Old 11-12-2012, 03:24 PM   #51
ajdelange
Senior Member
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Aug 2010
Location: McLean/Ogden, Virginia/Quebec
Posts: 5,962
Liked 591 Times on 488 Posts
Likes Given: 16

Default

Quote:
Originally Posted by whoaru99 View Post
No.

There is no 180 phase shift.Your own oscilloscope proves that using the waveform math because if you sum those waves you put up the result is zero volts.
The oscilloscope picture plainly shows two waveforms that are 180° out of phase. When one is at the voltage peak with respect to the reference (which is ground) the other is at the voltage minimum with respect to the reference. The voltage at a point is the potential difference between that point and some reference point. The potential difference (voltage) between two points is the difference in the potentials measured with respect to a common reference. In this case at peak we'd have +120 (ignore the sqrt(2)) factor on one phase and -120 on the other both with respect to the neutral. They are out of phase and the difference in potentials is 120 -(-120) = 240V. That's how this works. Subtracting the waveforms on the scope proves nothing except that they are (if I get a flat line) equal and opposite in phase (as they should be). Try to understand this. If you don't fully appreciate how voltages are measured it is little wonder you are confused.

Quote:
Originally Posted by whoaru99 View Post
The only reason it looks like they're 180 out is because you're using the wrong reference point. A parlor trick, for lack of better terms.
There is no such thing as a 'wrong' reference. The choice of reference is completely arbitrary as long as it is common. You may not like my choice of reference because it shows the fallacy in your argument but there is nothing wrong with it. If I choose the physicists reference, a sphere in space infinitely far away, there may be a cajillion volts potential difference between that point and the center tap on the transformer but that doesn't matter. When the potential at the top winding termination goes up to a cajillion + 120V the potential at the bottom winding will go down to a cajillion -120 and the difference will be 240.

And your choice doesn't change things either. With using the bottom phase as the reference you get +120 to the center tap and +240 to the top. Thus the potential across the top coil is +120. Thus the bottom is at -120 with respect to the center tap and the top at plus 120. Same as before.

If the choice is arbitrary then which point should we pick given that we can get the same information from any? I'd say the one that makes things the simplest. It seems obvious to me that in a balanced system with the center tap earthed ground (or the grounded conductor) is the obvious choice. When examining the wave form from an outlet on either side of the panel the reference is available to us. If we used a phase for the reference we'd have to drag a wire across the floor if the reference phase were connected to the opposite side of the system. Of course if all we are interested in is one side we can use that side's phase as the reference. Using the neutral produces equal voltages when both phases are examined. As the whole object of the system is to have 2 lower voltage circuits this would be desirable.The thing I really like about it is that it is consistent with the notion of the neutral as defined by the IEC as the conductor that connects to the star point in a Y connected polyphase system. IOW you don't have to shift gears when going from 3 phase to 2 phase systems.



Quote:
Originally Posted by whoaru99 View Post
One would think an EE would know that two waves of equal amplitude and frequency, when 180 out, will cancel not sum. Since we know the waves aren't canceled when both legs are used, we know the waves cannot be 180 out of phase.
We don't have two generators in series that are 180 apart. They are in phase. But they are connected L1---->T---->L2. Note that the high side (>) of the L1 generator is connected to the T (center tap) as is the low side of the L2 generator. This can be modeled by two generators which are 180° out of phase each with its low side connected to the center tap L1<---T--->L2 and that's what the textbooks and the 3 references mean/show when they diagram or talk about two out of phase sources. In any case L1 and L2 are 180° apart in phase with respect to T. They may do it this way because if you add a third arrow (generator with lo side to neutral) to make a thing that looks like the Mercedes logo you have the phasor diagram for a Y connected 3 phase system.

As this is going to be my swan song here (no point in repeating the same material to deaf ears again) I might suggest, if you know anything about electronics, that you have a look at things like push-pull amplifiers which are really exactly the same circuit with emphasis on trying to understand what the 'phase inverter' is for (in the simplest case it's a transformer connected just like the power pole ones but it can be electronics as well). Balanced mixers are another circuit which uses a center tapped transformer as a phase inverter.

Quote:
Originally Posted by whoaru99 View Post
All the spin, fancy dancing, and deflection doesn't change the fact that waves 180 out don't add, they cancel.
That depends on how they are connected. In a differential amplifier such as in a balanced microphone circuit (that's something else you might look at) they add. If you have two generators connected back to back (lo side of each to neutral), as we do here, they add. You must, when thinking about these things consider both the phase of the generator and how it is connected.

