Default Main power wire gauge for 50A panel

I've searched the forum and can't see to find a consistent answer for this. What size wire should I use to go from a 50A breaker in my main panel to a 50A spa panel with GFCI to my control panel? I feel like I've seen both 6 and 8 gauge copper THHN recommended. Also, is conduit needed or can the wire just be run through the wall?

I know there are a lot of other things that factor into this so here are some details...

Spa panel will be within a few feet of my main panel in my garage, which is drywalled.
Probably go with a 12-15' power cable to run from spa panel to control panel.
Including option to run 2 elements at the same time so will be pulling 45+ amps occasionally.

I'm going to have someone install the breaker and spa panel but wanted to be able to tell them exactly what I need and why. It's a friend of a friend of a friend type thing so I'd rather be able to have everything ready for them to just install it.

__________________
summerofgeorge is offline
 
Reply With Quote Quick reply to this message
Old 06-12-2012, 04:31 AM   #2
lschiavo
Drinks Beer
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
lschiavo's Avatar
Recipes 
 
Join Date: Sep 2009
Location: Surrounded by Yoopers
Posts: 4,002
Liked 793 Times on 529 Posts
Likes Given: 547

Default

#6 is the way to go. For such a short run, why go with 8? You may save a few dollars but will not technically be "NEC legal". I'd use 6 then when you add a few amps in the future you will not have to worry.

Edit: conduit depends on the application and your local codes. My brewery feed is in conduit but is not required to be...I'm sure that doesn't help you

__________________
lschiavo is offline
 
Reply With Quote Quick reply to this message
Old 06-12-2012, 06:02 PM   #3
summerofgeorge
Feedback Score: 0 reviews
Recipes 
 
Join Date: Feb 2008
Location: Mount Laurel, NJ
Posts: 280
Liked 1 Times on 1 Posts

Default

Thanks Ischiavo! Are you recommending using #6 for both the short run to the spa panel and also for the 12-15' main power cord?

The main reason I'm asking about all of this is safety/code...the other reason is that I'm trying to figure out how I'm going to distribute the power inside my panel. I want my terminal blocks or din blocks to be able to handle the incoming wire size.

__________________
summerofgeorge is offline
 
Reply With Quote Quick reply to this message
Old 06-12-2012, 11:06 PM   #4
lschiavo
Drinks Beer
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
lschiavo's Avatar
Recipes 
 
Join Date: Sep 2009
Location: Surrounded by Yoopers
Posts: 4,002
Liked 793 Times on 529 Posts
Likes Given: 547

Default

Quote:
Originally Posted by summerofgeorge View Post
Thanks Ischiavo! Are you recommending using #6 for both the short run to the spa panel and also for the 12-15' main power cord?

The main reason I'm asking about all of this is safety/code...the other reason is that I'm trying to figure out how I'm going to distribute the power inside my panel. I want my terminal blocks or din blocks to be able to handle the incoming wire size.
Yes, I would use 6 between the breaker and the terminal block in your control panel.

I really like these blocks and have used them in several panels:

http://www.elecdirect.com/product/66...7ea6ffdbd.aspx

You can run your 6 in and tap off to your fusing. They work nice. I usually put in four for the hots, neutral and ground.
__________________
lschiavo is offline
 
Reply With Quote Quick reply to this message
Old 06-14-2012, 01:05 AM   #5
hatrickwah
Sponsor
HBT_SPONSOR.png
Vendor Ads 
Feedback Score: 1 reviews
Recipes 
 
Join Date: Nov 2010
Location: The Woodlands, TX
Posts: 263
Liked 6 Times on 5 Posts

Default

Quote:
Originally Posted by summerofgeorge View Post
Thanks Ischiavo! Are you recommending using #6 for both the short run to the spa panel and also for the 12-15' main power cord?

The main reason I'm asking about all of this is safety/code...the other reason is that I'm trying to figure out how I'm going to distribute the power inside my panel. I want my terminal blocks or din blocks to be able to handle the incoming wire size.
I have 6 running from my panel to the spa to the control panel. Into DINs. The DINs I used can handle the 6# upto 22#. Quick and easy.

