 2007
Location: Nebraska
Posts: 664
Liked 100 Times on 77 Posts
Likes Given: 4

Default

IMO the only useful testing you can do with 120 VAC is the control functions of contactor coils, PID, and the other low voltage systems.

As Jeffmeh points out, the 240 volt power circuits can only be realistically tested when your 240 supply circuit is ready.

__________________

How hard can it be?

processhead is offline
 
Reply With Quote Quick reply to this message
Old 04-27-2013, 03:35 PM   #8
LandoLincoln
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
LandoLincoln's Avatar
Recipes 
 
Join Date: Feb 2011
Location: Joliet, IL
Posts: 2,204
Liked 571 Times on 329 Posts
Likes Given: 13

Default

Quote:
Originally Posted by processhead View Post
IMO the only useful testing you can do with 120 VAC is the control functions of contactor coils, PID, and the other low voltage systems.

As Jeffmeh points out, the 240 volt power circuits can only be realistically tested when your 240 supply circuit is ready.
That's exactly what I wanted to test. But I've decided to just cool my jets and wait it out until I have everything ready. But thanks for all of the input, fellas!


"I'll just sit here on the couch and wait. Take your time."
__________________
www.jolietbrewersguild.org
LandoLincoln is offline
 
Reply With Quote Quick reply to this message
Old 04-27-2013, 08:11 PM   #9
processhead
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
processhead's Avatar
Recipes 
 
Join Date: Oct 2007
Location: Nebraska
Posts: 664
Liked 100 Times on 77 Posts
Likes Given: 4

Default

BTW,
Hope your controller works as good as it looks!

__________________

How hard can it be?

processhead is offline
 
Reply With Quote Quick reply to this message
Old 04-27-2013, 09:18 PM   #10
LandoLincoln
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
LandoLincoln's Avatar
Recipes 
 
Join Date: Feb 2011
Location: Joliet, IL
Posts: 2,204
Liked 571 Times on 329 Posts
Likes Given: 13

Default

Quote:
Originally Posted by processhead View Post
BTW,
Hope your controller works as good as it looks!
Me too! Thanks for the compliment.
__________________
www.jolietbrewersguild.org
LandoLincoln is offline
 
Reply With Quote Quick reply to this message
Reply



Quick Reply
Message:
Options
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
2 Vessel, 2 PID, 3 element 120V Control Panel wiring hustlebird Electric Brewing 3 04-02-2013 08:44 PM
240v or 120v ronan Electric Brewing 19 10-04-2012 12:31 AM
120V Control Panel Build chaserchap Electric Brewing 3 02-01-2012 09:25 PM
120v Control Panel + 220v quick add on = Ultimate mobility? wh4tig0t Electric Brewing 2 01-11-2011 06:33 AM
Strange issue with 240v legs. 120v on both, no 240v Brewmoor Electric Brewing 5 12-03-2010 07:15 PM



Newest Threads

LATEST SPONSOR DEALS