02-05-2011, 06:55 PM
|
#1
|
|
Feedback Score: 0 reviews
Join Date: May 2009
Location: New Jersey
Posts: 591
Liked 1 Times on 1 Posts Likes Given: 2
|
Auber SYL-2352 PID issue: Temp way off
|
|
Hi all,
I'm testing my control box connections today and I'm at a bit of a loss as to why my one PID isn't reading right.
Background:
Basic theelectricbrewery.com clone
Three PID's using RTD probes wired to XLR receptacles
Facts:
PIDs are wired identical (345 on pid to the 3 connections on the XLR)
Using the same probe & cable to test each one
PIDs are all set to Sn21
Probe is in ice water for this test
Test:
Boil PID
Probe says 37-40* (in the realm, but don't have a spare term to check)
Mash PID
Probe says -318* and flashes (orAL)
HL PID
Probe says 37-40* (same as Boil...so if its off its off universally)
First thing I did was check to make sure all the connection were the same between the three and they are.
Now before I start switching the 3-4-5 connections does anyone have any thoughts?
Thanks
-Jay
__________________
Hazard Brewing
|
|
|
02-06-2011, 03:12 AM
|
#2
|
|
Feedback Score: 0 reviews
Join Date: Mar 2008
Location: Pottstown, Pa
Posts: 1,537
Liked 22 Times on 20 Posts Likes Given: 2
|
did you check the boil probe in the mash pid to see if it is a probe or a pid issue?
|
|
|
02-06-2011, 05:39 AM
|
#3
|
|
Feedback Score: 0 reviews
Join Date: Mar 2009
Location: Vancouver, WA
Posts: 49
Liked 2 Times on 2 Posts
|
check the connections on the mash PID, I had mine flashing orAL last evening when I powered it up with the RTD disconnected
|
|
|
02-06-2011, 02:38 PM
|
#4
|
|
Feedback Score: 0 reviews
Join Date: May 2009
Location: New Jersey
Posts: 591
Liked 1 Times on 1 Posts Likes Given: 2
|
milldoggy:
Its the same wire from the XLR to the probe...i've been testing them one at at a time
twardnw:
All the connections seem fine
What is the downside to randomly changing the RTD connections on the PID? Can it blowout the probe or something?
__________________
Hazard Brewing
|
|
|
02-06-2011, 05:45 PM
|
#5
|
|
Feedback Score: 0 reviews
Join Date: Mar 2009
Location: Vancouver, WA
Posts: 49
Liked 2 Times on 2 Posts
|
seem fine or test fine? I wouldn't trust them unless you can have continuity from end-to-end.
Don't know about switching out the probes while powered on, I would be very hesitant to do that.
|
|
|
02-06-2011, 10:23 PM
|
#6
|
|
Death by Magumba!
Feedback Score: 0 reviews
Join Date: Aug 2007
Location: Melbourne, Fl
Posts: 2,253
Liked 22 Times on 14 Posts Likes Given: 5
|
Make sure you have the PID set to use an RTD input, I think they default to a k thermocouple. Also you may have 2 of the three wires swapped. 2 wires should show 0 resistance and the third wire should show around 100 ohms or more between it and the other 2 wires. Make sure you have them landed in the right order on the PID.
Looking at the diagram on mine, the 2 wires that show 0 resistance go to terminals 3 and 4, the third wire goes to 5.
|
|
|
02-07-2011, 03:18 AM
|
#7
|
|
Feedback Score: 0 reviews
Join Date: May 2010
Location: Evanston, Illinois
Posts: 1,168
Liked 9 Times on 9 Posts
|
Quote:
Originally Posted by CodeRage
Make sure you have the PID set to use an RTD input, I think they default to a k thermocouple. Also you may have 2 of the three wires swapped. 2 wires should show 0 resistance and the third wire should show around 100 ohms or more between it and the other 2 wires. Make sure you have them landed in the right order on the PID.
Looking at the diagram on mine, the 2 wires that show 0 resistance go to terminals 3 and 4, the third wire goes to 5.
|
I'll bet this is it. I had the same problem initially.
__________________
On Tap: Surly Furious, Belgian Trippel, Da Yoopers Pale Ale, Chocolate Lager, Wee too Heavy (barrel aged Scottish), Belgian Barrel Aged Barleywine, Simcoe Pale Ale, Galaxy/Nelson Sauvin IIPA, Broken foot Pilsner, Da Yooper's Oatmeal Stout
Bourbon Barrel
Kegged:
Fermenting Gumballhead with Nelson Sauvin
on Deck: Dogfish Head Indian Brown Clone, Ocktoberfast Ale, Rodenbach Clone.
|
|
|
02-14-2011, 09:12 PM
|
#8
|
|
Feedback Score: 0 reviews
Join Date: May 2009
Location: New Jersey
Posts: 591
Liked 1 Times on 1 Posts Likes Given: 2
|
I had to rewire the three on the PID until it finally showed a true temp.
Very frustrating when you have three of them next to each other all wired the same and one needs to be wired differently.
Thanks for pointing me in the right direction!
__________________
Hazard Brewing
|
|
|
02-14-2011, 11:28 PM
|
#9
|
|
Feedback Score: 0 reviews
Join Date: Mar 2010
Location: Charlotte, NC
Posts: 2,755
Liked 142 Times on 118 Posts Likes Given: 188
|
I'm betting that the difference is in the way you connected the wires to the XLR connectors. Just swapping 2 wires when you solder them in place could do it. Especially when you are looking at opposite rotation when looking at the wire side of the plug and receptacle.
Just thinking out loud...
|
|
|
02-15-2011, 06:47 PM
|
#10
|
|
Feedback Score: 0 reviews
Join Date: May 2009
Location: New Jersey
Posts: 591
Liked 1 Times on 1 Posts Likes Given: 2
|
THat's what I thought too.
Only issue is the 3 XLR's are in a row as well all the same orientation and each using the same colored wires (R-K-W in my case).
It was just the middle one that needed to be different...(which oddly is the only one that has no SSR attached to it as it is mainly there for a temp readout / alarm purpose).
The other thing of note is on the BK and HLT PIDs have no issue being disconnected and reconnected to the probe while powered up.
They show the orAL error when unplugged but switch back after it is reconnected.
The MLT PID will not "recover" from being unplugged while powered up.
Get me wondering if maybe that PID might be a little "short-bus special"...not really a big concern as its impact on the system is low.