I plan on making a 240V keggle, using a 5500 watt element, an Auber PID w/RTD temp sensor, and THIS inline GFI cable.

My question is: How do I wire it up? Specifically, the neutral wire. I know the 2 hots connect to the element, and the ground gets bolted to the keggle itself.

I have plenty of experience with 120V household stuff, just not 240V.

Thanks for any help

__________________
Patched Kettle Brewery

"Drilling more holes than we need to, since 2010."
ExHempKnight is offline
 
Reply With Quote Quick reply to this message
Old 10-22-2010, 04:26 AM   #2
Walker
I use secondaries. :p
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
Walker's Avatar
Recipes 
 
Join Date: Sep 2005
Location: Cary, NC
Posts: 11,235
Liked 72 Times on 64 Posts
Likes Given: 11

Default

You don't need the neutral for your application. You can leave it dangling. Just put a wire cap on it.

__________________
Ground Fault Brewing Co.
Walker is offline
 
Reply With Quote Quick reply to this message
Old 10-22-2010, 04:27 AM   #3
ExHempKnight
Feedback Score: 0 reviews
Recipes 
 
Join Date: Oct 2010
Location: Roanoke
Posts: 117
Liked 2 Times on 2 Posts

Default

I thought that might be the case. Will it still provide ground fault protection?

__________________
Patched Kettle Brewery

"Drilling more holes than we need to, since 2010."
ExHempKnight is offline
 
Reply With Quote Quick reply to this message
Old 10-22-2010, 04:35 AM   #4
Walker
I use secondaries. :p
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
 
Walker's Avatar
Recipes 
 
Join Date: Sep 2005
Location: Cary, NC
Posts: 11,235
Liked 72 Times on 64 Posts
Likes Given: 11

Default

yes. it will. I can give you gory details about how the GFI works, but short answer is that it will still work.


One comment. Folks generally put the GFI as early in the system as they can... like right in the breaker box. Your comments indicate that you are connecting that cable to the kettle, which means you have GFI only on the kettle and not on the control box you are going to be building.

Is that accurate?

__________________
Ground Fault Brewing Co.
Walker is offline
 
Reply With Quote Quick reply to this message
Old 10-22-2010, 04:46 AM   #5
ExHempKnight
Feedback Score: 0 reviews
Recipes 
 
Join Date: Oct 2010
Location: Roanoke
Posts: 117
Liked 2 Times on 2 Posts

Default



That's straight out of the PID manual.

That is basically how I plan to wire it up. The GFI cable will be connected at the 240V input. Only difference will be that mine will have the ground running to the keggle (and possibly the control box, if that ends up being metal).
__________________
Patched Kettle Brewery

"Drilling more holes than we need to, since 2010."

Last edited by ExHempKnight; 10-22-2010 at 04:49 AM.
ExHempKnight is offline
 
Reply With Quote Quick reply to this message
Old 10-23-2010, 08:53 PM   #6
shushikiary
Feedback Score: 0 reviews
Recipes 
 
Join Date: Apr 2010
Location: denver
Posts: 161
Liked 6 Times on 6 Posts

Default

Note that your test button on the breaker may not work if the neutral is not connected but the breaker should still work.

You can connect the neutral to ground if you want to make the test button work, as long as how you have it wired has no current going through the breaker to ground you wont cause a safety issue. Most 2 poll GFCI's have a neutral in and then a pigtail, in which you're suppose to connect the neutral from the circuit to the neutral in on the breaker and then the pigtail to neutral. If you dont connect anything to the neutral in on the breaker and then put the pigtail to ground the test button will work and the GFCI will still protect you on a ground fault.

__________________
shushikiary is offline
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
Heatstick of doom! Start with wiring Qs. nostalgia Electric Brewing 40 01-16-2012 11:49 PM
Multiple GFCI wiring question Cpt_Kirks Electric Brewing 8 10-20-2010 03:22 PM
Wiring diagram advice frank551 Electric Brewing 6 10-19-2010 01:56 PM