Default Allen-Bradley Contactor Wiring Help

I need help. I purchased 4 Allen-Bradley C30 Contactors last year from zeus53219 (http://www.homebrewtalk.com/f16/cont...ements-273489/), but just now getting around to wiring my control panel. (I posted this Q in his classified as well)

The plan is to use 2 of the C30's together to bring in the 50a service. Then the other 2 to be used on each of the elements.

I understand the element wiring concept just don't know exactly where to stick the wires. Can someone please post a really good pic or an easy to follow diagram?

Now, combining the 2 contactors to bring in the 50a service is where I'm really confused. Can this be done, and obviously, if so, can someone please explain.

Thanks in advance.

__________________
ironmountainbrew is offline
 
Reply With Quote Quick reply to this message
Old 01-15-2013, 08:31 PM   #2
JRems
Feedback Score: 0 reviews
Recipes 
 
Join Date: Nov 2010
Location: Mahopac, NY
Posts: 2,229
Liked 58 Times on 50 Posts
Likes Given: 9

Default

Why would you need 2 contactors to bring in the power? You should only need to use one contactor to allow both hot wires to be connected. I don't know why you would need or want a contactor for the neutral and ground. Unless I am misunderstanding. Can you post a wiring diagram you are using?

__________________
Quote:
Originally Posted by Bobby_M View Post
Simcoe smells like 10 cats pissing on a pine tree. It's awesome.
JRems is offline
 
Reply With Quote Quick reply to this message
Old 01-15-2013, 09:38 PM   #3
Intimnasc
Feedback Score: 0 reviews
Recipes 
 
Join Date: Dec 2012
Location: Fort Worth, Texas
Posts: 69
Liked 10 Times on 7 Posts
Likes Given: 5

Default

Yes it absolutely can be done but should not be done. Calculate your total load not counting incidental loads twice and get the proper size relay. Here is why I say this. Say the relays are rated for 30 amps each and you wire them in parralell to split the load. They may work for a while until one fails and the other gets full load and blows up causing alot of damage to any other components mounted close. If they are rated for 50 plus amps just use one if not get the correct size.

__________________

“Beer is proof that God loves us and wants us to be happy.”
― Benjamin Franklin

Intimnasc is offline
 
Reply With Quote Quick reply to this message
Old 01-15-2013, 10:16 PM   #4
stevehaun
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Dec 2006
Location: hudson, wi
Posts: 564
Liked 12 Times on 12 Posts
Likes Given: 22

Default

According to your link, they are rated for 30 amps. You should not use them to bring in the 50 amp service. They can be used to control one 5500 watt element. To control the 50 amp service, you need a contactor that is rated for a 50 amp resistive load.

__________________
stevehaun is offline
 
Reply With Quote Quick reply to this message
Old 01-15-2013, 10:17 PM   #5
ryane
Feedback Score: 0 reviews
Recipes 
 
Join Date: Nov 2008
Location: Washington
Posts: 780
Liked 5 Times on 5 Posts

Default

You cant split the current between two contactors because in a 240V single phase center tap application the current flows between the two hot legs of the circuit

The link you posted said the contactor is good for 28A at 240V, so youll blow the contactor when using a 50a load.

If you want a cheap 2phase 50A resistive contactor you can get them HERE for ~$11 each plush shipping

once you get the correct contactors, you wire them up like the picture attached, although if your having trouble understanding the contactors you might want to reassess what your attempting, tell us everything you want to do, and we can all help to make sure your set up is safe

untitled.jpg  
ryane is offline
 
Reply With Quote Quick reply to this message
Old 01-15-2013, 10:48 PM   #6
ironmountainbrew
Feedback Score: 0 reviews
Recipes 
 
Join Date: Sep 2011
Location: Festus, MO
Posts: 39
Default

I made an assumption based on a diagram from ebrewsupply. It appears that he is using two 40a contactors to pull in the 50a service. I was really just double checking, but sounds like I may have been mistaken on how to use the contactors.

http://www.ebrewsupply.com/designs/P...D-Electric.pdf

He's using 1 40a contactor in to the ssr and contactor for one of the elements. Then the other to the 15a breaker and down to the other ssr and contactor.

I'm going off a diagram P-J created, but had assumed the two contactors would work based on the above diagram and was trying to figure out how to use the two contactors I had.

Here's the P-J diagram:

iron_mountain_brewing-syl-2352-5500w-3.jpg  
__________________
ironmountainbrew is offline
 
Reply With Quote Quick reply to this message
Old 01-15-2013, 11:46 PM   #7
ryane
Feedback Score: 0 reviews
Recipes 
 
Join Date: Nov 2008
Location: Washington
Posts: 780
Liked 5 Times on 5 Posts

Default

In the diagram posted from ebrewsupply, there are using two contactors where I would only use one, also each of their contactors are rated @ 40A resistive, not 28A

If you want to do this I would purchase a 50A contactor, use a single contactor to turn power on as I showed in the diagram and then you can use your c30s downstream, although I would just buy enough 50A contactors do it all , after all $20 extra isnt that much, and then everything downstream is rated to the input current (I would add fuses prior to the elements if you dont use the breaker as per PJs diagram to limit the current to 30A - this is needed to protect the 10awg SO cord you would use to run to the element)

__________________
RyanBrews - check out all the bread/funk/pickling/cheese and other crazy things I try...
ryane is offline
 
Reply With Quote Quick reply to this message
Old 01-16-2013, 03:21 AM   #8
ironmountainbrew
Feedback Score: 0 reviews
Recipes 
 
Join Date: Sep 2011
Location: Festus, MO
Posts: 39
Default

Thanks for all of the replies. Sounds like I'm going to order a 50a contactor to bring the main in and just go w what P-J provided. I liked the idea of using AB because they are higher quality and were a good deal from Zeus. Too bad I didn't know what I was doing when I bought them. Oh well. I'm sure I can sell the 2 contactors that I wont use to pay for a 50a.

__________________
ironmountainbrew is offline
 
Reply With Quote Quick reply to this message
Reply



Quick Reply
Message:
Options
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
allen bradley 1000 beerpoppa DIY Projects 11 01-30-2013 10:24 AM
Allen Bradley SLC 500 jmer1234 Electric Brewing 26 10-26-2012 04:11 AM
For Sale - More Electrical Stuff - Allen-Bradley This Time Around SweetSounds For Sale 9 10-02-2012 10:40 PM
Contactor wiring tjash Electric Brewing 4 09-15-2012 02:19 AM
Contactor Wiring Help TriangleIL Electric Brewing 16 04-03-2012 09:18 PM