__________________

Keeping busy brewing & building.

Electric Brewing Supply

My e-Brewery | Keezer Build & Tap Tower Refurbish |Glycol System

hatrickwah is offline
 
Reply With Quote Quick reply to this message
Old 06-14-2012, 01:43 AM   #6
gtmaus
Feedback Score: 0 reviews
Recipes 
 
Join Date: May 2012
Location: St. Louis, MO
Posts: 117
Liked 14 Times on 8 Posts
Likes Given: 15

Default

electrician here. You need 6 awg for 50 amps

__________________
gtmaus is offline
 
Reply With Quote Quick reply to this message
Old 06-14-2012, 01:52 AM   #7
P-J
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Mar 2010
Location: Charlotte, NC
Posts: 3,284
Liked 260 Times on 207 Posts
Likes Given: 459

Default

Quote:
Originally Posted by gtmaus View Post
electrician here. You need 6 awg for 50 amps
That is a huge "depends":

http://www.cerrowire.com/ampacity-charts

Depends on the wire rating and conductor rating.

Take a look at the chart.!
__________________
P-J is offline
 
Reply With Quote Quick reply to this message
Old 06-14-2012, 02:00 AM   #8
gtmaus
Feedback Score: 0 reviews
Recipes 
 
Join Date: May 2012
Location: St. Louis, MO
Posts: 117
Liked 14 Times on 8 Posts
Likes Given: 15

Default

Quote:
Originally Posted by P-J View Post
That is a huge "depends":

http://www.cerrowire.com/ampacity-charts

Depends on the wire rating and conductor rating.

Take a look at the chart.!
Of course there's a lot more to it. You need to consider ambient temp, raceway (conduit or open air), number of conductors ampacity derating percentages and insulation type. I was just making it easier for him. I know what I do for a living.
__________________
gtmaus is offline
 
Reply With Quote Quick reply to this message
Old 06-14-2012, 02:13 AM   #9
P-J
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Mar 2010
Location: Charlotte, NC
Posts: 3,284
Liked 260 Times on 207 Posts
Likes Given: 459

Default

Quote:
Originally Posted by gtmaus View Post
...
I know what I do for a living.
Understood. No problem - However - I took exception to the blanket statement that was made. There is one hell of a lot more to it than that.

It's like the other issue that I have a hard time ignoring. The "percentage rule" for the power draw on a electrical outlet circuit. There is more to it than most "electricians" seem to realize.

Another thing... Never mind - it no longer matters.
__________________
P-J is offline
 
Reply With Quote Quick reply to this message
Old 06-14-2012, 02:20 AM   #10
gtmaus
Feedback Score: 0 reviews
Recipes 
 
Join Date: May 2012
Location: St. Louis, MO
Posts: 117
Liked 14 Times on 8 Posts
Likes Given: 15

Default

Quote:
Originally Posted by P-J View Post
Understood. No problem - However - I took exception to the blanket statement that was made. There is one hell of a lot more to it than that.

It's like the other issue that I have a hard time ignoring. The "percentage rule" for the power draw on a electrical outlet circuit. There is more to it than most "electricians" seem to realize.

Another thing... Never mind - it no longer matters.
no worries here. I was just trying to keep it simple and help. 6 awg is what I would run if it was in my house.
__________________
gtmaus is offline
 
Reply With Quote Quick reply to this message
Reply



Quick Reply
Message:
Options
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
what gauge wire? bagpiperjosh Electric Brewing 8 04-14-2012 12:52 AM
What guage wire from main panel to spa panel? AdamCanFly Electric Brewing 22 02-01-2012 03:36 AM
Gauge of ground wire GRHunter Electric Brewing 12 05-25-2011 11:26 PM
Any issue using larger gauge wire? adivito Electric Brewing 7 04-11-2011 10:45 PM
Heatstick 12 gauge electrical wire/cord? redalert Electric Brewing 11 01-07-2011 04:09 PM



Newest Threads

LATEST SPONSOR DEALS