Your problem seems to be mostly caused by inability to recognize that there are other ways to model things than the model you cleave to. L1-->T-->L2 with the generators in phase is a fine model if you use T as the reference and a workable but clumsy one if you use L1 or L2. But L1<--T-->L2 is an equally good model if the generators are 180° apart in phase (and again you have the choice of reference). It's a better model in that it is symmetrical as is the system it is modeling. Symmetry makes things easier to see (for most people). The results will be the same with either. Voltages measured at L1 with respect to T will be of equal amplitude and opposite phase compared to voltages measured at L2 with respect to T.


Quote:
Originally Posted by whoaru99 View Post
Further, the point about being two phase in this case is wrong. I grant you that two phase power could exist and may well exist in the wild (120/208 - 120V L-N, 208V L-L), but what we're discussing isn't that nor is that common household distribution.
Certainly in most cases brewers will be in their homes in the US but the US isn't the whole world and the fact that in most cases it comes from a transformer on a pole doesn't make it wrong. You are still getting two phases. My reason for bringing this up was I thought that if you could understand what's happening in a 120/208 biphase system and appreciated that the only difference between that and the split phase system is 120° vs 180° you would understand that they are really the same in terms of voltages. But that didn't work. I also brought up the zig-zag generator wiring method as a means of obtaining split phase in the hopes that this would help you to see how things work but that didn't work either.



Quote:
Originally Posted by whoaru99 View Post
Frankly, I think the whole notion of two waves in this regard (120/240 split voltage) is even flawed. It's the same wave, you're just looking at half of it on the left and half on the right from the midpoint.
I thought you were of the opinion that looking at things with respect to the midpoint was a parlor trick.


Quote:
Originally Posted by whoaru99 View Post
No out of phase involved because it's just plain old, simple, single phase.
Once the third wire goes in it is no longer single phase. I will not repeat the definition of polyphase as I getting tired of laying this out for you over and over again. But I will point out that the two waveforms are not exact copies of one another because the transformer is not perfectly symmetric nor is the load. If one side has a power factor different from the other there will even be a phase shift so that you will have a phase difference of something other than 180°. This removes the 'mirror phase' argument but I feel more like a lawyer than an engineer in pointing that out.

If you look at voltages with respect to the midpoint there is no question that one phase will be 180° out with respect to the other (at least in most practitioner's minds).


Quote:
Originally Posted by whoaru99 View Post
All the talking point trying to apply polyphase theory are non sequitur.
Charlie Chan said in one of those movies "Mind like parachute. Function best when open." It's disapointing that you can't see the relevance but I don't feel that I've wasted my time entirely as it's sort of fun to go back and review some of this stuff.
__________________
ajdelange is offline
 
Quick reply to this message
Old 11-12-2012, 04:37 PM   #52
stlbeer
Senior Member
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
stlbeer's Avatar
Recipes 
 
Join Date: Jan 2008
Location: Fenton, MO
Posts: 882
Liked 33 Times on 32 Posts
Likes Given: 82

Default

Ajdelange and Whoaru99,

Thanks for schooling us on how we get 240v in our houses/breweries. This has been a very thought provoking thread and you've both delivered your arguments very well without resorting to diminishing the other.

Well done.

__________________
My RIMS eBrewery build
stlbeer is offline
 
Quick reply to this message
Old 11-12-2012, 04:45 PM   #53
ajdelange
Senior Member
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Aug 2010
Location: McLean/Ogden, Virginia/Quebec
Posts: 5,962
Liked 591 Times on 488 Posts
Likes Given: 16

Default

Quote:
Originally Posted by stlbeer View Post
Ajdelange and Whoaru99,

Thanks for schooling us on how we get 240v in our houses/breweries. This has been a very thought provoking thread and you've both delivered your arguments very well without resorting to diminishing the other.

Well done.
If somebody got something out of it it was worth doing it.
__________________
ajdelange is offline
 
Quick reply to this message
Old 11-12-2012, 05:09 PM   #54
whoaru99
Feedback Score: 0 reviews
Recipes 
 
Join Date: Oct 2012
Posts: 1,590
Liked 124 Times on 101 Posts
Likes Given: 16

Default

Here's another interesting read, from the previously referenced source, that confirms once again what I've been saying all along.

