Quote:
Originally Posted by Sublime8365
Reading through the forums a bit it's possible that I have a faulty SSR I guess. How would I test that with a voltmeter?
|
Your PID should put out a small DC current, around 12VDC. Using your multimeter in DC mode, disconnect the SSR feed from the PID and set it to manual at 100% - check the voltage across the two posts; if you have 12VDC, good. Turn everything off, reconnect the SSR to the PID, and disconnect the main feed in / out of the SSR (the 120v line). With your meter set to measure ohms, check across the two posts - you should get little or no reading. Then turn on the PID, set to 100%, and measure again - you should measure a much higher reading, indicating that the switch has closed and you have a clear path for current. How your multimeter is set up may change how your output looks, depending on whether you have a digital or analog device. If all that has worked so far, plug it all back in as normal, and take voltage readings (AC) from the power-in post on the SSR (touch one lead to the post, another to your neutral hub (120v) or the other hot line (240v), doesn't matter). Then do the same for the power-out post. Both should read the same with the PID at 100% manual.
This should, hopefully, get you to where we can figure out what's wrong.
Quote:
Originally Posted by Sublime8365
Would that affect my contactor not working with my switch?
|
Your contactor has nothing to do with your SSR. The ability for the contactor to open / close is totally independant of what the SSR is doing. If your contactor is not closing the circuit correctly, then you have a problem there and no amount of trouble shooting the SSR will fix it.
-Kevin