The typical household supply, 120/240V, is just plain old single phase with nothing operating 180 degrees out from anything else. In-phase voltages from the two legs add, out of phase voltages from the two legs would cancel. There is no way you'd get 240V from two 120V legs that are out of phase with each other. It's no more complex than that despite the attempted obfuscation to say otherwise.

They even use some of the same examples that you tried to use, but they got it right.

http://www.allaboutcircuits.com/vol_2/chpt_2/3.html

__________________

Primary: Pre-prohibition Lager
Secondary: Russian Imperial Stout
Drinking: Chinook IPA
Drinking: Waldo Lake Amber
Drinking: Edwort's Apfelwein

whoaru99 is offline
 
Quick reply to this message
Old 11-12-2012, 08:15 PM   #55
audger
Feedback Score: 0 reviews
Recipes 
 
Join Date: Apr 2011
Location: ., Connecticut
Posts: 1,497
Liked 40 Times on 40 Posts
Likes Given: 1

Default

Quote:
Here's another interesting read, from the previously referenced source, that confirms once again what I've been saying all along.
that is assuming we are talking about multiple "phases" of power, which we are not. 240v is a single "phase". it sounds like people are using words like "phase" and "single phase" and "polyphase" without knowing exactly what that means.

first- there is really no such thing as "two phase" power (let me qualify that with; "commonly found around here in the US"). we have either single phase or three phase power. "two phase" is a misnomer when comparing two different single phase (120v) power feeds. the two lines coming in that make up 240v are actually from the same "phase" of the three-phase transformer.


this is a diagram of the output of a wye transformer (those canisters about the size of a beer keg that hang on the electric pole outside your house; normally in clusters of two or three).



so the lines coming into your house would be; A, B, and Neutral/ground (your neighbor might be connected to lines B, C and neutral; and someone else to A, C, and neutral, etc). so you can see we are dealing with only one "phase". A+B=phase1, B+C=phase2, A+C=phase3; we only have lines A+B coming into the house, so we can only have access to that one phase.

now, how do we get 120 volts at the wall plug? the voltage potential between any two of the legs in the above picture is 240v. if you put a multimeter between A+B, or B+C, or A+C; it will read 240v. however- the voltage potential between any one of the legs and neutral happens to be 120v. there is some math that explans why this works, but im not going to muddy the waters for those who arent numbers people. but hopefully this helps you visualize why both sides of a 240v circuit are actually the same "phase", yet seemingly 180 degrees apart (A and B are actually 120 degrees apart in a three phase circuit).

so to answer the question 'how do we get 120 volts at the wall plug?'; one prong of the plug would be connected to A (or B), and the other prong of the plug would connect to neutral... giving 120v. if you have two plugs; one fed by A, and the other fed by B... you could design a device that plugged into each of them and provided 240v of power (one whole "phase").

EDIT: i mixed up my delta and wye transformers, though it doesnt matter exactly for this discussion- the idea is the same... its all one single "phase". but line voltage on a wye transformer between A+B (or any other combo of two) is actually 208v. see here...
__________________
audger is offline
 
Quick reply to this message
Old 11-12-2012, 09:08 PM   #56
ajdelange
Senior Member
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Aug 2010
Location: McLean/Ogden, Virginia/Quebec
Posts: 5,962
Liked 591 Times on 488 Posts
Likes Given: 16

Default

Where do you guys come up with this stuff? If the voltage between the coil ends in your diagram (A, B or C) and the neutral is 120 V the voltage from one terminus to another (A-B, B-C or C-A) is 208 V because the the A-N, B-N and C-N are separated in phase by 120°. This is not how your house is connected. Go out to the pole and look. Assuming A, B, C, N (i.e. all three phases) appear on your pole there will a terminal on the transformer that is wired to one of the phases (A, B or C). There will be another terminal which may just be tied to the transformer can (the end of the secondary inside the can is also connected to it in this case) which is wired to the neutral. These are the primary coil terminals. Then at the top on the other side from the primary terminals are 3 other (secondary) terminals which are connected to the service entrance in your house. These are the two phases from the secondary winding with the middle one being the center tap point (neutral). At your service entrance the neutral will be bonded to a wire from an earthing rod and the neutral and two phases will enter your house. These are, as has been extensively discussed, approximately (depending on transformer and load balance) 180° out of phase with one another when measured WRT the neutral. From one of these to neutral you would measure 120*sqrt(2) volts at cycle peak. From the other to neutral you would measure -120*sqrt(2). Between the two phases you would measure (120 -(-120))*sqrt(2) = 240*sqrt(2).

In the Y connection the voltage from say A-N is 120*sqrt(2). From B-N it would be 120*sqrt(2)*(-cos(60°) + j*sin(60°)). The difference is

120*sqrt(2)*(1 -(-cos(60)) - j*sin(60))

= 120*sqrt(2)*(1.5 - j*sqrt(3)/2))

The j means this component is at right angles so the magnitude is

120*sqrt(2)*sqrt( (3/2)^2 + (sqrt(3)/2)^2) =

120*sqrt(2)*sqrt(9/3 + 3/4) = 120*sqrt(2)*sqrt(12/4) =

120*sqrt(2)*sqrt(3) = 208*sqrt(2) volts or 208 VRMS for 120 VRMS on a phase.

Your neighborhood will have the load distributed between the 3 pole phases but this is done by hooking one transformer to A, another to B another to C and so on.

I swore I was done with power but this is just so far off I can't let it stand.

__________________
ajdelange is offline
 
Quick reply to this message
Old 11-12-2012, 09:14 PM   #57
P-J
HBT_LIFETIMESUPPORTER.png
Feedback Score: 0 reviews
Recipes 
 
Join Date: Mar 2010
Location: Charlotte, NC
Posts: 3,257
Liked 250 Times on 201 Posts
Likes Given: 441

Default

I cannot believe how deep the grave is that has been dug for this thread.

Just goes to show how much BS can cover up other things.

Keep going guys. The thread is dead now anyway.

Un-Subscribed now.

__________________
P-J is offline
 
Quick reply to this message
Old 11-12-2012, 10:12 PM   #58
whoaru99
Feedback Score: 0 reviews
Recipes 
 
Join Date: Oct 2012
Posts: 1,590
Liked 124 Times on 101 Posts
Likes Given: 16

Default

Quote:
Originally Posted by audger View Post

first- there is really no such thing as "two phase" power (let me qualify that with; "commonly found around here in the US"). we have either single phase or three phase power. "two phase" is a misnomer when comparing two different single phase (120v) power feeds. the two lines coming in that make up 240v are actually from the same "phase" of the three-phase transformer.
Actually there is two phase power. I agree though it is relatively uncommon, perhaps even obsolete in the original form, and certainly not the 120/240V single phase, split voltage system common to households.
__________________

Primary: Pre-prohibition Lager
Secondary: Russian Imperial Stout
Drinking: Chinook IPA
Drinking: Waldo Lake Amber
Drinking: Edwort's Apfelwein

whoaru99 is offline
 
Quick reply to this message
Old 11-13-2012, 03:28 AM   #59
stlbeer
Senior Member
HBT_SUPPORTER.png
Feedback Score: 0 reviews
 
stlbeer's Avatar
Recipes 
 
Join Date: Jan 2008
Location: Fenton, MO
Posts: 882
Liked 33 Times on 32 Posts
Likes Given: 82

Default

Mods - please close this thread to additional updates.

__________________
My RIMS eBrewery build
stlbeer is offline
 
Quick reply to this message
Old 11-13-2012, 09:50 AM   #60
Yuri_Rage
Gritty.
HBT_MODERATOR.png
Feedback Score: 0 reviews
 
Yuri_Rage's Avatar
Recipes 
 
Join Date: Jul 2006
Location: Southwest
Posts: 13,916
Liked 607 Times on 376 Posts
Likes Given: 54

Default

Between the namecalling and the nearly on-topic engineering debate that has gone wildly awry, it is time to close this thread.

__________________
Homebrewed Blog..........YouTube Channel .......... Shirts, posters, etc
Yuri_Rage is offline
 
Quick reply to this message
Closed Thread



Quick Reply
Message:
Options
Thread Tools


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale - RIMS: Tri-clamp 4500W element ALL NEW conardg For Sale 3 11-09-2012 10:24 PM
4500W element 240V v 220V (easy question) ekjohns Electric Brewing 14 09-05-2012 03:27 PM
4500W. LWD element too much for a 8gallon boil? BrewinBigD Electric Brewing 5 03-16-2012 12:27 AM
Help Finding 4500W Heating Element <12" SOB Electric Brewing 3 01-14-2011 04:49 PM
Using 2 simmerstats to control 4500W/5500W element gregdech DIY Projects 10 04-15-2010 03:46 PM